    Unhappy Gravity liquid/vapor separator to little?



    Hi
    Im from Peru, i have problems with liquid carryover to suction line compressors in ammonia system for an IQF tunnel, aeroheat model 2010, 2 Mycom N42WB, Gravity Liquid/vapor horizontal separator (2200 mm length x 600 mm dia).
    When start 2nd compressor, at 67% capacity, liquid carryover right to compressors. The contractor said the size of the separator is small, need to change for 3500 mm lenght x 1200 mm dia. because when we will load the tunnel could be worse.

    is that correct?
    thanks
    aphun



  2. #2
    Join Date
    Nov 2008
    Location
    Peru
    Posts
    11
    Rep Power
    0

    Re: Gravity liquid/vapor separator to little?

    i forgot diagram
    Attached Files Attached Files

  3. #3
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    374
    Rep Power
    18

    Re: Gravity liquid/vapor separator to little?

    Hi Aphun,
    600 mm is really little, at least 1000 mm

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Gravity liquid/vapor separator to little?

    The high pressure liquid level makeup is suspect by your schematic also .
    It is close to dry suction, so higher velocities could cause carryover .
    Make sure regulating valve is adjusted so it is feeding liquid makeup 70 - 75 % of the time when at max load .
    Also make sure liquid reciever has good level so no hi pressure gas blasting into surge drum .

  5. #5
    Join Date
    Nov 2008
    Location
    Peru
    Posts
    11
    Rep Power
    0

    Re: Gravity liquid/vapor separator to little?

    Thanks Josef/Ranger1
    Here a contractor thinks if we place a liquid acumulator tank before suction compresors could we avoid that.
    But, that means increase the suction length in 10 mts (actual 18mts 5"dia) more, does it afect the suction temperature of the gas in order to get -35ºC in the tunnel?
    Thanks
    aphun

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Gravity liquid/vapor separator to little?

    Wont affect temps but you then also have to have heat source to boil off refrigerant that comes back to suction trap .
    ie liquid line coil inside suction trap also hi level cut out float control .

  7. #7
    Join Date
    Nov 2008
    Location
    Peru
    Posts
    11
    Rep Power
    0

    Re: Gravity liquid/vapor separator to little?

    Hi Ranger
    if the contractor wants to put inside this tank a heater like oil compressor with a level switch, in order to eliminate the liquid every time this turn on?
    thanks

  8. #8
    Join Date
    Nov 2008
    Location
    Peru
    Posts
    11
    Rep Power
    0

    Re: Gravity liquid/vapor separator to little?

    Hi
    About the liquid carryover, its not the size of vessel; we raise the suction pipe over the level of the LVS, and remove the demister pad inside, instead put drop eliminator; and the problem is gone.
    aphun

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Gravity liquid/vapor separator to little?

    Quote Originally Posted by aphun
    we raise the suction pipe over the level of the LVS, and remove the demister pad inside, instead put drop eliminator...
    A demister pad and droplet eliminator (I'm assuming you mean chevron style) both operate with similar velocities therefore, I would think the main issue could be assigned to the suction pipe being too close to the liquid level in the vessel.

    If that is the case, then you had insufficient separation distance to dis-engage the liquid form the vapor stream.
    If all else fails, ask for help.


  10. #10
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Gravity liquid/vapor separator to little?

    With out going in and doing a design calculation on your surge drum, I would first look at a few things.

    -Liquid level
    -where the liquid enters the vessel in relation to suction and liquid level.
    -location of wet return
    -suction location
    -excessive oil in the drum

    You would be surprised at the number of so-called refrigeration experts that can not properly design a suction or pump drum.

    Ken

  11. #11
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Gravity liquid/vapor separator to little?

    Quote Originally Posted by TXiceman
    You would be surprised at the number of so-called refrigeration experts that can not properly design a suction or pump drum.
    Now, now, don't be mean.

    I agree with you though. Most of the "experts" use rating tables and have no appreciation for the actual mechanics involved.
    If all else fails, ask for help.


Similar Threads

  1. gravity coil
    By nh3simman in forum Fundamentals
    Replies: 5
    Last Post: 25-10-2008, 02:09 PM
  2. Replies: 23
    Last Post: 06-06-2008, 02:27 PM
  3. Gravity Recirculated PHE
    By gwapa in forum NH3
    Replies: 37
    Last Post: 04-04-2007, 04:23 AM
  4. DX v/s Gravity
    By Hemant Anand in forum Industrial
    Replies: 7
    Last Post: 19-07-2006, 02:16 AM
  5. Gravity Deli not defrosting completely.
    By kengineering in forum Commercial
    Replies: 13
    Last Post: 26-04-2006, 11:25 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •