18-11-2008, 07:53 PM #1
R22 TEV suitable to use on a 407c charge?
Got a 407c pool heat pump factory fitted with a fixed position R22 thermal expansion valve. I’m getting intermittent flood-back and occasional high amps. I’ve since relocated bulb and insulated which has improved the situation.
22 and 407C have similar pressure temperature readings. Can someone advice if a R22 TX valve is interchangeable for use on a 407c charged unit?
-
18-11-2008, 08:05 PM #2
Re: R22 TEV suitable to use on a 407c charge?
R22 Power Assemblys were used originally when R407C systems introduced in the UK, as R407C power assemblys were not available, usually you will need to adjust, to obtain the correct superheat. It can be a little trial and error but persevere and you should be able to get it set correctly.
-
18-11-2008, 08:42 PM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
18-11-2008, 09:24 PM #4
Re: R22 TEV suitable to use on a 407c charge?
Answer is still the same, but action will be different. R22 Power Assembly can be used on R407C. Trial and error on Phial position should cure the problem, and get the superheat within range. Try some Heatsink compound between phial and pipe it may help
Not wanting to teach granny to suck eggs. but the phial position in relation to the pipesize is very important. Get this right and rest will follow.
-
18-11-2008, 10:27 PM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: R22 TEV suitable to use on a 407c charge?
Generally TEV for R22 are set at 3-5K superheat. Superheat for R407 should be 6-8K. I don't see how phial placement could lead to increase of superheat.
If TEV is nonadjustable it cannot be adjusted for proper superheat and need to be changed with new one (preferabli wih R407C powerhead)
Check this article!
-
19-11-2008, 09:25 AM #6
Re: R22 TEV suitable to use on a 407c charge?
-
19-11-2008, 09:43 AM #7
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: R22 TEV suitable to use on a 407c charge?
Phial=bulb
Bulb should be located as stated at instalation manual of TEV (like this one) and is usually between 1 and 4 o'clock (8 and 11 o'clock) depending on suction pipe size.Last edited by nike123; 19-11-2008 at 09:50 AM.
-
19-11-2008, 11:59 AM #8
Re: R22 TEV suitable to use on a 407c charge?
( don't see how phial placement could lead to increase of superheat.
If TEV is nonadjustable it cannot be adjusted for proper superheat)
I seen some will move the bulb closer to the evaporator I even it on the evaporator to decrease superheat or move it far as they can down stream to increase superheat
-
19-11-2008, 02:08 PM #9
Re: R22 TEV suitable to use on a 407c charge?
I think he meant a valve body that was brazed in rather than flared?
-
19-11-2008, 02:12 PM #10
Re: R22 TEV suitable to use on a 407c charge?
Similar Threads
-
407c Charge
By N.Lewis in forum RefrigerantsReplies: 5Last Post: 27-02-2008, 09:21 AM -
To charge or not to charge?
By Fire and Ice in forum Old Refrigeration PhotosReplies: 12Last Post: 20-01-2008, 08:11 PM -
Help please. How to charge a unit
By God55 in forum Air ConditioningReplies: 18Last Post: 23-03-2007, 10:07 AM -
Subcooling vs charge graph?
By Larry2 in forum FundamentalsReplies: 4Last Post: 01-12-2006, 07:40 PM -
Who's in charge?
By chillin out in forum Chit Chat & Service StoriesReplies: 1Last Post: 01-10-2006, 10:51 PM