    Question R22 TEV suitable to use on a 407c charge?



    Got a 407c pool heat pump factory fitted with a fixed position R22 thermal expansion valve. I’m getting intermittent flood-back and occasional high amps. I’ve since relocated bulb and insulated which has improved the situation.

    22 and 407C have similar pressure temperature readings. Can someone advice if a R22 TX valve is interchangeable for use on a 407c charged unit?



  2. #2
    Join Date
    Sep 2008
    Location
    Lancs - UK
    Age
    67
    Posts
    30
    Rep Power
    0

    Re: R22 TEV suitable to use on a 407c charge?

    R22 Power Assemblys were used originally when R407C systems introduced in the UK, as R407C power assemblys were not available, usually you will need to adjust, to obtain the correct superheat. It can be a little trial and error but persevere and you should be able to get it set correctly.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: R22 TEV suitable to use on a 407c charge?

    Quote Originally Posted by Iceman1956 View Post
    R22 Power Assemblys were used originally when R407C systems introduced in the UK, as R407C power assemblys were not available, usually you will need to adjust, to obtain the correct superheat. It can be a little trial and error but persevere and you should be able to get it set correctly.
    Quote Originally Posted by danielt_smith View Post
    Got a 407c pool heat pump factory fitted with a fixed position R22 thermal expansion valve.
    Check that post again!

  4. #4
    Join Date
    Sep 2008
    Location
    Lancs - UK
    Age
    67
    Posts
    30
    Rep Power
    0

    Re: R22 TEV suitable to use on a 407c charge?

    Answer is still the same, but action will be different. R22 Power Assembly can be used on R407C. Trial and error on Phial position should cure the problem, and get the superheat within range. Try some Heatsink compound between phial and pipe it may help

    Not wanting to teach granny to suck eggs. but the phial position in relation to the pipesize is very important. Get this right and rest will follow.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: R22 TEV suitable to use on a 407c charge?

    Quote Originally Posted by Iceman1956 View Post
    Answer is still the same, but action will be different. R22 Power Assembly can be used on R407C. Trial and error on Phial position should cure the problem, and get the superheat within range. Try some Heatsink compound between phial and pipe it may help

    Not wanting to teach granny to suck eggs. but the phial position in relation to the pipesize is very important. Get this right and rest will follow.
    Generally TEV for R22 are set at 3-5K superheat. Superheat for R407 should be 6-8K. I don't see how phial placement could lead to increase of superheat.
    If TEV is nonadjustable it cannot be adjusted for proper superheat and need to be changed with new one (preferabli wih R407C powerhead)

    Check this article!

  6. #6
    Join Date
    Nov 2007
    Location
    Australia
    Posts
    5
    Rep Power
    0

    Smile Re: R22 TEV suitable to use on a 407c charge?

    Quote Originally Posted by Iceman1956 View Post
    R22 Power Assemblys were used originally when R407C systems introduced in the UK, as R407C power assemblys were not available, usually you will need to adjust, to obtain the correct superheat. It can be a little trial and error but persevere and you should be able to get it set correctly.
    Thanks for the feed back.
    Replacing old TEV with one with an adjustable setting. Will try with setting of 6-8K.
    I am unsure of the term 'phial placement'. The bulb was at 12 o'clock on the pipe and I relocated to 8 o'clock if that's what is meant?

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: R22 TEV suitable to use on a 407c charge?

    Quote Originally Posted by danielt_smith View Post
    Thanks for the feed back.
    Replacing old TEV with one with an adjustable setting. Will try with setting of 6-8K.
    I am unsure of the term 'phial placement'. The bulb was at 12 o'clock on the pipe and I relocated to 8 o'clock if that's what is meant?
    Phial=bulb

    Bulb should be located as stated at instalation manual of TEV (like this one) and is usually between 1 and 4 o'clock (8 and 11 o'clock) depending on suction pipe size.
    Last edited by nike123; 19-11-2008 at 09:50 AM.

  8. #8
    Join Date
    Aug 2006
    Location
    Spencer ma.
    Age
    60
    Posts
    108
    Rep Power
    18

    Re: R22 TEV suitable to use on a 407c charge?

    ( don't see how phial placement could lead to increase of superheat.
    If TEV is nonadjustable it cannot be adjusted for proper superheat)

    I seen some will move the bulb closer to the evaporator I even it on the evaporator to decrease superheat or move it far as they can down stream to increase superheat

  9. #9
    Join Date
    Aug 2007
    Location
    UK
    Age
    42
    Posts
    135
    Rep Power
    17

    Re: R22 TEV suitable to use on a 407c charge?

    I think he meant a valve body that was brazed in rather than flared?

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: R22 TEV suitable to use on a 407c charge?

    Quote Originally Posted by danielt_smith View Post
    I’m getting intermittent flood-back...
    How can we have a discussion of superheat without knowing what superheat you are getting? Where are the pressure and temperature measurements?

Similar Threads

  1. 407c Charge
    By N.Lewis in forum Refrigerants
    Replies: 5
    Last Post: 27-02-2008, 09:21 AM
  2. To charge or not to charge?
    By Fire and Ice in forum Old Refrigeration Photos
    Replies: 12
    Last Post: 20-01-2008, 08:11 PM
  3. Help please. How to charge a unit
    By God55 in forum Air Conditioning
    Replies: 18
    Last Post: 23-03-2007, 10:07 AM
  4. Subcooling vs charge graph?
    By Larry2 in forum Fundamentals
    Replies: 4
    Last Post: 01-12-2006, 07:40 PM
  5. Who's in charge?
    By chillin out in forum Chit Chat & Service Stories
    Replies: 1
    Last Post: 01-10-2006, 10:51 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •