    question. how to set prv on chill water make up line?



    how and what would you set the pressure regulating valve on the chillwater make up line?



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: question. how to set prv on chill water make up line?

    Quote Originally Posted by spongebob View Post
    how and what would you set the pressure regulating valve on the chillwater make up line?
    Measure the height of the loop (feet) and divide by two. This is the minimum pressure (psi) that must be maintained at the bottom of the loop.

    For example, if the height of the building/loop is 50 ft, the system needs 25 psi at the bottom when the water pressure is at its lowest (coldest water). Any less will put the top of the system in a vacuum and invite air problems.

    PRV's come factory set at 12 psi, which is sufficient for most residential systems, but the setting must be increased for higher structures.
    Last edited by Gary; 18-11-2008 at 02:03 PM.

  3. #3
    spongebob's Avatar
    spongebob Guest

    Re: question. how to set prv on chill water make up line?

    thanks for the info.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: question. how to set prv on chill water make up line?

    To correctly determine pressures in systems and to dimension expansion vessels, safety valves, filling networks and etc.... you could use this software.

Similar Threads

  1. cold river water
    By eftimios in forum Fundamentals
    Replies: 8
    Last Post: 09-11-2008, 06:37 PM
  2. Water chiller help
    By ultralo1 in forum Trouble Shooting
    Replies: 6
    Last Post: 12-05-2007, 11:52 AM
  3. Iced suction line - Question from Rockfun
    By Brian_UK in forum Air Conditioning
    Replies: 8
    Last Post: 14-06-2006, 07:24 PM
  4. Will iron rich water attack copper & s/steel?
    By garyb in forum Trouble Shooting
    Replies: 1
    Last Post: 14-02-2006, 03:55 PM
  5. Minimal required R134a speed in suction line
    By DaBit in forum CPU Overclockers
    Replies: 32
    Last Post: 08-05-2002, 05:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •