18-11-2008, 07:06 AM #1
question. how to set prv on chill water make up line?
how and what would you set the pressure regulating valve on the chillwater make up line?
-
18-11-2008, 01:47 PM #2
Re: question. how to set prv on chill water make up line?
Measure the height of the loop (feet) and divide by two. This is the minimum pressure (psi) that must be maintained at the bottom of the loop.
For example, if the height of the building/loop is 50 ft, the system needs 25 psi at the bottom when the water pressure is at its lowest (coldest water). Any less will put the top of the system in a vacuum and invite air problems.
PRV's come factory set at 12 psi, which is sufficient for most residential systems, but the setting must be increased for higher structures.Last edited by Gary; 18-11-2008 at 02:03 PM.
-
19-11-2008, 04:41 AM #3
Re: question. how to set prv on chill water make up line?
thanks for the info.
-
19-11-2008, 09:22 AM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: question. how to set prv on chill water make up line?
To correctly determine pressures in systems and to dimension expansion vessels, safety valves, filling networks and etc.... you could use this software.
Similar Threads
-
cold river water
By eftimios in forum FundamentalsReplies: 8Last Post: 09-11-2008, 06:37 PM -
Water chiller help
By ultralo1 in forum Trouble ShootingReplies: 6Last Post: 12-05-2007, 11:52 AM -
Iced suction line - Question from Rockfun
By Brian_UK in forum Air ConditioningReplies: 8Last Post: 14-06-2006, 07:24 PM -
Will iron rich water attack copper & s/steel?
By garyb in forum Trouble ShootingReplies: 1Last Post: 14-02-2006, 03:55 PM -
Minimal required R134a speed in suction line
By DaBit in forum CPU OverclockersReplies: 32Last Post: 08-05-2002, 05:19 AM