    CO2 (R744) Evaporator



    Dear All,

    Do anybody have experiences about designing CO2 Evaporator ?
    Is it different max. operating pressure pump evaporator and DX evaporator ? Because I've ever known for DX evap max operating pressure design is 32 bar and Pumped evap design is 50 bar, but they use same material tube from stainles steel 304. Why is it different ?


    If I have pumped evap CO2 and only use test pressure (1.1 x 32 bar) 35 bar. It is OK ?

    BR
    CITS



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: CO2 (R744) Evaporator

    No it is not. You have to consider the standstill pressure, not the working pressure or the phase of refrigerant. If for any reason your evaporator will have two-phase CO2 at standstill, then the design pressure is much, much higher. It all depends on how you are sizing the safety valve on the low side.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Designing Roll Bond Evaporator
    By Munzar Ata in forum Fundamentals
    Replies: 11
    Last Post: 05-08-2010, 11:31 AM
  3. Evaporator TD and refrigeration effect
    By nambiandy in forum Fundamentals
    Replies: 2
    Last Post: 11-10-2008, 11:39 AM
  4. Absortpion Refrigeration - Evaporator Basics
    By knudo in forum Fundamentals
    Replies: 4
    Last Post: 28-08-2007, 08:03 AM
  5. What is the best location for a evaporator fan?
    By Jasno999 in forum Fundamentals
    Replies: 3
    Last Post: 21-02-2007, 12:34 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •