    Hi all,
    I've been set a task of preparing a powerpoint presentation and reading it out in front of the class at college. This is the task;
    "Describe system layout and operating principles for multi evaporator systems with independant control for each evaporator"

    I've decided to explain about a VRF, however i have a few questions.

    Firstly, how does heat recovery work? I know that it uses the heat from one room and transfers it to another room but this can be done with out the compressor running, or so i have heard. Is this true? and if so how?

    What type of VRV/VRF's are there, i.e 2pipe (that heat or cool) 3 pipe (that can heat and cool simultaneously) and supposedly Mitsubishi have brought out a 2pipe that can do what daikins 3 pipe does, how true is this and again how does this work.

    Lastly do the indoor units on VRV/VRFs have evaporator pressure regulators on or are these not needed?

    Lots of questions, sorry


    The difference between genius and stupidity is that genius has its limits.

    Marc

  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: A couple of questions

    Good luck Marc... EPRs are not required on these AC units because you have EEV on the inlet.

    Personally I would have gone for a multi evaporator cold room system as it should be easier to explain.

    {edit} Have a look at the Sporlan EPR document here..
    http://www.parker.com/literature/Spo...0090/90-20.pdf
    Last edited by Brian_UK; 15-11-2008 at 11:33 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: A couple of questions

    Mitsubishi City Multi VRF R2 heat recovery operation example.

    One indoor unit in heating mode ( condenser )
    One indoor unit in cooling mode ( evaporator )
    Outdoor unit compressor sends hot gas to B/C distributon box which in turn sends the hot gas to the indoor unit asking for heat.
    The indoor unit heating condenses the hot gas to a warm liquid which returns to the B/C distrubution box & through a subcooler to get rid of bubbles in liquid.
    The B/C disribution box sends cool liquid to unit asking for cooling.
    The cooling unit flashed off the liquid through the LEV valve & vapor returns to the B/C distributon box.
    From B/C distributon box vapor returns on suction pipe back to outdoor units.

    Full heat recovery from room cooling to room heating.
    Only 2 pipes needed.
    Been doing it like this since 2001 in the UK & longer in japan.

    The refrigeration is simple basic stuff its all the electrinic control thats complicated.

  4. #4
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: A couple of questions

    Quote Originally Posted by Brian_UK View Post
    Good luck Marc... EPRs are not required on these AC units because you have EEV on the inlet.

    Personally I would have gone for a multi evaporator cold room system as it should be easier to explain.

    {edit} Have a look at the Sporlan EPR document here..
    http://www.parker.com/literature/Spo...0090/90-20.pdf
    I would like to talk about a cold room but i dont know enough about them because i don't work on them often.
    The problem that i am having with using a VRF system is how far do i go? Do i talk about 2 pipers or 3 pipers, bc boxes or bs boxes, fixed speed compressors or inverter compressors and the list goes on... meaning my presentation will go on for a long time and everyone will probably be asleep by then.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  5. #5
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: A couple of questions

    Quote Originally Posted by Thermatech View Post

    One indoor unit in heating mode ( condenser )
    One indoor unit in cooling mode ( evaporator )
    Outdoor unit compressor sends hot gas to B/C distributon box which in turn sends the hot gas to the indoor unit asking for heat.
    The indoor unit heating condenses the hot gas to a warm liquid which returns to the B/C distrubution box & through a subcooler to get rid of bubbles in liquid.
    The B/C disribution box sends cool liquid to unit asking for cooling.
    The cooling unit flashed off the liquid through the LEV valve & vapor returns to the B/C distributon box.
    From B/C distributon box vapor returns on suction pipe back to outdoor units.
    So what you have explained is how a 2 piper works? So discharge is sent to BC box and superheated vapour is returned on the suction line.
    I heard that heat recovery can be done when the outdoor unit has stopped running and the heat from one room can be used and transferred to another room that requires heating. Not sure if its Mitsuibishi or Daikin systems that do this, or both.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: A couple of questions

    Hi Marc

    The compressor is needed in both 2 pipe and 3 pipe systems (Mitsi and Daikin) to produce the circulation. Without the compressor you cannot achieve any heating or cooling.

    With Daikin 3 pipe, if the indoor units are balanced, i.e. 5 cooling and 5 heating, then the outdoor coil is not needed and the outdoor condenser fans do not run, but the compressor does.

    As soon as one of the indoor units is satisfied on thermostat or changes mode then the indoor circuit become unbalanced and the outdoor coil acts as either condenser or evaporator to make up the imbalance.

    Does this make sense to you?

  7. #7
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: A couple of questions

    Hi Frank,
    yes that makes sense. I wondered how it could work without the compressor running but i was assured it did.
    Thanks.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  8. #8
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: A couple of questions

    I need a picture of inside a BC for my presentation but can't find one anywhere. Does anyone know where i could get one?
    The difference between genius and stupidity is that genius has its limits.

    Marc

  9. #9
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: A couple of questions

    You might find something usefull on the Mitsubishi Electric USA or Austrailia web sites.

    BTW
    in full heat recovery the compressor runs to circuulate refrigerant but outdoor coil & fan are not needed or used.

    All the best for your presentation.

  10. #10
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: A couple of questions

    Quote Originally Posted by marc5180 View Post
    I would like to talk about a cold room but i dont know enough about them because i don't work on them often.
    The problem that i am having with using a VRF system is how far do i go? Do i talk about 2 pipers or 3 pipers, bc boxes or bs boxes, fixed speed compressors or inverter compressors and the list goes on... meaning my presentation will go on for a long time and everyone will probably be asleep by then.
    don't worry, when i went for mi presentation or final script, it was 364 pages. i designed an indoor ice rink of 1800mē. they were happy. the other guys had 10 or 15 pages. i heard last year it was still there as model for newcomers.

    Ice

Similar Threads

  1. Please help with these questions!!
    By tsl001 in forum Supermarket Refrigeration
    Replies: 31
    Last Post: 05-05-2010, 11:19 AM
  2. Interview questions
    By zimbo in forum Chit Chat & Service Stories
    Replies: 16
    Last Post: 10-09-2008, 10:06 PM
  3. Questions about Chiller Design
    By Vincent Yu in forum Fundamentals
    Replies: 9
    Last Post: 06-06-2008, 01:00 PM
  4. A couple of questions.
    By marc5180 in forum Fundamentals
    Replies: 10
    Last Post: 05-03-2008, 01:04 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •