    Mitsubishi Fault codes



    Hi guys,First post in quite awhile.
    Have an issue with a Mitsubishi MR SLIM A/C,MODEL PUH-5YKSA (Australia). Hope one of the experts can help me with the fault codes, specifically the P8 fault. Cheers steptoe111



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Mitsubishi Fault codes

    Indoor unit pipe probe temperature abnormal.

    Look what simple search function of this forum returns when you search for "fault codes"

    http://www.refrigeration-engineer.co...earchid=633108

  3. #3
    Join Date
    Feb 2008
    Location
    Adelaide South Australia
    Posts
    6
    Rep Power
    0

    Re: Mitsubishi Fault codes

    Many thanks Nike,not finding this site very easy to navigate yet! I read from your reply that the system is suffering from low refrigerant syndrome? Cheers

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Mitsubishi Fault codes

    Quote Originally Posted by steptoe111 View Post
    Many thanks Nike,not finding this site very easy to navigate yet! I read from your reply that the system is suffering from low refrigerant syndrome? Cheers
    If the termistor is OK, then possibility is that is refrigerant amount, or air flow problem!

  5. #5
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Mitsubishi Fault codes

    On the old R22 Mr Slim units the indoor unit could only send 2 commands to the outdoor unit using 12v d/c 3 core interconnecting cable.
    1/ compressor on
    2/ Reversing valve energized.


    The outdoor unit was unable to send any data back to the indoor unit.

    The way the indoor unit detected any problem with the outdoor unit was by constantly monitoring the refrigerant temperature at the indoor coil & difference from room return air.

    In cooling the indoor unit reports P8 if the difference between return air & refrigerant coil temp is less than 5 deg C for about 8 mins.
    The coil temp must be more than 5 deg C below room return air temp for the indoor unit to consider that the outdoor unit is operating.

    So P8 covers a multitude of sins.
    possibilities are
    1/ indoor unit temperature sensors reading incorrect temperature.
    2/ Some sort of problem with the outdoor unit.
    3/ incorrect interconnecting wiring connections.
    4/ interconnect cable from indoor unit connected to another outdoor unit (crossed pipes & control cable between multiple systems)

    A good place to start is at the outdoor unit circuit board.
    There is a row of red LED's on the control circuit board.
    If any are blinking then look at the label on the service access panel which should have a list of the faults indicated by the blinking LED's.

  6. #6
    Join Date
    Apr 2008
    Location
    australia
    Age
    58
    Posts
    47
    Rep Power
    0

    Re: Mitsubishi Fault codes

    Quote Originally Posted by Thermatech View Post
    On the old R22 Mr Slim units the indoor unit could only send 2 commands to the outdoor unit using 12v d/c 3 core interconnecting cable.
    1/ compressor on
    2/ Reversing valve energized.


    The outdoor unit was unable to send any data back to the indoor unit.

    The way the indoor unit detected any problem with the outdoor unit was by constantly monitoring the refrigerant temperature at the indoor coil & difference from room return air.

    In cooling the indoor unit reports P8 if the difference between return air & refrigerant coil temp is less than 5 deg C for about 8 mins.
    The coil temp must be more than 5 deg C below room return air temp for the indoor unit to consider that the outdoor unit is operating.

    So P8 covers a multitude of sins.
    possibilities are
    1/ indoor unit temperature sensors reading incorrect temperature.
    2/ Some sort of problem with the outdoor unit.
    3/ incorrect interconnecting wiring connections.
    4/ interconnect cable from indoor unit connected to another outdoor unit (crossed pipes & control cable between multiple systems)

    A good place to start is at the outdoor unit circuit board.
    There is a row of red LED's on the control circuit board.
    If any are blinking then look at the label on the service access panel which should have a list of the faults indicated by the blinking LED's.
    What would you do if there were no leds lit on outdoor pcb?

  7. #7
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: Mitsubishi Fault codes

    Fistly check for mains power at condensing unit. If that is correct and turning the power off for a couple of minutes and then re-instating power then pressing SW2 button should change over the display mode. LD8 should be lit to indicate that power is on for the crankcase heater. Post back for next set of info.

Similar Threads

  1. Mitsubishi Fault Codes. (and spares schematics)
    By Grizzly in forum Air Conditioning
    Replies: 0
    Last Post: 29-04-2008, 05:45 PM
  2. mitsubishi a/c fault codes
    By leey in forum New to RE
    Replies: 12
    Last Post: 04-04-2008, 10:46 PM
  3. mitsubishi city multi fault code
    By robin r33 gtr in forum Air Conditioning
    Replies: 5
    Last Post: 05-11-2007, 10:23 PM
  4. fault codes for mitsubishi heavy industries air con
    By mal in forum Trouble Shooting
    Replies: 1
    Last Post: 21-10-2006, 06:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •