Results 1 to 12 of 12
    Nov 2008
    NELSON BAY AUST
    43
    48
    Cool Trouble shooting tx valves
    This may be a silly q but i have recently started working in commercial refrigeration and am wonder if any one has any helpful info on trouble shootin tx valves, i have a few systems running with full sight glasses and still not floodin evap correctly not sure if i may have restriction or if orifice needs changing or even checking and adjusting super heats i have many years expirence in domestic refrigeration and whitegoods so if any q's on these dont hesitate also ill be askin on pressure controls soon but more interested in txv's at moment thanks guys hope to chat about things soon
    Split Croatia
    57
    6,151
    36
    Apr 2001
    79
    5,071
    35
    Re: Trouble shooting tx valves
    Quote Originally Posted by TECH TIM View Post
    Not unlike a domestic fridge, the evaporator is fully flooded ONLY when the refrigerated space is down to design temperature. When the refrigerated space is warm, the superheat is supposed to be high.
    Apr 2008
    phillippines
    125
    tech tim,
    what is the application,btuh rating of equipment,system pressure and txv rating?
    regards,
    abet
    Nov 2008
    NELSON BAY AUST
    43
    48
    Thank for links very helpful
    Nov 2008
    NELSON BAY AUST
    43
    48
    Thanks Gary for your reply that has seemed to be the case after running 24hr or so evap seem alot better thanks again
    Nov 2008
    NELSON BAY AUST
    43
    48
    not real sure on tech specs i have been workin on various displays and drink fridges mainly, most jobs have been compressor changes but i havnt had much to do with tx valves etc and have noted coils flood differently to domestics wich is my forte... im wanting to leave that behind and move on to commercial/ industrial all in good time i guess thanks for your replie
    Aug 2005
    5,302
    Direct expansion evaporators are NEVER flooded (on purpose).
    The inside of the evaporator coil will have approx. 80-85% of it's internal area wetted by liquid refrigerant. The last 15-20% of the coil surface area is used for superheating the refrigerant vapor.
    If you start a system up warm, the superheat will be higher than normal. Do not adjust the TXV during this time.
    Wait until the temperatures are down to the expected range and then check the superheat.
    May 2008
    midlands
    64
    37
    excellent posts with links thanks guys helped me work out why my 404 walkin freezer isnt getting the right superheat after compressor and evep change
    Feb 2011
    malaysia
    5
    its very wrong and sily to adjust the txv. the txv is pre-set by the factory
    now you have big problem you compressor will damage and txv need to replace good luck
    3,853
    Quote Originally Posted by unicorn77 View Post
    You can always adjust the valve back to how it should be set, so long as it is not faulty.
    Jun 2009
    North East England
    41
    712
    Good point if i ever adjust a txv i always count the number of turns to try and make sure the setting is returned to it's original position
  1. LG split system fan cont. trouble shooting
    By ianv in forum Trouble Shooting
    Last Post: 01-02-2011, 03:31 PM
  2. Contactor service and trouble shooting
    By zerodegreec in forum Electrical
    Last Post: 16-09-2008, 12:58 PM
  3. Trouble Shooting
    By Vincent Yu in forum Fundamentals
    Last Post: 22-11-2005, 02:04 PM
  4. Trouble shooting Guide
    By raghu in forum Trouble Shooting
    Last Post: 21-05-2005, 03:03 PM
  5. 24V trouble shooting
    By Frig Pig in forum Trouble Shooting
    Last Post: 09-01-2004, 05:58 AM