    pingu's Avatar
    pingu Guest
    1501 fault mitsubishi vrf
    hi what would cause a 1501 fault apart from overcharging of gas ow its on 410a
    11,025
    Re: 1501 fault mitsubishi vrf
    I thought that a 1501 fault was an undercharge fault which means there is a leak somewhere.
    Mar 2007
    Warwickshire UK
    723
    21
    1500 is for overcharge
    The outdoor unit looks at the discharge pressure & discharge temperature & then calculates the discharge superheat.
    If the discharge superheat is less than 10 deg C & the outdoor unit stops at this condition twice in 30 mins then the system stops on 1500 fault.
    The system has major liquid flood back to outdoor unit or the sensors are providing incorrect data to the outdoor control circuit board.
    If the system has correct refrigerant charge then other possible causes are
    1/ discharge pressure sensor incorrect data.
    2/ discharge temp sensor incorrect data.
    3/ a liquid to suction bypass in the system which is allowing liquid to flood back to the outdoor unit & overflow the suction accumulator.
    For 1501 fault please provide outdoor model number
    Feb 2008
    504
    21
    this is from mitsi manual 1500 fault code can not find 1501 fault code
    1500 Refrigerant
    overcharge
    An error can be detected
    by the discharge temperature
    superheat.
    1. If the discharge SH
    10K or less is detected
    during operation (the
    first detection), the
    once, turns to anti-restart
    mode for 20 seconds,
    and restarts
    after 20 seconds automatically.
    2. If the discharge SH
    again within 30 minutes
    after first stop of
    the outdoor unit (the
    second detection), the
    outdoor unit will make
    an error stop, and the
    error code "1500" is
    displayed.
    3. If discharge SH 10K or
    less is detected more
    than 30 minutes after
    the outdoor unit stops,
    and the operation described
    in step 1
    above will start.
    4.For 30 minutes after
    the stop of the outdoor
    unit, preliminary errors
    will be displayed on
    the LED display.
    (1) Overcharged refrigerant Refer to the page on refrigerant
    amount evaluation.
    (2) Thermistor input circuit
    failure on the main board
    (3) Faulty mounting of thermistor
    (TH11, TH12)
    Check the temperature and the pressure
    of the sensor with LED monitor
  1. mitsubishi heavy split fault
    By grovecoooling in forum Air Conditioning
    Last Post: 13-03-2011, 12:29 PM
  2. Mitsubishi VRF Fault
    By marc5180 in forum Air Conditioning
    Last Post: 14-08-2008, 10:48 PM
  3. Fault code for a mitsubishi heavy
    Last Post: 29-02-2008, 08:22 PM
  4. mitsubishi city multi fault code
    By robin r33 gtr in forum Air Conditioning
    Last Post: 05-11-2007, 10:23 PM