    Chilled water binder test point
    One for the UK chiller technicians.
    Can anyone recomend a manufacturer / supplier in the uk for binder type pressure gauge.
    I want to measure water pressure drop across a heat exchanger & there are some binder type access points installed in the flow & return pipework.
    I have not done much chilled water work for a good many years now so I am at bit rusty.But as water cooled VRF is becoming more popular I am finding that it would be usfull to have this type of kit again.
    Aug 2001
    1,046
    Re: Chilled water binder test point
    I haven't seen binder gauges for many years.
    I would suggest that you look at suppliers of boiler gauge equipment in the UK.
    Good luck - all my old gauges were calibrated in psi and I went SI 20 years ago.
    Somerset
    69
    4,699
    Quote Originally Posted by Thermatech View Post
    Thermatech
    We use them all the time, they are still available from BSS or Plumbcenter (sorry Climatecenter.)
    I will try and look up the reference/ part numbers and get back to you
    Argus.
    We still use psi and multiply by 7 (when not having a calculator) to convert to kpa.
    Aug 2001
    1,046
    Glad you can still get them.
    It always beats me how people commission chillers without them as it's impossible to check the flow rate without measuring the PD.
    How many chillers get still installed with-out the test points?
    Aug 2005
    5,302
    Argus, what is a binder gauge? It sounds like differential pressure gauge?
    11,025
    The older type differential gauge is almost obsolete, it's all digital now
    See here...
    http://www.cranefs.co.uk/index.asp?F...%3A44%3A546393
    Flow 2006 software here...
    http://www.cranefs.co.uk/index.asp?F...%3A46%3A195464
    Aug 2005
    5,302
    OK Brian. Thanks. I guess I'm showing my age now, huh? My old gauge was just that, old. However, it worked well and I have to agree you cannot accurately commission a chiller without one of these (or your newer fancy digital model that comes in a box )
    Aug 2001
    1,046
    It was a trade name that became synonymous with the product.... bit like ‘Hoover’ for a vacuum cleaner.
    Here's a link that describe it, but Brian may have already covered it.
    http://www.test-plugs.com/
    In essence it consisted of a small brass connection point that was installed in the immediate flow and return lines on chillers, boilers etc.
    The whole thing consisted of a small brass fitting, with a screwed cap that was removable to reveal a pierced rubber insert that could take a pointed tube attached to a gauge or thermometer. When pushed through the rubber seal it could then directly sample the water pressure or temperature at source. Gauges are open to inaccuracies, but if you had a calibrated manometer with binder points it was possible to check the exact PD through a chiller.
    A double-reading thermocouple would also give the TD.
    When removed the rubber insert closed up to seal the pipe and the seal cap was replaced.
    They were VERY useful.... but prone to leaks when the rubber perished and the cap was lost.
    I don’t know about you, but I have seldom seen a chiller that had the PD that the commissioning engineer said it should have had when I checked it with a gauge.
    Aug 2005
    5,302
    Thanks Argus. The test plugs referred to are similar to what we call Pete's Plugs.
    The PD gauge I had was a NIST-certified gauge and measured in.H2O to achieve improved accuracy instead of psi.
    I think this entire process is a bit like a game of darts. If you get in the bulls-eye, it's close enough. Even if you were lucky enough to have a chart for chiller/condenser flow vs. pressure loss it was still a crap shoot sometimes.
    You can use a pump curve and head to help verify the PD data, but it is all within some tolerance as far as I was able to decipher.
    11,025
    The age old problem of course is fouling of the heat exchanger, hot or cold, which always screws up your readings.
    A commissioning valve with built-in orifice is the best thing but whether they get fitted is another matter.
    Apr 2007
    West Midlands
    45
    55
    Hi guy's
    I commission chiller's and i have to check the pressure drop's using the binder gauges ( when the nipples are installed!) If there's no point's installed we refuse to sign off the commissioning of the unit until there fitted. The Delta T gives us a idea of the flow across but you can't beat physically seeing it!
    Our maintenances also require us to check the pressure drop.
    Not to sure where they obtain the gauges tho, my company gave me 3 with different measurements of readings. If you can't find them still let me know and i'll ask our office.
    Mar 2007
    Warwickshire UK
    723
    21
    Many thanks for your replies chaps.
    I offen tend to commission with the system running flatout then I know within a few kw the system performance duty. I accuratly measure the Td flow & return. Then I can calculate the water flow L/s or M3/hr ect.
    The regulating valve can be adjusted to provide the Td & water volume required.
    As the tolerance for VRF flow temperature is +10 deg C to +50 deg C this method is normally ok.
    But for trouble shooting it would be helpfull to have another method of measurment to prove volume flow arround the water circuit.
    I did hear tell of ultra sonic flow test meters but would assume they would be very expensive.
    Did anyone have any experiance with this type of kit ?
    11,025
    I used an ultrasonic many, many years ago.
    It did the job that I wanted but you are dependent on having dirty water flowing. I know that sound silly but it is the dirt particles, or bubbles, that are being sensed.
    If you can get a proper orifice in then so much the better.
    Aug 2005
    5,302
    My experience with ultrasonic flow meters is that you need to be careful where you place them on the piping, you need something in the water to measure the flow, and that their sensitivity is dependent on the quality and calibration.
    Some models are not very expensive, others are.
    Apr 2006
    41
    1,620
    Dwyer has manomitors of difriential types!
    I got a Minihelic 5000 series for doing low pressure PD tests calibrated to "H2O
  1. pure water from air
    Last Post: 26-02-2009, 12:25 PM
  2. Chilled water bypass problem
    By MACT in forum Trouble Shooting
    Last Post: 16-10-2008, 02:01 AM
  3. Energy saving in Chilled water system
    By psrao in forum Tools and Calculators
    Last Post: 15-01-2008, 06:54 PM
  4. chilled water PHE
    By priti in forum Trouble Shooting
    Last Post: 31-07-2002, 08:25 PM