    Chilled water binder test point



    One for the UK chiller technicians.

    Can anyone recomend a manufacturer / supplier in the uk for binder type pressure gauge.

    I want to measure water pressure drop across a heat exchanger & there are some binder type access points installed in the flow & return pipework.

    I have not done much chilled water work for a good many years now so I am at bit rusty.But as water cooled VRF is becoming more popular I am finding that it would be usfull to have this type of kit again.



  2. #2
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Chilled water binder test point

    .

    I haven't seen binder gauges for many years.

    I would suggest that you look at suppliers of boiler gauge equipment in the UK.

    Good luck - all my old gauges were calibrated in psi and I went SI 20 years ago.

    .

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Chilled water binder test point

    Quote Originally Posted by Thermatech View Post
    One for the UK chiller technicians.

    Can anyone recomend a manufacturer / supplier in the uk for binder type pressure gauge.

    I want to measure water pressure drop across a heat exchanger & there are some binder type access points installed in the flow & return pipework.

    I have not done much chilled water work for a good many years now so I am at bit rusty.But as water cooled VRF is becoming more popular I am finding that it would be usfull to have this type of kit again.
    Thermatech
    We use them all the time, they are still available from BSS or Plumbcenter (sorry Climatecenter.)
    I will try and look up the reference/ part numbers and get back to you
    Argus.
    We still use psi and multiply by 7 (when not having a calculator) to convert to kpa.
    Grizzly

  4. #4
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Chilled water binder test point

    .


    Glad you can still get them.

    It always beats me how people commission chillers without them as it's impossible to check the flow rate without measuring the PD.

    How many chillers get still installed with-out the test points?


    .

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Chilled water binder test point

    Argus, what is a binder gauge? It sounds like differential pressure gauge?
    If all else fails, ask for help.


  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Chilled water binder test point

    The older type differential gauge is almost obsolete, it's all digital now

    See here...
    http://www.cranefs.co.uk/index.asp?F...%3A44%3A546393

    Flow 2006 software here...
    http://www.cranefs.co.uk/index.asp?F...%3A46%3A195464
    Last edited by Brian_UK; 11-11-2008 at 06:55 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Chilled water binder test point

    OK Brian. Thanks. I guess I'm showing my age now, huh? My old gauge was just that, old. However, it worked well and I have to agree you cannot accurately commission a chiller without one of these (or your newer fancy digital model that comes in a box )
    Last edited by US Iceman; 11-11-2008 at 07:05 PM. Reason: edit
    If all else fails, ask for help.


  8. #8
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Chilled water binder test point

    Quote Originally Posted by US Iceman View Post
    Argus, what is a binder gauge? It sounds like differential pressure gauge?
    .

    It was a trade name that became synonymous with the product.... bit like ‘Hoover’ for a vacuum cleaner.

    Here's a link that describe it, but Brian may have already covered it.
    http://www.test-plugs.com/

    In essence it consisted of a small brass connection point that was installed in the immediate flow and return lines on chillers, boilers etc.

    The whole thing consisted of a small brass fitting, with a screwed cap that was removable to reveal a pierced rubber insert that could take a pointed tube attached to a gauge or thermometer. When pushed through the rubber seal it could then directly sample the water pressure or temperature at source. Gauges are open to inaccuracies, but if you had a calibrated manometer with binder points it was possible to check the exact PD through a chiller.
    A double-reading thermocouple would also give the TD.

    When removed the rubber insert closed up to seal the pipe and the seal cap was replaced.

    They were VERY useful.... but prone to leaks when the rubber perished and the cap was lost.

    I don’t know about you, but I have seldom seen a chiller that had the PD that the commissioning engineer said it should have had when I checked it with a gauge.


    .

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Chilled water binder test point

    Thanks Argus. The test plugs referred to are similar to what we call Pete's Plugs.

    The PD gauge I had was a NIST-certified gauge and measured in.H2O to achieve improved accuracy instead of psi.

    I think this entire process is a bit like a game of darts. If you get in the bulls-eye, it's close enough. Even if you were lucky enough to have a chart for chiller/condenser flow vs. pressure loss it was still a crap shoot sometimes.

    You can use a pump curve and head to help verify the PD data, but it is all within some tolerance as far as I was able to decipher.
    If all else fails, ask for help.


  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Chilled water binder test point

    The age old problem of course is fouling of the heat exchanger, hot or cold, which always screws up your readings.

    A commissioning valve with built-in orifice is the best thing but whether they get fitted is another matter.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Apr 2007
    Location
    West Midlands
    Age
    45
    Posts
    55
    Rep Power
    17

    Re: Chilled water binder test point

    Hi guy's

    I commission chiller's and i have to check the pressure drop's using the binder gauges ( when the nipples are installed!) If there's no point's installed we refuse to sign off the commissioning of the unit until there fitted. The Delta T gives us a idea of the flow across but you can't beat physically seeing it!

    Our maintenances also require us to check the pressure drop.

    Not to sure where they obtain the gauges tho, my company gave me 3 with different measurements of readings. If you can't find them still let me know and i'll ask our office.

  12. #12
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Chilled water binder test point

    Many thanks for your replies chaps.

    I offen tend to commission with the system running flatout then I know within a few kw the system performance duty. I accuratly measure the Td flow & return. Then I can calculate the water flow L/s or M3/hr ect.
    The regulating valve can be adjusted to provide the Td & water volume required.
    As the tolerance for VRF flow temperature is +10 deg C to +50 deg C this method is normally ok.

    But for trouble shooting it would be helpfull to have another method of measurment to prove volume flow arround the water circuit.

    I did hear tell of ultra sonic flow test meters but would assume they would be very expensive.

    Did anyone have any experiance with this type of kit ?

  13. #13
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Chilled water binder test point

    I used an ultrasonic many, many years ago.

    It did the job that I wanted but you are dependent on having dirty water flowing. I know that sound silly but it is the dirt particles, or bubbles, that are being sensed.

    If you can get a proper orifice in then so much the better.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  14. #14
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Chilled water binder test point

    My experience with ultrasonic flow meters is that you need to be careful where you place them on the piping, you need something in the water to measure the flow, and that their sensitivity is dependent on the quality and calibration.

    Some models are not very expensive, others are.
    If all else fails, ask for help.


  15. #15
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Chilled water binder test point

    Dwyer has manomitors of difriential types!

    I got a Minihelic 5000 series for doing low pressure PD tests calibrated to "H2O

Similar Threads

  1. pure water from air
    By Lc_shi in forum New Technologies
    Replies: 32
    Last Post: 26-02-2009, 12:25 PM
  2. Chilled water bypass problem
    By MACT in forum Trouble Shooting
    Replies: 5
    Last Post: 16-10-2008, 02:01 AM
  3. Energy saving in Chilled water system
    By psrao in forum Tools and Calculators
    Replies: 5
    Last Post: 15-01-2008, 06:54 PM
  4. chilled water PHE
    By priti in forum Trouble Shooting
    Replies: 1
    Last Post: 31-07-2002, 08:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •