    Drier, Sight Glass, Solenoid valve , which order?



    On a standard cold room, freezer , underbar etc... , In which order should the sight glass, drier and solenoid valve go and does it really matter? This is assuming that the reciever has a valve that can be used to pump the system down. Also assuming that the client prefers that the sight glass is in the plant room so fitting it closer to the TEXV is not possible. The solenoid valve must also be in the plantroom?



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Drier, Sight Glass, Solenoid valve , which order?

    Quote Originally Posted by Drew View Post
    On a standard cold room, freezer , underbar etc... , In which order should the sight glass, drier and solenoid valve go and does it really matter?
    In truth no it does not matter

    Quote Originally Posted by Drew View Post

    This is assuming that the reciever has a valve that can be used to pump the system down. Also assuming that the client prefers that the sight glass is in the plant room so fitting it closer to the TEXV is not possible. The solenoid valve must also be in the plantroom?
    As a rule they are normally placed

    Dryer - Solenoid - Sightglass and the reason behind that is simple realy.

    The dryer is a filter so is first to remove any rubbish in the system.

    The solenoid is just a valve so can go anyware in the liquid line( the closer to the TEV the better on some systems if liquid hammer is to be prevented).

    The sight glass is a window into the system and by having it last in the line, you can see if the refrigerant is flowing correctly which also proves if the dryer and mag valve are operating correctly.

    taz.

    .

  3. #3
    Join Date
    Oct 2005
    Location
    In a 2 bedroom unit. Why's That? :)
    Posts
    314
    Rep Power
    19

    Re: Drier, Sight Glass, Solenoid valve , which order?

    Quote Originally Posted by taz24 View Post
    In truth no it does not matter


    .
    Sry Tas I have to dissagree with that.


    The sight glass always goes after the drier. What will happen to the sight glass if the drier becomes blocked??

    ...and I would put the solinoid first so the dryier can be accessed easier for servicing, although you are right, the sequence is generally drier, solinoid, sight glass, but there is no problem if the reciever has a service valve in putting the solinoid wherever you like.
    Last edited by dogma; 10-11-2008 at 12:22 PM. Reason: added a bit

  4. #4
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Drier, Sight Glass, Solenoid valve , which order?

    Quote Originally Posted by dogma View Post
    Sry Tas I have to dissagree with that.


    The sight glass always goes after the drier. What will happen to the sight glass if the drier becomes blocked??

    ...and I would put the solinoid first so the dryier can be accessed easier for servicing, although you are right, the sequence is generally drier, solinoid, sight glass, but there is no problem if the reciever has a service valve in putting the solinoid wherever you like.
    Even though he said it doesn't matter, he did say the sight glass last is the most ideal. It doesn't matter in the way of system performance so he's right. Preference in the order does have other factors in play, like not making the drier sweat, getting more value out of the sightglass etc.
    You can't just snip out one line of a his post to argue that he's wrong, he clearly meant performance won't be affected either way, then explained the ideal setup anyway.
    On that note, the drier should be first, you can still replace it by pumping down at the reciever (like the OP stipulated in their senario). A drier after a pump down solenoid will get heaps of condensation on it every time the solenoid pumps down as the refrigerant inside boils of, meaning rust etc.
    So taz24s ideal arrangement which he said was best, ie. drier, valve, sightglass. Drier being anywhere on the liquid line, valve and sightglass as close as possible to the TXV.
    Last edited by paul_h; 10-11-2008 at 02:04 PM.

  5. #5
    Join Date
    Apr 2008
    Location
    Tasmania
    Posts
    216
    Rep Power
    18

    Re: Drier, Sight Glass, Solenoid valve , which order?

    I have also been told to put the sight glass first , because if the drier does block up and you have installed it second the system will show short of refrigerant and a technician who does not know to check for a blocked drier might treat the fault as a gas leak and possibly landup overcharging the system.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Drier, Sight Glass, Solenoid valve , which order?

    Quote Originally Posted by Drew View Post
    I have also been told to put the sight glass first , because if the drier does block up and you have installed it second the system will show short of refrigerant and a technician who does not know to check for a blocked drier might treat the fault as a gas leak and possibly landup overcharging the system.
    Then he shouldn't be working alone yet then.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Oct 2005
    Location
    In a 2 bedroom unit. Why's That? :)
    Posts
    314
    Rep Power
    19

    Re: Drier, Sight Glass, Solenoid valve , which order?

    Quote Originally Posted by paul_h View Post
    You can't just snip out one line of a his post to argue that he's wrong, he clearly meant performance won't be affected either way, then explained the ideal setup anyway.

    Agreed.


    My appologies TAZ.


    _Dogma-

  8. #8
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Drier, Sight Glass, Solenoid valve , which order?

    Quote Originally Posted by paul_h View Post
    Even though he said it doesn't matter, he did say the sight glass last is the most ideal. It doesn't matter in the way of system performance so he's right. Preference in the order does have other factors in play, like not making the drier sweat, getting more value out of the sightglass etc.
    You can't just snip out one line of a his post to argue that he's wrong, he clearly meant performance won't be affected either way, then explained the ideal setup anyway.
    On that note, the drier should be first, you can still replace it by pumping down at the reciever (like the OP stipulated in their senario). A drier after a pump down solenoid will get heaps of condensation on it every time the solenoid pumps down as the refrigerant inside boils of, meaning rust etc.
    So taz24s ideal arrangement which he said was best, ie. drier, valve, sightglass. Drier being anywhere on the liquid line, valve and sightglass as close as possible to the TXV.
    I've just come back to this discussion and read the replies.

    Cheers Paul.

    Quote Originally Posted by dogma View Post
    Agreed.


    My appologies TAZ.


    _Dogma-
    No problem Dogma.
    It was a discussion and you were only making your point.

    We may not always agree on what is best but while we are talking we are learning. I know I learn from this site most days so as the advert says

    Its good to talk.

    Cheers anyway..

    taz.

  9. #9
    Join Date
    Aug 2006
    Location
    Canada
    Age
    61
    Posts
    149
    Rep Power
    18

    Re: Drier, Sight Glass, Solenoid valve , which order?

    Quote Originally Posted by Brian_UK View Post
    Then he shouldn't be working alone yet then.
    Agreed, needs some more time apprenticing.

  10. #10
    JCDARBY's Avatar
    JCDARBY Guest

    Re: Drier, Sight Glass, Solenoid valve , which order?

    Hi, im a new user but i would put it in the order of drier sight glass then sol valve for a pump down system just to prevent your drier rusting out.

  11. #11
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Drier, Sight Glass, Solenoid valve , which order?

    Quote Originally Posted by taz24 View Post
    In truth no it does not matter

    Dryer - Solenoid - Sightglass and the reason behind that is simple realy.

    .
    Why do you placed solenoid before sightglass?

    I see Sporlan recomendations where sightglass placed after solenoid, but also saw many system where solenoid placed after sightglass...
    If you placed: Dryer - Sightglass - Solenoid, then you'll see only normal/unnormal dryer work.

    If you placed: Dryer - Solenoid - Sightglass, then you'll see solenoids hold of refrigerant. But sightglass is the additional distance between solenoid and TEV. When the system stoped, solenoid is closed and liquid refrigerant between solenoid and TEV goes through TEV to evaporator. If solenoid is far from evaporator then large amount of refrigerant may collect in the evaporator and after compressor starting it goes to compressor in liquid phase...
    Also if solenoid placed far from TEV then TEV gets hammer when solenoid is openning.

    About dryer Sporlan recomendation:
    Catch-All Filter-Driers are most effective in the liquid line. Place thefilter-drier immediately ahead of other liquid line controls, such as thethermostatic expansion valve, solenoid valve, and see all miosture Liquid Indicator. When applied in this way, the Catch-All provides maximum protection for the expansion valve and solenoid valve from dirt that may be in the system. If the system contains appreciable
    moisture, then this location gives the best results in protecting the expansion valve from freeze-up. If possible, place the filter-drier in a cold location.
    In some places will have to think ...

  12. #12
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Drier, Sight Glass, Solenoid valve , which order?

    Quote Originally Posted by Aik View Post
    Why do you placed solenoid before sightglass?


    If you placed: Dryer - Solenoid - Sightglass, then you'll see solenoids hold of refrigerant. But sightglass is the additional distance between solenoid and TEV. When the system stoped, solenoid is closed and liquid refrigerant between solenoid and TEV goes through TEV to evaporator. If solenoid is far from evaporator then large amount of refrigerant may collect in the evaporator and after compressor starting it goes to compressor in liquid phase...
    Also if solenoid placed far from TEV then TEV gets hammer when solenoid is openning.

    About dryer Sporlan recomendation:

    I agree with what you say.

    There is an argument for sight glass / mag valve and one for mag valve / sight glass.

    In my opinion the dryer should be first then the other 2 components will be placed in order, best to suit the aplication.

    If you want the mag valve just before the TEV then you would not put the sight lass after it, but if you wanted to use the sight glass to tell you if the mag valve has a restriction in it then it could be placed after it.

    Horses for courses I spose

    The most important thing is for most applications, the posistioning won't effect performance but it will effect diagagnosing issues within the system.

    All the best taz

    .
    Last edited by taz24; 15-06-2010 at 01:45 PM.

  13. #13
    Join Date
    Feb 2008
    Location
    manchester
    Posts
    80
    Rep Power
    17

    Re: Drier, Sight Glass, Solenoid valve , which order?

    Drier should always be first in, if mag valve first in line it can shatter the drier core with liquid being blasted into the drier when mag valve opens. It doesnt happen alot but it will then major issues trying to get the core bits out of the system.

    I will always go drier sightglass then mag valve

  14. #14
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,090
    Rep Power
    33

    Re: Drier, Sight Glass, Solenoid valve , which order?

    Quote Originally Posted by Kp3 View Post
    Drier should always be first in, if mag valve first in line it can shatter the drier core with liquid being blasted into the drier when mag valve opens. It doesnt happen alot but it will then major issues trying to get the core bits out of the system.

    I will always go drier sightglass then mag valve
    i agree you risk drier probs and drier as close to receiver or condensor if no receiver .

  15. #15
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: Drier, Sight Glass, Solenoid valve , which order?

    Drew,
    I agree with Kp3,,,Drier/Sightglass/Solenoid.
    I was taught that when Noah was loading the ark.

  16. #16
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Drier, Sight Glass, Solenoid valve , which order?

    Why we install an SV after drier when using pump down: if you should install drier after SV, then the drier will become cold after each pump down and it will therefore rust (driers are made of steel) very fast.

    Normal situation...at standstill,it can dry out the liquid in the drier.
    Last edited by Peter_1; 16-06-2010 at 11:57 AM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  17. #17
    Join Date
    Dec 2008
    Location
    england
    Age
    77
    Posts
    137
    Rep Power
    16

    Re: Drier, Sight Glass, Solenoid valve , which order?

    well guys,i would put sight glass,drier then solenoid.i have seen through experience what can happen when an apprentice is sent out on his own at an early age.its alright saying they should know what they are doing but these firms want them out earning as soon as possible.they might know it all but at times the brain does;nt control their hands.very clever but cant do the job.

Similar Threads

  1. Odd view in a sight glass
    By dkemper in forum Trouble Shooting
    Replies: 16
    Last Post: 16-06-2010, 12:10 PM
  2. Leaking sight Glass!?!!
    By The MG Pony in forum Fundamentals
    Replies: 10
    Last Post: 19-04-2007, 06:09 AM
  3. liquid line sight glass mystery
    By austech in forum Technical Discussions
    Replies: 19
    Last Post: 18-07-2006, 08:16 PM
  4. Sight Glass Located
    By Abe in forum Trouble Shooting
    Replies: 3
    Last Post: 22-01-2002, 01:22 AM
  5. Sight Glass,
    By Abe in forum Trouble Shooting
    Replies: 4
    Last Post: 03-08-2001, 08:36 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •