    Hye all,
    I would like to know how to calculate the capacity (Q = m X c X delta T ) if the flow rate of the refrigerant or chilled water can not be determined?Any suggestion or thought are much appreciated!
    ThanX!
    Aug 2009
    New Zealand
    2,554
    Re: Chilled Water/Refrigerant Flow rate
    Very strange question,
    I presume that this is an existing installation?
    If so check your refrigerant pressures , temps and current.
    transpose against compressor manufactures data. Duty.
    Then check your TD across the evap on the water side, do the calcs using the the comp duty, to give water flow.
    If water is pumped check pump pressures and current against manufactures data, to back up water flow rate.
    Oct 2009
    Malaysia
    sorry the question not in detail..
    yeah,this is an existing chiller system where they not installed any flow metering device at the pipeline,so i could not check the flow rate of chilled water..
    actually,i wanted to do energy assesment of the chiller. I need to calculate it's performance (actual) and compare with the design condition.
    since there is no way of getting the flowrate of the chilled water,maybe there are some other ideas or assumption can be made like assumming the actual flowrate is same with the design flow rate.
    BTW,thanks Mad Fridgie for the reply!
    Aug 2009
    New Zealand
    2,554
    Quote Originally Posted by schiZ0prEni View Post
    You can purchase (hire) a non contact flow meter
    This could give actual flows.
    11,025
    Or, if the machine can be stopped and partially stripped, you could check the duty of the expansion valve.
    Jun 2001
    N.Ireland
    1,630
    Hello
    you could hire out an ultrasonic flow meter and measure the flow without breaking into the system, or break into the system a fit a flow meter.
    Kind Regards Andy
    Aug 2003
    Netherlands
    49
    620
    Get the chiller running in full load.
    Make sure its running as near as possible to the design setpoint and than just fill in the data you have into the formula. Take 4.18 kj/kg for water, the measured dT across the evaporator and the design capacity in kW. You can calculate the flow rate in l/s!
    If it ain't broke, don't fix it!
    Oct 2003
    5,630
    Take AMP readings and at the same time DP over the pump and look in the pump chart to determine flow.
    Oct 2003
    5,630
    Andy, you don't have to brake in physical in the pipes?
    Is the material of the pipe important in this measurement?
    11,025
    Peter, you can normally use them on most pipe types, they depend on the water being slightly dirty.
    I've used them in the past quite successfully.
    See some models here....
    http://www.rshydro.co.uk/Portable-c-321.html
    Oct 2003
    5,630
    I always thought you had to make at least 2 holes in the tube. I could have use those in the past where I had some cases where flow needed to be measured.
    I already searched yesterday on the net and I found interesting information.
    Learned again something here. Thanks
    4,710
    Peter.
    It's true isn't it that we never know it all.
    May I just add to the excellent info the guys have already given you.
    That the larger ones we sometimes use, have a programmable setting.
    Where you select the material the pipe is made from.
    The ones we have are so expensive that they are normally "shared" across several depots.
    Because we have Marine Guys we have been known to borrow theirs!
    cheers Grizzly
    Jun 2001
    N.Ireland
    1,630
    Hi Peter
    I can see i've been beaten to the answers
    Being tight I normally don't use then, prefering to use the pump curves.
    I have now opted to use either an oriface plate or a double regulating valve with manometer connections on all new chilled water jobs. Yet to buy a differential pressure manometer, but we can hire one.
    Kind Regards Andy
    pnkrishna08's Avatar
    pnkrishna08 Guest
    hi..i need cooling load formulae
  1. Flow Rate through Fan Coil Unit
    By deepu in forum Air Conditioning
    Last Post: 21-07-2009, 06:42 AM
  2. How to calculate the Flow rate of air blower(centrifugal type)
    By nadeemnisa in forum Technical Speculations
    Last Post: 26-06-2009, 07:53 AM
  3. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Last Post: 10-03-2009, 01:03 PM
  4. high volume flow rate
    By cakabo28 in forum Technical Discussions
    Last Post: 04-10-2007, 03:41 AM
  5. Shell/Tube flow rate?
    By reggie in forum Fundamentals
    Last Post: 17-11-2002, 05:41 PM