    Chilled Water/Refrigerant Flow rate



    Hye all,

    I would like to know how to calculate the capacity (Q = m X c X delta T ) if the flow rate of the refrigerant or chilled water can not be determined?Any suggestion or thought are much appreciated!

    ThanX!



  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Chilled Water/Refrigerant Flow rate

    Very strange question,
    I presume that this is an existing installation?
    If so check your refrigerant pressures , temps and current.
    transpose against compressor manufactures data. Duty.
    Then check your TD across the evap on the water side, do the calcs using the the comp duty, to give water flow.
    If water is pumped check pump pressures and current against manufactures data, to back up water flow rate.

  3. #3
    Join Date
    Oct 2009
    Location
    Malaysia
    Age
    37
    Posts
    16
    Rep Power
    0

    Re: Chilled Water/Refrigerant Flow rate

    sorry the question not in detail..
    yeah,this is an existing chiller system where they not installed any flow metering device at the pipeline,so i could not check the flow rate of chilled water..

    actually,i wanted to do energy assesment of the chiller. I need to calculate it's performance (actual) and compare with the design condition.

    since there is no way of getting the flowrate of the chilled water,maybe there are some other ideas or assumption can be made like assumming the actual flowrate is same with the design flow rate.

    BTW,thanks Mad Fridgie for the reply!

  4. #4
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Chilled Water/Refrigerant Flow rate

    Quote Originally Posted by schiZ0prEni View Post
    sorry the question not in detail..
    yeah,this is an existing chiller system where they not installed any flow metering device at the pipeline,so i could not check the flow rate of chilled water..

    actually,i wanted to do energy assesment of the chiller. I need to calculate it's performance (actual) and compare with the design condition.

    since there is no way of getting the flowrate of the chilled water,maybe there are some other ideas or assumption can be made like assumming the actual flowrate is same with the design flow rate.

    BTW,thanks Mad Fridgie for the reply!
    You can purchase (hire) a non contact flow meter
    This could give actual flows.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Chilled Water/Refrigerant Flow rate

    Or, if the machine can be stopped and partially stripped, you could check the duty of the expansion valve.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Chilled Water/Refrigerant Flow rate

    Quote Originally Posted by schiZ0prEni View Post
    sorry the question not in detail..
    yeah,this is an existing chiller system where they not installed any flow metering device at the pipeline,so i could not check the flow rate of chilled water..

    actually,i wanted to do energy assesment of the chiller. I need to calculate it's performance (actual) and compare with the design condition.

    since there is no way of getting the flowrate of the chilled water,maybe there are some other ideas or assumption can be made like assumming the actual flowrate is same with the design flow rate.

    BTW,thanks Mad Fridgie for the reply!

    Hello

    you could hire out an ultrasonic flow meter and measure the flow without breaking into the system, or break into the system a fit a flow meter.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  7. #7
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Chilled Water/Refrigerant Flow rate

    Get the chiller running in full load.
    Make sure its running as near as possible to the design setpoint and than just fill in the data you have into the formula. Take 4.18 kj/kg for water, the measured dT across the evaporator and the design capacity in kW. You can calculate the flow rate in l/s!
    If it ain't broke, don't fix it!

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Chilled Water/Refrigerant Flow rate

    Take AMP readings and at the same time DP over the pump and look in the pump chart to determine flow.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Chilled Water/Refrigerant Flow rate

    Andy, you don't have to brake in physical in the pipes?
    Is the material of the pipe important in this measurement?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Chilled Water/Refrigerant Flow rate

    Peter, you can normally use them on most pipe types, they depend on the water being slightly dirty.

    I've used them in the past quite successfully.

    See some models here....
    http://www.rshydro.co.uk/Portable-c-321.html
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Chilled Water/Refrigerant Flow rate

    I always thought you had to make at least 2 holes in the tube. I could have use those in the past where I had some cases where flow needed to be measured.
    I already searched yesterday on the net and I found interesting information.
    Learned again something here. Thanks
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Chilled Water/Refrigerant Flow rate

    Quote Originally Posted by Peter_1 View Post
    I always thought you had to make at least 2 holes in the tube. I could have use those in the past where I had some cases where flow needed to be measured.
    I already searched yesterday on the net and I found interesting information.
    Learned again something here. Thanks
    Peter.
    It's true isn't it that we never know it all.
    May I just add to the excellent info the guys have already given you.
    That the larger ones we sometimes use, have a programmable setting.
    Where you select the material the pipe is made from.
    The ones we have are so expensive that they are normally "shared" across several depots.
    Because we have Marine Guys we have been known to borrow theirs!
    cheers Grizzly

  13. #13
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Chilled Water/Refrigerant Flow rate

    Quote Originally Posted by Peter_1 View Post
    Andy, you don't have to brake in physical in the pipes?
    Is the material of the pipe important in this measurement?
    Hi Peter
    I can see i've been beaten to the answers

    Being tight I normally don't use then, prefering to use the pump curves.
    I have now opted to use either an oriface plate or a double regulating valve with manometer connections on all new chilled water jobs. Yet to buy a differential pressure manometer, but we can hire one.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  14. #14
    pnkrishna08's Avatar
    pnkrishna08 Guest

    Re: Chilled Water/Refrigerant Flow rate

    hi..i need cooling load formulae

Similar Threads

  1. Flow Rate through Fan Coil Unit
    By deepu in forum Air Conditioning
    Replies: 4
    Last Post: 21-07-2009, 06:42 AM
  2. How to calculate the Flow rate of air blower(centrifugal type)
    By nadeemnisa in forum Technical Speculations
    Replies: 9
    Last Post: 26-06-2009, 07:53 AM
  3. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  4. high volume flow rate
    By cakabo28 in forum Technical Discussions
    Replies: 5
    Last Post: 04-10-2007, 03:41 AM
  5. Shell/Tube flow rate?
    By reggie in forum Fundamentals
    Replies: 4
    Last Post: 17-11-2002, 05:41 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •