Heat Pump Design
Can anybody tell me that for active defrost in heat pumps (reversing the cycle to defrost the frost/ice), there will be absolutely a requirement for accumulator. The compressor for the heat pump system is scroll. The heat pump is a water to air system. Evaporator is heated by ambient air and condenser is cooled by water.
-
04-11-2008, 03:40 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Heat Pump Design
No, there is no absolute requirement for accumulator if total charge of system is not higher then compressor manufacturer recommends.
-
13-11-2008, 03:12 AM #3
Re: Heat Pump Design
Certainly, there is absolute requirement for accumulator. Because the plate heat exchanger can only contain a little liquid refrigerant, and the working conditions in different seasons vary a lot. So there must have a accumulator to contain the surplus refrigerant that is not needed in refrigeration cycle during lower loads.
-
13-11-2008, 08:05 AM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Heat Pump Design
Nothing is absolute:
Accumulator is considered a Copeland
specification requirement on all air source heat
pumps unless slugging and floodback test under
low ambient and defrost conditions are run and
satisfactorily passed to prove that operation without
an accumulator is acceptable.
Last edited by nike123; 13-11-2008 at 08:18 AM.
-
13-11-2008, 01:55 PM #5
Re: Heat Pump Design
Accumilators in the suction line are not absolute if the system is sized corectley.
They tend to have them fitted with heatpumps because the cond will be larger
than the evap and when on reverse cycle there is the possiblity of liquid flooding
back to the comp. Some systems use TEV's and some use Capilaries.
They all require different requirements. TEV's need liquid storage, whether that
is in the receiver or backed up in the condenser. Capilaries need to be critical charged.
It is horse's for course's and you can never say you absolutly need do do somthing.
taz.Last edited by taz24; 13-11-2008 at 01:58 PM.
-
13-11-2008, 02:57 PM #6
-
22-03-2009, 03:49 PM #7
-
22-03-2009, 05:04 PM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
22-03-2009, 05:30 PM #9
Re: Heat Pump Design
^ Thanks very much.
-
22-03-2009, 06:25 PM #10
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Heat Pump Design
Some information could be found here!
http://www.hvacrinfo.com/ae_index.htm
-
22-03-2009, 09:00 PM #11
Re: Heat Pump Design
Thanks so much for the link - that is incredibly helpful. Much obliged.
Similar Threads
-
Design heat pump for a pool
By rolandh in forum Heat PumpsReplies: 10Last Post: 23-09-2010, 10:50 AM -
Capacity control
By sparrow in forum TrainingReplies: 44Last Post: 18-01-2010, 07:49 PM -
Heat Pump Design Model on the Web
By nike123 in forum Heat PumpsReplies: 1Last Post: 07-05-2008, 11:21 AM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM