    Smile Heat Pump Design



    Can anybody tell me that for active defrost in heat pumps (reversing the cycle to defrost the frost/ice), there will be absolutely a requirement for accumulator. The compressor for the heat pump system is scroll. The heat pump is a water to air system. Evaporator is heated by ambient air and condenser is cooled by water.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Heat Pump Design

    No, there is no absolute requirement for accumulator if total charge of system is not higher then compressor manufacturer recommends.

  3. #3
    Join Date
    Aug 2006
    Location
    China
    Age
    55
    Posts
    52
    Rep Power
    18

    Re: Heat Pump Design

    Certainly, there is absolute requirement for accumulator. Because the plate heat exchanger can only contain a little liquid refrigerant, and the working conditions in different seasons vary a lot. So there must have a accumulator to contain the surplus refrigerant that is not needed in refrigeration cycle during lower loads.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Heat Pump Design

    Quote Originally Posted by yangchenchen View Post
    Certainly, there is absolute requirement for accumulator. Because the plate heat exchanger can only contain a little liquid refrigerant, and the working conditions in different seasons vary a lot. So there must have a accumulator to contain the surplus refrigerant that is not needed in refrigeration cycle during lower loads.
    Nothing is absolute:
    Accumulator is considered a Copeland
    specification requirement on all air source heat
    pumps unless slugging and floodback test under
    low ambient and defrost conditions are run and
    satisfactorily passed to prove that operation without
    an accumulator is acceptable
    .
    http://www.hvacrinfo.com/cope_ae_bulletins/TAE1243.PDF


    Quote Originally Posted by yangchenchen View Post
    Every model compressor recommend the refrigerant mass charging .
    Quote Originally Posted by nike123 View Post
    No, there is no absolute requirement for accumulator if total charge of system is not higher then compressor manufacturer recommends.
    Last edited by nike123; 13-11-2008 at 08:18 AM.

  5. #5
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Heat Pump Design

    Quote Originally Posted by yangchenchen View Post
    Certainly, there is absolute requirement for accumulator. Because the plate heat exchanger can only contain a little liquid refrigerant, and the working conditions in different seasons vary a lot. So there must have a accumulator to contain the surplus refrigerant that is not needed in refrigeration cycle during lower loads.

    Accumilators in the suction line are not absolute if the system is sized corectley.
    They tend to have them fitted with heatpumps because the cond will be larger
    than the evap and when on reverse cycle there is the possiblity of liquid flooding
    back to the comp. Some systems use TEV's and some use Capilaries.
    They all require different requirements. TEV's need liquid storage, whether that
    is in the receiver or backed up in the condenser. Capilaries need to be critical charged.

    It is horse's for course's and you can never say you absolutly need do do somthing.

    taz.
    Last edited by taz24; 13-11-2008 at 01:58 PM.

  6. #6
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Heat Pump Design

    Quote Originally Posted by yangchenchen View Post
    Certainly, there is absolute requirement for accumulator. Because the plate heat exchanger can only contain a little liquid refrigerant, and the working conditions in different seasons vary a lot. So there must have a accumulator to contain the surplus refrigerant that is not needed in refrigeration cycle during lower loads.
    I guess my heat pump at home was manufactured wrong because there is no accumulator on it. Just kidding, there is no requirement for a accumulator for a heat pump, its up to the manufacturer and the the design of the heat pump.

  7. #7
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Heat Pump Design

    Quote Originally Posted by nike123 View Post
    No, there is no absolute requirement for accumulator if total charge of system is not higher then compressor manufacturer recommends.
    Do you perhaps have links to what a Copeland would recommend as total system charge, for Copeland scroll series compressors?

    The ZR & ZH series in particular.

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Heat Pump Design

    Quote Originally Posted by desA View Post
    Do you perhaps have links to what a Copeland would recommend as total system charge, for Copeland scroll series compressors?

    The ZR & ZH series in particular.
    I think that i stated in catalog, but I need to check.

  9. #9
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Heat Pump Design

    ^ Thanks very much.

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Heat Pump Design

    Some information could be found here!
    http://www.hvacrinfo.com/ae_index.htm

  11. #11
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Heat Pump Design

    Thanks so much for the link - that is incredibly helpful. Much obliged.

Similar Threads

  1. Design heat pump for a pool
    By rolandh in forum Heat Pumps
    Replies: 10
    Last Post: 23-09-2010, 10:50 AM
  2. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  3. Heat Pump Design Model on the Web
    By nike123 in forum Heat Pumps
    Replies: 1
    Last Post: 07-05-2008, 11:21 AM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •