Results 1 to 11 of 11
    behmin's Avatar
    behmin Guest
    Smile Heat Pump Design
    Can anybody tell me that for active defrost in heat pumps (reversing the cycle to defrost the frost/ice), there will be absolutely a requirement for accumulator. The compressor for the heat pump system is scroll. The heat pump is a water to air system. Evaporator is heated by ambient air and condenser is cooled by water.
    Split Croatia
    57
    6,151
    36
    Re: Heat Pump Design
    No, there is no absolute requirement for accumulator if total charge of system is not higher then compressor manufacturer recommends.
    China
    55
    52
    Certainly, there is absolute requirement for accumulator. Because the plate heat exchanger can only contain a little liquid refrigerant, and the working conditions in different seasons vary a lot. So there must have a accumulator to contain the surplus refrigerant that is not needed in refrigeration cycle during lower loads.
    Split Croatia
    57
    6,151
    36
    Quote Originally Posted by yangchenchen View Post
    Nothing is absolute:
    Accumulator is considered a Copeland
    specification requirement on all air source heat
    pumps unless slugging and floodback test under
    low ambient and defrost conditions are run and
    satisfactorily passed to prove that operation without
    an accumulator is acceptable
    http://www.hvacrinfo.com/cope_ae_bulletins/TAE1243.PDF
    Every model compressor recommend the refrigerant mass charging .
    Oct 2006
    1,843
    21
    Accumilators in the suction line are not absolute if the system is sized corectley.
    They tend to have them fitted with heatpumps because the cond will be larger
    than the evap and when on reverse cycle there is the possiblity of liquid flooding
    back to the comp. Some systems use TEV's and some use Capilaries.
    They all require different requirements. TEV's need liquid storage, whether that
    is in the receiver or backed up in the condenser. Capilaries need to be critical charged.
    It is horse's for course's and you can never say you absolutly need do do somthing.
    taz.
    Jan 2006
    Valrico, Florida
    509
    I guess my heat pump at home was manufactured wrong because there is no accumulator on it. Just kidding, there is no requirement for a accumulator for a heat pump, its up to the manufacturer and the the design of the heat pump.
    Mar 2009
    KZN, South Africa
    64
    2,212
    Do you perhaps have links to what a Copeland would recommend as total system charge, for Copeland scroll series compressors?
    The ZR & ZH series in particular.
    Split Croatia
    57
    6,151
    36
    Quote Originally Posted by desA View Post
    I think that i stated in catalog, but I need to check.
    Mar 2009
    KZN, South Africa
    64
    2,212
    ^ Thanks very much.
    Split Croatia
    57
    6,151
    36
    Some information could be found here!
    http://www.hvacrinfo.com/ae_index.htm
    Mar 2009
    KZN, South Africa
    64
    2,212
    Thanks so much for the link - that is incredibly helpful. Much obliged.
  1. Design heat pump for a pool
    By rolandh in forum Heat Pumps
    Last Post: 23-09-2010, 10:50 AM
  2. Capacity control
    By sparrow in forum Training
    Last Post: 18-01-2010, 07:49 PM
  3. Heat Pump Design Model on the Web
    By nike123 in forum Heat Pumps
    Last Post: 07-05-2008, 11:21 AM
  4. frostles heat pump