    Electric motors at service factor



    Hi guys:

    Does anyone have experience or input on running large motors @ service factor. My motor guru's say as long as I am sufficiently cooling the windings, go for it. I expect some penalty in insulation service life on the windings, but can accept that with my operating parameters IE <1000 hrs/yr.

    thanks

    Dan



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Electric motors at service factor

    Your motor guru's right.

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Electric motors at service factor

    I would tend to agree with the motor shop with one caveat. This being, the motor is operated at sea level or not too much above it. My logic for this is as follows; as the elevation increases, the air density decreases. The lower air density will result in less mass flow available for motor cooling. Remember the motor fan provided for cooling only pushes CFM, which is constant. The mass flow decreases with higher elevations. And mass flow is what does the cooling.

    If the operation is in the service factor and the motor is cooled by reasonably cool air then this is same principle as motors on evaporators in blast freezers. They too are often overloaded, but don't burnout because of the cooling provided by the extremely cold air.
    If all else fails, ask for help.


  4. #4
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Electric motors at service factor

    Quote Originally Posted by dglaab View Post
    Hi guys:

    Does anyone have experience or input on running large motors @ service factor. My motor guru's say as long as I am sufficiently cooling the windings, go for it. I expect some penalty in insulation service life on the windings, but can accept that with my operating parameters IE <1000 hrs/yr.

    thanks

    Dan
    Do you have high head pressue?

  5. #5
    Join Date
    Nov 2008
    Location
    alaska
    Age
    58
    Posts
    11
    Rep Power
    0

    Re: Electric motors at service factor

    No, we are actually running 125 psi or less. This question is more of a technical question than an operational one

    thanks

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Electric motors at service factor

    Another way to look at this is by way of an example:

    If the compressor requires 100 HP I would rather run a 125 HP motor with a 1.0 service factor at 100 HP rather than run a 100 motor with a 125 HP load on it (if it had a 1.25 SF).

    I just made up the numbers but you see the difference.
    If all else fails, ask for help.


  7. #7
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Electric motors at service factor

    I think that all el. motor designed for certain maximum load at certain maximum air temperature. If air temperature is cooler, then design temperature, you can go carefully into the service factor. Usually, we need this overload during summer operation at extremly hot air temperature.

Similar Threads

  1. ode to a service engineer
    By Tycho in forum Chit Chat & Service Stories
    Replies: 5
    Last Post: 09-10-2009, 10:13 PM
  2. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM
  3. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 05:11 PM
  4. Electric Motors - Fans - blades
    By MrReds in forum Refrigeration Books
    Replies: 5
    Last Post: 23-11-2006, 07:56 PM
  5. Hot Gas vs. Electric Defrost
    By herefishy in forum Technical Discussions
    Replies: 26
    Last Post: 08-03-2005, 07:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •