    Iarp Chiller



    IARP ECX600 Upright chiller which according to the customer has been loosing gas every couple of months. He has been spending a fortune on people coming over to 'top it up' for the last three years!!!

    I pressure tested and found the Evaporator has four very small pin hole leaks. The evaporator is badly corroded and needs replacing. Has anyone replaced one? Looks pretty awkward!

    Not sure who supplies IARP spares either so any help on that would be appreciated.

    Unit possibly 10 years+ old

    Many Thanks

    Lucas.



  2. #2
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Iarp chillers

    Hi lucas

    Yes familiar with the cabinet,where on the evaparator are the leaks can they be repaired ?.I have repaired leaks in the past on the knuckles and pipework.If not spares available from:

    GH england
    chipenham,
    wiltshire,
    (01249)449300


    Regards Mark

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46
    hi lucas,

    you can also get information at http://www.iarp.it/Cater-prod_ECX_600.html#

    whec such problems start, it is best to install a new evaporator and if the original is of bad qulity, you can have a new one made by any coil manufacturer and it should be cheeper.


    chemi

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34
    Is this a tube in tube or a plate evaporator or are we perhaps talking abouth the condensor?

  5. #5
    Join Date
    Sep 2003
    Location
    UK
    Posts
    54
    Rep Power
    21

    Thanks

    Thanks for all info.

    Three of the leaks are repairable but the forth isn't due to its position.

    The Evap is badly corroded so even if repair was possible who knows how long it would be before more leaks appeared.

    Thanks all.

Similar Threads

  1. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  2. DIY aquarium chiller
    By BarraCuda in forum Technical Discussions
    Replies: 18
    Last Post: 06-10-2010, 11:02 PM
  3. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  4. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM
  5. Chiller
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 08-04-2006, 02:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •