    VRV outdoor unit location



    Hi,

    We are working on a VRV system (Myself for first time).

    Wanted to know minimum clearance required between wall and outdoor unit for having proper amount of air volume flow rate through outdoor units.

    Units are located on an exterior overhang and one side is wall while other three sides are open.

    Thanks

    Vijay Kumar


    Vijay Kumar
    HVAC Design Engineer

    BMCPL

    "The more you sweat in peace less you bleed in war"

  2. #2
    Join Date
    May 2007
    Location
    Moscow
    Age
    40
    Posts
    82
    Rep Power
    17

    Re: VRV outdoor unit location

    Minimum clearence is 300 mm in this case. And 400 mm between 2 outdoors. This information should be in Installation Manual of VRV.