charging system with liquid refrigerant
Hello, everybody
can someone please tell me if it is possible to charge liquid refrigerant from the suction valve and what are the steps to follow.
thanks very much in advance.
-
31-10-2008, 09:42 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: charging system with liquid refrigerant
Yes, it is possible! Safest way is to charge with Kwik-charge device.
Second way is if you have manifolds with sight glass you could throttle valve to make sure that there is no liquid refrigerant in glass.
Third option is to charge small amounts of liquid (2-5% of total charge) and then wait some time that refrigerant evaporate in system before adding more liquid refrigerant!
Or you could use 2m capillary for HP/LP controls as metering device if system is big enough!Last edited by nike123; 31-10-2008 at 09:49 PM.
-
01-11-2008, 07:15 AM #3
Re: charging system with liquid refrigerant
Depends a little bit on the size of the system: if you have a household compressor, be careful.
If you have a 30 HP, then you can connect your manifold hoses direct to the suction and charge continuously liquid without any problem.
If you have a 1HP to 3 +/- HP, open your manifold for 5 to 10 seconds and then wait for 5 to 10 seconds. Monitor carefully the noise of the compressor.
Suction gas cooled compressor can be charged mostly with liquid without problem because the refrigerant flashes off on the warm windings.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
01-11-2008, 06:12 PM #4
Re: charging system with liquid refrigerant
do we not have to charge only liquid whit the new refrigs like R407c & R410a ??
and if we do it,is it not VERY VERY carefully on the amount of charging???
Ice
ps;Peter,got the papers and price from vinçotte...mucho mucho dinero's
-
01-11-2008, 06:16 PM #5
Re: charging system with liquid refrigerant
Icecube, you also have to go to school to do your exams, apart from the company registration.
Met one of the Israelian moderators in Gent, Chemi. He was her for some days.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
01-11-2008, 06:30 PM #6
Re: charging system with liquid refrigerant
so now you telling me !!! would be pleased to meat Chemi in person. maybe next time.
i now about the school,but going to whait until next year 2009. financial reasons.
Ice
-
01-11-2008, 06:51 PM #7
Re: charging system with liquid refrigerant
I only knew it the same day I met him.
He was here for a visit at Petersime in Zulte.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
01-11-2008, 07:00 PM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
01-11-2008, 07:46 PM #9
Re: charging system with liquid refrigerant
Rhodia - gas manufacturer n°1 in France - says this statement is retrieved.
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
02-11-2008, 04:18 PM #10
Re: charging system with liquid refrigerant
how dos he prove it ?? maybe on small cylinders white a total of 13kg. but on the bigger ones like 80 & more, i do have mi doubts.
Nike123, thats what i meant by filling on liquid,just don't let the liquid reach the compressor.
Ice
-
02-11-2008, 04:27 PM #11
Re: charging system with liquid refrigerant
It was an official statement of the manufacturer themselves, so I don't think they will spread this news if it isn't true.
Because this statement can turn back right in their face and used against them, I believe it.
Some statements/manipulations/facts which were taken as the only truth sometimes becomes revised because practical use/field experience learned us the opposite.
Same for a manifold, may you use an R22 manifold on an R134a installation?
When R134a was fist introduced, we all had double manifolds, and we were learned that if you connected your R12 manifold on an R134a installations that the R134a compressor should burn in a short time afterwards.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
02-11-2008, 04:33 PM #12
Re: charging system with liquid refrigerant
so we no longer have to fill in liquid for the mixt gasses. nice to now. so we will no longer have to worry about the compressors on liquid filling.thats makes things allot easier .
Ice
-
02-11-2008, 04:34 PM #13
Re: charging system with liquid refrigerant
for the manifolds it was obvious,the oil!!
always check the cind of oil the system is working on.
Ice
Similar Threads
-
Liquid receiver
By Renato RR in forum FundamentalsReplies: 134Last Post: 02-03-2011, 06:55 AM -
automating a chilled brine refrigeration system using ammonia refrigerant
By luciom in forum IndustrialReplies: 29Last Post: 02-10-2008, 09:48 PM -
Refrigerant Charging
By sparrow in forum TrainingReplies: 4Last Post: 27-09-2008, 09:11 AM -
Best way to sense level of liquid refrigerant in receiver?
By star882 in forum FundamentalsReplies: 2Last Post: 16-11-2005, 05:34 PM