    charging system with liquid refrigerant



    Hello, everybody
    can someone please tell me if it is possible to charge liquid refrigerant from the suction valve and what are the steps to follow.
    thanks very much in advance.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: charging system with liquid refrigerant

    Yes, it is possible! Safest way is to charge with Kwik-charge device.
    Second way is if you have manifolds with sight glass you could throttle valve to make sure that there is no liquid refrigerant in glass.
    Third option is to charge small amounts of liquid (2-5% of total charge) and then wait some time that refrigerant evaporate in system before adding more liquid refrigerant!
    Or you could use 2m capillary for HP/LP controls as metering device if system is big enough!
    Last edited by nike123; 31-10-2008 at 09:49 PM.

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: charging system with liquid refrigerant

    Depends a little bit on the size of the system: if you have a household compressor, be careful.
    If you have a 30 HP, then you can connect your manifold hoses direct to the suction and charge continuously liquid without any problem.
    If you have a 1HP to 3 +/- HP, open your manifold for 5 to 10 seconds and then wait for 5 to 10 seconds. Monitor carefully the noise of the compressor.
    Suction gas cooled compressor can be charged mostly with liquid without problem because the refrigerant flashes off on the warm windings.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: charging system with liquid refrigerant

    do we not have to charge only liquid whit the new refrigs like R407c & R410a ??
    and if we do it,is it not VERY VERY carefully on the amount of charging???

    Ice

    ps;Peter,got the papers and price from vinçotte...mucho mucho dinero's

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: charging system with liquid refrigerant

    Icecube, you also have to go to school to do your exams, apart from the company registration.
    Met one of the Israelian moderators in Gent, Chemi. He was her for some days.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: charging system with liquid refrigerant

    so now you telling me !!! would be pleased to meat Chemi in person. maybe next time.

    i now about the school,but going to whait until next year 2009. financial reasons.

    Ice

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: charging system with liquid refrigerant

    I only knew it the same day I met him.
    He was here for a visit at Petersime in Zulte.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: charging system with liquid refrigerant

    Quote Originally Posted by icecube51 View Post
    do we not have to charge only liquid whit the new refrigs like R407c & R410a ??
    and if we do it,is it not VERY VERY carefully on the amount of charging???
    We should only draw liquid from charging cylinder to avoid change in aspect of substances.
    Then, after liquid is drawn from cylinder, is when we could (and should) evaporate it!

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: charging system with liquid refrigerant

    Rhodia - gas manufacturer n°1 in France - says this statement is retrieved.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: charging system with liquid refrigerant

    how dos he prove it ?? maybe on small cylinders white a total of 13kg. but on the bigger ones like 80 & more, i do have mi doubts.
    Nike123, thats what i meant by filling on liquid,just don't let the liquid reach the compressor.

    Ice

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: charging system with liquid refrigerant

    It was an official statement of the manufacturer themselves, so I don't think they will spread this news if it isn't true.
    Because this statement can turn back right in their face and used against them, I believe it.
    Some statements/manipulations/facts which were taken as the only truth sometimes becomes revised because practical use/field experience learned us the opposite.

    Same for a manifold, may you use an R22 manifold on an R134a installation?

    When R134a was fist introduced, we all had double manifolds, and we were learned that if you connected your R12 manifold on an R134a installations that the R134a compressor should burn in a short time afterwards.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: charging system with liquid refrigerant

    so we no longer have to fill in liquid for the mixt gasses. nice to now. so we will no longer have to worry about the compressors on liquid filling.thats makes things allot easier .

    Ice

  13. #13
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: charging system with liquid refrigerant

    for the manifolds it was obvious,the oil!!
    always check the cind of oil the system is working on.
    Ice

Similar Threads

  1. Liquid receiver
    By Renato RR in forum Fundamentals
    Replies: 134
    Last Post: 02-03-2011, 06:55 AM
  2. Replies: 29
    Last Post: 02-10-2008, 09:48 PM
  3. Refrigerant Charging
    By sparrow in forum Training
    Replies: 4
    Last Post: 27-09-2008, 09:11 AM
  4. Replies: 2
    Last Post: 16-11-2005, 05:34 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •