    Daikin control wiring



    Two questions on the control wiring for a Daikin VRV-S system.

    Is it possible to run either the Transmission or Remote Control wiring through a third party float switch that will be attached to a condensate overflow pan? Assuming it is acceptable, is there a better cable to use - Transmission or Remote Control?

    Also, is it acceptable to have splices in any of this control wiring? If so, is there a preferred method for reconnecting - wire nuts, bullet connectors?

    Many thanks.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin control wiring

    I think that if you interrupt the control wiring in any way you will end up with a fault condition that will shut down the whole system.

    As for wire connectors, as long as they are good quality and maintain electrical integrity then they should be OK.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin control wiring

    Quote Originally Posted by Brian_UK View Post
    I think that if you interrupt the control wiring in any way you will end up with a fault condition that will shut down the whole system.

    As for wire connectors, as long as they are good quality and maintain electrical integrity then they should be OK.

    Thank you Brian.

    So running control wiring through any type of micro switch would cause a fault. Is there a way to stop a indoor ducted unit if condensate does start dripping from it into a catch pan placed under it?

    The placement of the indoor ducted air handlers is such that it would be a lot easier to pre-wire them and just have a short section of wiring coming out of it that we would then connect to when the unit is put into place. This would be for the tranmission and remote control wiring. The easiest way to connect would be with simple wire nuts but if that is considered less than acceptable for a long term solution we could do it with another connection type. Just wondered if there was any exerience that would direct us.

  4. #4
    Join Date
    Dec 2006
    Location
    London & Surrounding Counties
    Posts
    122
    Rep Power
    18

    Re: Daikin control wiring

    Wouldn't it be easier just to use the high level alarm switch on the condensate pump cut the mains power to the indoor unit? I realise it's a VRV and that this could generate a fault code, but it shouldn't shut down the entire system surely. If for example your using a central station to control each indoor unit then usually the controller would prompt the fault on the one indoor unit based in reflection of it's unit address??

    J

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin control wiring

    If you break the comms cable through a high float switch on a condensate pump you will generate a U4 fault.

    if you break the mains to a fan coil you will cause the whole system to fault/stop.

    The better way to do it is to break the small wire high level float connection on to the pcb from the lift pump and wire your external high level float in series. This will generate a HLF error on the affected fan coil only and allow the rest of the system to continue operating.

  6. #6
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin control wiring

    Quote Originally Posted by frank View Post
    If you break the comms cable through a high float switch on a condensate pump you will generate a U4 fault.

    if you break the mains to a fan coil you will cause the whole system to fault/stop.

    The better way to do it is to break the small wire high level float connection on to the pcb from the lift pump and wire your external high level float in series. This will generate a HLF error on the affected fan coil only and allow the rest of the system to continue operating.

    Perfect! Thanks.

  7. #7
    Join Date
    Nov 2007
    Location
    surrey
    Posts
    1
    Rep Power
    0

    Re: Daikin control wiring

    Inside of a ducted unit there is a green plug on the pcb this is the units very own high level cut out, you can splice into one side of this and it will only affect the unit in question. if you interupt the control wiring you can shut the whole system down for the sake of one pump....

  8. #8
    Join Date
    Sep 2007
    Location
    IL
    Age
    47
    Posts
    56
    Rep Power
    17

    Re: Daikin control wiring

    As was discussed here, you cannot interrupt neither the central control wiring (f1 f2) nor remote control wiring (p1 p2). However, if you like to interlock the operation of the indoor unit with other devices (pump, microswitch, motion sensor etc') you can use the dry contacts (t1 t2) on each indor in order to stop its operation.

  9. #9
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin control wiring

    Quote Originally Posted by Krondor View Post
    As was discussed here, you cannot interrupt neither the central control wiring (f1 f2) nor remote control wiring (p1 p2). However, if you like to interlock the operation of the indoor unit with other devices (pump, microswitch, motion sensor etc') you can use the dry contacts (t1 t2) on each indor in order to stop its operation.

    Thank you Krondor.

    I thought the T1 - T2 contacts were to be connected between any indoor unit and the outdoor so the outdoor could be stopped. If you short between T1 - T2 that will stop the individual indoor?

  10. #10
    Join Date
    Sep 2007
    Location
    IL
    Age
    47
    Posts
    56
    Rep Power
    17

    Re: Daikin control wiring

    yes, exactly

  11. #11
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin control wiring

    hey guys,
    don't use t1 or t2, why don't you use the high level alarm on the pcb, i think it is either x8a or x15a have a look at the wiring diagram, when this is open it will bring up an A3 fault which is a condensate high level alarm float switch which will shut the expansion valve and stop that unit only from cooling, if the unit you have has a condensate pump in it from manufacture, put your pumps high level switch in series with it.
    that way will be the best and easiest way to achieve it. when it faults it will point you in the right direction straight away.
    Last edited by brunstar; 23-11-2008 at 09:16 PM.

  12. #12
    roesli's Avatar
    roesli Guest

    Red face Re: Daikin control wiring

    yes too

  13. #13
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin control wiring

    Quote Originally Posted by brunstar View Post
    hey guys,
    don't use t1 or t2, why don't you use the high level alarm on the pcb, i think it is either x8a or x15a have a look at the wiring diagram, when this is open it will bring up an A3 fault which is a condensate high level alarm float switch which will shut the expansion valve and stop that unit only from cooling, if the unit you have has a condensate pump in it from manufacture, put your pumps high level switch in series with it.
    that way will be the best and easiest way to achieve it. when it faults it will point you in the right direction straight away.
    The x8a connection is listed as the float switch. Is this the connection you were thinking of wiring in series?

Similar Threads

  1. Daikin vrv control wiring
    By Jase in forum Air Conditioning
    Replies: 4
    Last Post: 23-03-2011, 04:01 AM
  2. Transmission wiring on Daikin VRV2
    By Markie in forum Air Conditioning
    Replies: 19
    Last Post: 25-09-2009, 06:24 PM
  3. Daikin VRV wiring adapter board
    By mchild in forum Air Conditioning
    Replies: 6
    Last Post: 24-11-2008, 11:02 AM
  4. Daikin A/C Cellar Temperature Control
    By Cellar Dweller in forum Fundamentals
    Replies: 15
    Last Post: 10-01-2008, 11:55 PM
  5. PIR Control for a Daikin
    By daddymac in forum Air Conditioning
    Replies: 3
    Last Post: 11-05-2007, 07:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •