    Re: Low pressure trip !!

    [quote=nike123;124368]
    Quote Originally Posted by oilzee View Post


    Who has installed that valves and for what reason? Are they are on other correctly working identical systems?
    we installed that valve according to supplier design so we had 1 year warranty for the compressor .
    For me this system was first time i did .For them , I have no idea .

  2. #2
    Join Date
    Aug 2008
    Location
    malaysia
    Posts
    76
    Rep Power
    16

    Re: Low pressure trip !!

    can i say , it was too much compressor oil in the system and affected low pressure trip !!

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Low pressure trip !!

    Quote Originally Posted by oilzee View Post
    can i say , it was too much compressor oil in the system and affected low pressure trip !!
    Did you checked oil level after you have full load for some time to allow proper oil return?

  4. #4
    Join Date
    Aug 2008
    Location
    malaysia
    Posts
    76
    Rep Power
    16

    Re: Low pressure trip !!

    Quote Originally Posted by nike123 View Post
    Did you checked oil level after you have full load for some time to allow proper oil return?
    after i released the oil yesterday , its maintain at 3/4 full level ( half and hour running , full load )
    but today i checked it was almost full .( no load )

  5. #5
    Join Date
    Aug 2008
    Location
    malaysia
    Posts
    76
    Rep Power
    16

    Re: Low pressure trip !!

    i m going to release some more oil by next tuesday and monitor the system .

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Low pressure trip !!

    What is that compressor model#?
    Am I correct when I say that you actualy have compressor pack comprised of 4x20Hp and 2x10Hp which together feeds evaporators in blast freezer thru 1 common liquid line.
    Or I get something wrong?

  7. #7
    Join Date
    Aug 2008
    Location
    malaysia
    Posts
    76
    Rep Power
    16

    Re: Low pressure trip !!

    Quote Originally Posted by nike123 View Post
    What is that compressor model#?
    Am I correct when I say that you actualy have compressor pack comprised of 4x20Hp and 2x10Hp which together feeds evaporators in blast freezer thru 1 common liquid line.
    Or I get something wrong?
    i m verry sorry because my infomation provided not clear
    actually our system has one compressor for one evaporator , that mean 4 sets of 20Hp refrigeration system ( 4 x liquid line , 4 x Suction Accumulator )

    So one system has 3 regulators then 4 system have 12 regulators .

    Compressor Model : 4G-20.2-40P( compressoroil already changed to ester oil )

    Evaporator : one unit is 29.8kw@6KTD

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  3. MV600 head pressure trip (ghost)
    By andre_fridge in forum Technical Discussions
    Replies: 9
    Last Post: 28-01-2006, 02:16 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •