Thread: mitsubishi fault indication
28-10-2008, 05:36 PM #1
Can anybody please tell me how to take a fault signal for a BMS system, from a city multi system with a G50 controller.
thanks in advance
Danny
28-10-2008, 07:01 PM #2
Re: mitsubishi fault indication
Can you give me the exact Model of the outdoor unit and the year etc...?
31-10-2008, 01:02 PM #3
G50 will support remote run & fault indication by using the CN2 plug on the back of the G50.
You need a 9 wire adaptor connect cable part No PAC-YG10HA-E available from MEUK or distributors. Its about £26.00.
You will need to wire it in with a relay to interface with the BMS.
02-11-2008, 12:30 AM #4
Depends of BMS branch, first you have to check if you can make an interface with this BMS with LonWorks or BAC Net, to make a preparation depending of this selection.
22-11-2008, 12:14 AM #5
Have you done this as I can't get it to work!!!!!! using the circuit diagram and the cable.
22-11-2008, 10:04 AM #6
G50 with PAC-YG10HA-E
The remote on / off fuction has to be activated at the G50.
Its is set in the Fuction setting page.
1/ get into the engineers mode.
2/ scroll through & select Fuction setting page.
3/ select the fuction you want to activate. In this instance you might be looking at using fuction number 6.
'perform on/off operation with level signal.
Suggest down load G50 manual for full details.
mitsubishi heavy split fault
By grovecoooling in forum Air ConditioningReplies: 7Last Post: 13-03-2011, 12:29 PM -
Mitsubishi VRF Fault
By marc5180 in forum Air ConditioningReplies: 5Last Post: 14-08-2008, 10:48 PM -
Fault code for a mitsubishi heavy
By marc5180 in forum Air ConditioningReplies: 7Last Post: 29-02-2008, 08:22 PM -
mitsubishi city multi fault code
By robin r33 gtr in forum Air ConditioningReplies: 5Last Post: 05-11-2007, 10:23 PM
