Thread: Eev failure
-
28-10-2008, 04:56 PM #1
Eev failure
hi,
i used a ALCO EX6 valve to control the system mass flow. the on-off frequency of compressor is 1circle/2min. when compressor is switched on, the valve should open and functionally control the mass flow;when compressor is switched off, the valve should be closed.
the failure is that sometimes the valve is out of control the mass flow. after reset the valve, the valve is ok.
thanks for your troubleshooting.
-
28-10-2008, 07:56 PM #2
Re: Eev failure
You say that the compressor switches on or off every 2 minutes, is that correct ?
If it is then it is a very short time for the compressor and also for the valve to start controlling properly.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
29-10-2008, 12:36 PM #3
Re: Eev failure
Try the link below for technical info. A digital input can be used to positively shut this valve. If the control input does not revert back to zero the valve may lose its reference. Alco literature explains better.
http://www.ecopeland.com/alcoliterat...section=alco27
Similar Threads
-
Carrier Transicold Container Problem
By Shamel in forum TransportReplies: 39Last Post: 23-01-2012, 11:23 PM -
temporary communication failure in supermarket rack controller
By racktech2008 in forum Supermarket RefrigerationReplies: 12Last Post: 27-04-2008, 09:17 AM -
defrost thermostat closed failure
By rkmoorthy in forum Trouble ShootingReplies: 2Last Post: 02-03-2008, 10:55 PM -
screw compressor failure
By aygul in forum Trouble ShootingReplies: 23Last Post: 09-12-2004, 09:09 AM -
Compressor failure...... cause
By herefishy in forum Technical SpeculationsReplies: 8Last Post: 06-12-2002, 12:15 AM