    Question COP and Refrigeration Capacity Caculation?



    Hi all,

    I'm new to RE as well as this field. However, I'm going to do the instrumentation to evaluate the COP & Refrigeration Capacity of a domestic heat pump (3kW cooling/1.5kW heating). Could someone please explain about the instrumentation & data that I need for the calculations?

    I'm getting confused as I have to do all the new things in a very short time.

    Thanks in advance



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,847
    Rep Power
    21

    Re: COP and Refrigeration Capacity Caculation?

    Quote Originally Posted by Uni View Post
    Hi all,

    I'm new to RE as well as this field. However, I'm going to do the instrumentation to evaluate the COP & Refrigeration Capacity of a domestic heat pump (3kW cooling/1.5kW heating). Could someone please explain about the instrumentation & data that I need for the calculations?

    I'm getting confused as I have to do all the new things in a very short time.

    Thanks in advance

    I dont use Wikipedia often but it may answer your questions.


    http://en.wikipedia.org/wiki/Coefficient_of_performance



    COP is only a ratio between energy in and energy out.
    The higher the energy out for the cost of the energy in = higher COP.

    Cheers taz

    .

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: COP and Refrigeration Capacity Caculation?

    Quote Originally Posted by Uni View Post
    Hi all,

    I'm new to RE as well as this field. However, I'm going to do the instrumentation to evaluate the COP & Refrigeration Capacity of a domestic heat pump (3kW cooling/1.5kW heating). Could someone please explain about the instrumentation & data that I need for the calculations?

    I'm getting confused as I have to do all the new things in a very short time.

    Thanks in advance
    I think the COP of this unit will be a negative value
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: COP and Refrigeration Capacity Caculation?

    Quote Originally Posted by Uni View Post
    Hi all,

    I'm new to RE as well as this field. However, I'm going to do the instrumentation to evaluate the COP & Refrigeration Capacity of a domestic heat pump (3kW cooling/1.5kW heating). Could someone please explain about the instrumentation & data that I need for the calculations?

    I'm getting confused as I have to do all the new things in a very short time.

    Thanks in advance
    Hi Uni have a look at this and try searching GOOGLE its where i got this
    http://www.winfridge.com/HSU-notes.html


    regards Norm
    My wife used to say you never listen to a word I say at least I think that what she said

  5. #5
    Join Date
    Jul 2007
    Location
    LIbya
    Age
    58
    Posts
    72
    Rep Power
    17

    Re: COP and Refrigeration Capacity Caculation?

    Hi Uni
    U can use temperature measurement and pressure gages to Calculate the COP and refrigerant capacity.
    Noori

  6. #6
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Lightbulb Re: COP and Refrigeration Capacity Caculation?

    Thanks for your quick responses.

    I am a student learning about instrumentation. I chopped the AC down and installed all the following stuffs:

    - Wet&dry bulb thermocouples at Evaporator (Indoor) Air Inlet & Outlet
    - Anemometer at the Evaporator
    - Pressure transducers + thermocouples to measure all the pressures and temperatures (evap in/out, cond in/out, suction/discharge, compressor shell)
    - Data logger & software
    - Nothing to measure mass flow rate


    So far, I have tried the charge tuning test. This helped me a lot to gain a better understanding about the system behavior. Now I want to move on to the COP & Capacity test.


    Generally said,

    C.O.P.= heat transferred/electricity input

    Electricity input can be measured by a Watt-meter, so I have it installed already.

    1. How do we measure the heat transferred?

    2. Is there any other practical method to do this?
    by using wet/dry bulb evap in/out temp and air flow (cube/hour) for example
    Someone used calorimeters, etc. which I do not understand.

    Please everyone, be more detailed. I'm really interested in this field


  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: COP and Refrigeration Capacity Caculation?

    Quote Originally Posted by Uni View Post

    2. Is there any other practical method to do this?
    by using wet/dry bulb evap in/out temp and air flow (cube/hour) for example
    Exactly that! You need entering air wet and dry bulb temperature (or dry bulb temperature and relative humidity) and leaving air wet and dry bulb temperature (or dry bulb temperature and relative humidity). Applying that to Mollier chart you should find enthalpy of entering and leaving air and you only need air density and air flow to calculate sensible and latent heat of that air in measure of time.
    Yo could easily calculate that with numerous versions Mollier chart software or by doing your own calculations.
    Last edited by nike123; 02-11-2008 at 06:55 AM.

  8. #8
    Join Date
    Feb 2001
    Location
    Doncaster, England
    Posts
    199
    Rep Power
    25

    Re: COP and Refrigeration Capacity Caculation?

    Hi Nike123,

    Applying that to Mollier chart
    don't you mean pschrometric chart?
    Tony

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: COP and Refrigeration Capacity Caculation?

    Quote Originally Posted by Tony View Post
    Hi Nike123,



    don't you mean pschrometric chart?
    Sorry, I mean Mollier diagram.
    The Mollier Diagram :
    The Mollier diagram, also called the ix diagram, is based on the relationship between heat content and water vapour content of air. The heat, or energy, content is difficult to measure directly, so the diagram is cunningly distorted to give the illusion of being based on the relationship between temperature and relative humidity and water vapour content. Temperature is easy to measure, relative humidity is considered by some people to be easy to measure and so the diagram is transformed into a useful tool.
    The Mollier diagram is a variant of the psychrometric chart. A move from the Mollier diagram to the psychrometric chart is explained here.
    Last edited by nike123; 29-10-2008 at 02:26 PM.

  10. #10
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: COP and Refrigeration Capacity Caculation?

    Thanks, Nike123. I will try to get it done bu the next test.