    Expansion tank



    Hello,

    I am using R23 refrigerant. I inject 100 pounds of R23 from a tank at 2000 psi (liquid form) into a refrigerant line at ambiant temperature, and I want to have no more than 300 psi. What is the calculation to obtain the volume required in my line.
    Thanks



  2. #2
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Expansion tank

    try and use "coolpack" you can find it here http://www.et.web.mek.dtu.dk/Coolpack/UK/download.html

    Ice

  3. #3
    Join Date
    Sep 2006
    Location
    Wales
    Posts
    10
    Rep Power
    0

    Re: Expansion tank

    The pressure in a cylinder of R23 will be around 500 psi at normal ambient temperatures. 100lb of R23 corresponds to 86.25 litres of fluid at the critical temperature of 26.3 deg C. At this temperature the critical pressure is 700 psi. so at the same temperature 2 x 86.25 will give 350psi. This should mean that you need a system volume of at least 700/300 x 86.25 = 201.25 litres. Most cascade systems have a standing pressure nearer to 100 psi though. Hope this helps.

Similar Threads

  1. design of expansion tank
    By scherif in forum Technical Discussions
    Replies: 8
    Last Post: 24-08-2010, 11:24 PM
  2. How an expansion tank works?
    By Raadster in forum Fundamentals
    Replies: 6
    Last Post: 25-07-2008, 02:25 PM
  3. expansion water tank sizing program
    By Lc_shi in forum Fundamentals
    Replies: 0
    Last Post: 01-09-2005, 04:24 AM
  4. Expansion
    By alesindo in forum Fundamentals
    Replies: 11
    Last Post: 30-07-2005, 09:16 AM
  5. water expansion tank
    By Lc_shi in forum Air Conditioning
    Replies: 5
    Last Post: 30-01-2005, 11:49 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •