    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi



    Quote Originally Posted by bruisermac View Post
    hey M L CA ... sounds like you need to wire your condenser fan to run all the time. that should be fine with R404a as you needed the cycling action with R134a to keep the head pressure up in cold ambients.

    the reason its tripping is cause it wants to pump down on defrost but because the fan is off it builds head and trips fast even before it can shut off. you may have a problem with the cycle switch as it should cut in on a rise in pressure. i have seen before that the compressor contactors stick and work erratically at best. we always lube those contactors.
    Or it may possibly be overcharged with refrigerant.



  2. #102
    Join Date
    Jul 2007
    Location
    Vancouver, Canada
    Age
    49
    Posts
    97
    Rep Power
    17

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    yes it could...it is hard to help a guy over the internet isnt it...the best is when they say its messed up but the pressures are "good" that is funny sh@t!!!

  3. #103
    Join Date
    Dec 2007
    Location
    Tampa, Florida U.S.A
    Age
    51
    Posts
    590
    Rep Power
    17

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by bruisermac View Post
    yes it could...it is hard to help a guy over the internet isnt it...the best is when they say its messed up but the pressures are "good" that is funny sh@t!!!
    Yeah sometimes its a challenge. My favorite one is "I think the pressures are okay, I will hook up gauges and check". I posted a what is normal pressure work sheet some where on this forum maybe a year and half ago.

    R-T

  4. #104
    saleemsalem's Avatar
    saleemsalem Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by reefermechanic View Post
    Hi saleemsalem

    did you check TR(transformer)? You try replace the transformer with new one. Good luck.

    reefer mechanic.
    Actually I did not replaced the Transfotmer, because its output Voltages were Normal 18volts and 22volts AC.

  5. #105
    Join Date
    Dec 2007
    Location
    Tampa, Florida U.S.A
    Age
    51
    Posts
    590
    Rep Power
    17

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by saleemsalem View Post
    Actually I did not replaced the Transfotmer, because its output Voltages were Normal 18volts and 22volts AC.
    I think Reefermech was thinking that if the voltage leaving the transformer was higher that this could cause higher current draws for the controllers devices. This does make logical sense, but since you have proper voltage on the secondary, then transformer is not the issue.

    You have changed the controller twice and still pops the fuses, do you know exactly when the fuses pop? Do they pop right away or does the unit continue through its start up sequence and then pop. If so in which part of the sequence does the fuse blow? During Evap fan start up, during condensor fan start up, during compressor start up? Typically this will give you clues as to what device that the controller is blowing the fuse on.

    If it is popping right away then you will probally have to get out your DMM and perform a resistance check on all inputs and outputs for a path to ground or internal low resistance due to a faulty shorted electrical device.

    Let us know what you find

    A-Z

  6. #106
    Join Date
    Nov 2008
    Location
    Surabaya/Indonesia
    Age
    51
    Posts
    44
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi William,
    As I know, just go to misc. function menu to reset time and date. No need password.

  7. #107
    Join Date
    Sep 2009
    Location
    tangier
    Age
    40
    Posts
    5
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Good day.
    i'm a biginner technician in reefer side.i want to bay some data retreive connector .but i have problem to found them ...
    can some body assist.
    badilou.nabil@hotmail.com

  8. #108
    Join Date
    Nov 2008
    Location
    Surabaya/Indonesia
    Age
    51
    Posts
    44
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    everybody,
    sorry, wrong post yesterday

  9. #109
    khoadg's Avatar
    khoadg Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by reefermechanic View Post
    Hi Opieman.

    İ think i found service manual of your machine.You need which one??

    RD-II and RD-II MAX (TK40181-1-MM).pdf

    RD-II Max (TK41023-1-MM Rev 1 10-27-03).pdf

    RD-II SR (TK41131-1-MM Rev 04-03).pdf

    RD-II TCI & RD-TLE (TK50394-1-MM Rev. 2-99).PDF



    Also you give to me your mail adress.İ will send to you)))

    See you,

    Reefermechanic

    Hi!
    Please help to send these manuals to my email: khoadg@yahoo.com
    Thank a million!

  10. #110
    Join Date
    Dec 2005
    Location
    Upper left hand corner of the USA
    Age
    64
    Posts
    203
    Rep Power
    19

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Whats ya doing teguh ? lol

  11. #111
    deliazmi's Avatar
    deliazmi Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Does anybody have documents about general principles of reefer's control system and how it designed? Information about connection of sensors,cable diagrams and repair manuels would hellp me too, Thank you..

  12. #112
    Join Date
    Oct 2009
    Location
    Canada
    Age
    35
    Posts
    7
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    I have a carrier 511-362 thats going off on Alarm 15 but that alarm does not appear on the list of alarm codes on the reefer or in the manual that I can locate...if you know what this means let me know. I'm a newbie and working by myself and don't really want to call someone else in if its just something stupid.

  13. #113
    Join Date
    Dec 2005
    Location
    Upper left hand corner of the USA
    Age
    64
    Posts
    203
    Rep Power
    19

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by ci_1612 View Post
    carrier 511-362 thats going off on Alarm 15 but that alarm does not appear on the list of alarm codes on the reefer or in the manual
    Later models show that alarm as "loss of cool". I'm guessing yours has gone through some software upgrades and thus won't show newer alarm # on the door.
    Go to Carriers website and check out the later model PDFs.

  14. #114
    Join Date
    Nov 2008
    Location
    Surabaya/Indonesia
    Age
    51
    Posts
    44
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    The latest SW ver. is 5146.

  15. #115
    rig19elect's Avatar
    rig19elect Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi guys,
    I am new to this site. I have 2 faults codes on sr-2 alarm window: 4 and 204. I found a plastic back stuck in evaporator so it was preventing airflow. I fixed but need to reset these codes. Can anyone pls help.
    Thanks

    Jesmond
    Rig19 Electrician

  16. #116
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    ........................
    Last edited by reefermechanic; 27-02-2013 at 09:56 AM.

  17. #117
    toddymcbride's Avatar
    toddymcbride Guest

    Question Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hi, only new to this site and new to transport Refrig. I have just recently started work on a Truck with an RD11 50SR 380V
    B/M No. 915527. on R404a ...
    the in cabin computer is a Thermoking Thermoguard Base - 5D52175G01
    S.P 45-1066
    The problem that has been occuring is the unit runs until the temp decreases to about 2degrees C then unit cuts into defrost then cools again then defrosts etc etc..

    The screen showed just before defrosting
    Room 1.3oC
    DIS -2.7oC
    Coil -7.2oC

    Set up for DF1 4 and DDR 45
    The air pressure switch has been disconnect. I have checked the operating pressures 120kpa suction and 1650 kpa Head pressure. I hosed out condensor coil and check evap conditon No ice on coil..

    What does
    (("SELECTING CYCLE SENTRY OR
    CONTINUOUS MODE"
    1. Press the On Key to turn the unit on.
    2. Press the Select key to display [CYCLS]
    and [YES] or [nO].
    3. Press the Up or Down Arrow key to
    select the desired mode. [YES] = Cycle
    Sentry, [nO] = Continuous.
    4. Press the Enter key. The display will
    briefly show [Lod], and then the new mode

    will reappear.))

    Is it possible to change how the unit activates defrost.? becuase the owner only uses the truck for about 4 hours a day can the defrost relay be removed ?? I would appreciated any help or ideas!!

  18. #118
    ppsmtu's Avatar
    ppsmtu Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hi
    good day
    i want to know aboutthermo king reefer unit on message (quest not allowed by timer). can u explain me and how to clear this message ?
    thanks you
    pyae

  19. #119
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    .............................................
    Last edited by reefermechanic; 27-02-2013 at 10:00 AM.

  20. #120
    pacoperez60's Avatar
    pacoperez60 Guest

    Talking Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hello sr, I HAVE A PROBLEM WITH MY REFEER , HAS THIS MESSAGE. ENGINE STALLED. IDONT NOT WATH IS THAT CAN YOU HELP ME IM SORRY FOR MY BAD WRITER THANX SO MUCH

  21. #121
    pacoperez60's Avatar
    pacoperez60 Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    I forgot my unit its a carrier ultima53 year 2000

  22. #122
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by pacoperez60 View Post
    I forgot my unit its a carrier ultima53 year 2000

    hi pacoperez,

    first nice too meet you.I think your unit is truck or trail unit.I repairing reefer container units.I cant help you..Sorry...

    see you

    reefer mechanic..

  23. #123
    altics's Avatar
    altics Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by reefermechanic View Post
    Hi Opieman.

    İ think i found service manual of your machine.You need which one??

    RD-II and RD-II MAX (TK40181-1-MM).pdf

    RD-II Max (TK41023-1-MM Rev 1 10-27-03).pdf

    RD-II SR (TK41131-1-MM Rev 04-03).pdf

    RD-II TCI & RD-TLE (TK50394-1-MM Rev. 2-99).PDF



    Also you give to me your mail adress.İ will send to you)))

    See you,

    Reefermechanic
    hi...can you give me some link...heres my my email add.....agonish_04@yahoo.com

  24. #124
    triardi's Avatar
    triardi Guest

    Exclamation Request Service Manual Reefer Container "DAIKIN" LXE 10 D

    Dear Reefer Mechanic,

    Would you like to sent me Service Manual / Operating Manual of Reefer Container "DAIKIN" LXE 10 D ?

    My Email Address is tri_ardi@yahoo.com

    Best Regards,
    Triardi S.

  25. #125
    Join Date
    Nov 2009
    Location
    singapore
    Age
    40
    Posts
    11
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Dear bro...
    When i was doing pti (thermoking unit,magnum), alarm 115 and 116 were come out.it does mean sensors faulty but when i check connection and ohm,showing that all in good condition (2000 ohm) please help me how should do?

  26. #126
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    .....................
    Last edited by reefermechanic; 27-02-2013 at 10:00 AM.

  27. #127
    Join Date
    Mar 2009
    Location
    tanger
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    HAY ALL,
    i am technician in the reefer , pls i have probleme with t.KING ( quest allowed) i want to clear it but i need help .

    BESTB REGARD

  28. #128
    Join Date
    Nov 2009
    Location
    singapore
    Age
    40
    Posts
    11
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Sorry for late reply,mate ! I haven't try to change yet coz i haven't spare part yet but i'll be change return air sensor and reply you no sooner.
    Thank you so much for your reply.

  29. #129
    Join Date
    Nov 2009
    Location
    singapore
    Age
    40
    Posts
    11
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Thanks a ton. It's really worked!
    When i was changed return air sensor , the unit is ok and pti pass.....i am quite curious coz the measure the value of ohm is nothing different with the old and new one sensor..? ?

  30. #130
    Join Date
    Nov 2008
    Location
    Surabaya/Indonesia
    Age
    51
    Posts
    44
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi, banana
    Try icebath calibration

  31. #131
    reefer-tech's Avatar
    reefer-tech Guest

    Post To ppsmtu - re QUEST

    Quote Originally Posted by ppsmtu View Post
    hi
    good day
    i want to know aboutthermo king reefer unit on message (quest not allowed by timer). can u explain me and how to clear this message ?
    thanks you
    pyae

    Hi, you shouldn't need to clear this. Quest is a power saving initiative. Starcool and ThermoKing also use it, Daikin call it DTMS2.
    It is exactly as you state "a message". It is telling you that the power saving mode (Quest) is currently not active due to a controller initiated time delay.
    As per Reefermechanic's menu picture, it is in the MISC sub menu Under STATUS.
    Quest should be left to do what it is supposed to, and only turned off if you have a very good reason :-)

    "QUEST power-saving mode is a software-based control option for Carrier Transicold refrigeration units that intelligently cycles refrigeration on and off based on temperature limits designed for specific perishables. It can cut energy requirements for refrigeration by up to 50% while also reducing power-related emissions."

  32. #132
    faiq sulafi's Avatar
    faiq sulafi Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    pak teguh...
    punya softwere untuk daikin, \tk, mitshubisi.
    kalo ada boleh untuk di share ke saya
    terima kasih

  33. #133
    zaher adidas's Avatar
    zaher adidas Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Please i need manuel for trailer theroking

  34. #134
    zaher adidas's Avatar
    zaher adidas Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Please i need manuel for trailer theroking ANYONE CAN HELP ME SEND IT TO ZAHERADIDAS@HOTMAIL.COM

  35. #135
    reefersup's Avatar
    reefersup Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by terminal View Post
    plz i have probleme with dakin for f 803 END F109; I WANT TO KNOW THE GOOD SOLUTION FOR THIS PROBLEME;THINKS MY TETCHER
    hi the problem is ev .u must adjust ev or change it . tnks:reefer sup

  36. #136
    reefersup's Avatar
    reefersup Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    note that it's no alarm ,i thinc sae tect reefer play in cofiguration i check and i bac whit good ansower. tnks/reefer sup

  37. #137
    reefersup's Avatar
    reefersup Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by terminal View Post
    HAY ALL,
    i am technician in the reefer , pls i have probleme with t.KING ( quest allowed) i want to clear it but i need help .

    BESTB REGARD
    note that it's no alarm ,i thinc sae tect reefer play in cofiguration i check and i bac whit good ansower. tnks/reefer sup

  38. #138
    Join Date
    Dec 2007
    Location
    Malaysia
    Age
    45
    Posts
    26
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi reefermechanic ,can you advice me on truck unit - T/K Spectrum MT ?

  39. #139
    Join Date
    Dec 2007
    Location
    Malaysia
    Age
    45
    Posts
    26
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    PM me .tq.

  40. #140
    Join Date
    Oct 2009
    Location
    Canada
    Age
    35
    Posts
    7
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    I have an old carrier 511-331. Its not modulating at all and also seems to be turning on only when the return comes 1 degree over set point and will go down 4 or so degrees under setpoint. Now I havent spent much time on it but have tested power coming to the plug connected to the stepper motor..I have voltage coming through on all 4 lines.. Should only have power on A/B or C/D at one time as A/B open and C/D close it if my memory serves me correctly. So that tells me the stepper motor itself is not the issue, however does this mean somehow it is the microlink or could it be the power module or even something else? just trying to get another opinion as it is a leased box and I cant just start changing random parts. P.S I did check to see if quest software was on this box and it is not.

  41. #141
    Join Date
    Apr 2009
    Location
    MOROCCO
    Age
    41
    Posts
    6
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    dear all;
    first happy now year;i have reefer daikin with AL :d301;but i dont new the solution,plz help me urgently

  42. #142
    Join Date
    Jul 2007
    Location
    Vancouver, Canada
    Age
    49
    Posts
    97
    Rep Power
    17

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hey 1612

    check for broken wires behind the compressor and suction valve. they rub on the back wall sometimes. also the drive module or if its an APL the emergency module fails. if it has an emergency module remove it and plug into the SMV directly

  43. #143
    Join Date
    Sep 2009
    Location
    tangier
    Age
    40
    Posts
    5
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    good day evey body .
    i look for some advice from the refrigeration-engineer experiance.
    me issus is i can found the stare cool reefer unit softwear to import the data logger from this unit..
    please advice .
    badilou.nabil@yahoo.com

  44. #144
    nunogato's Avatar
    nunogato Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi

    I need 2 manuals for these equipments:

    ThermoKing MDII-MAX
    Carrier Mistral 800

    please send it to nunovgato at gmail.com

    Thanks

  45. #145
    climo-tecnica's Avatar
    climo-tecnica Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    alguien en español por favor nesesito datos diagramas de carrier intercambio informacion tengo todo de thermo king grasias ggeras@hotmail.com

  46. #146
    Join Date
    Nov 2008
    Location
    China
    Posts
    19
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi Climo-tecnica,
    Could you speak in English?

  47. #147
    Join Date
    Nov 2008
    Location
    China
    Posts
    19
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi Ci 1612,
    I think you should check CD18 CD20 and CD34 to verify the setting of configuration, software versions and Economy mode.

  48. #148
    Join Date
    Nov 2008
    Location
    China
    Posts
    19
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi Starezone,

    Please receive email for software.

  49. #149
    Dante's Avatar
    Dante Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi, reefermechanic

    Im Dante, can I charge a Carrier reefer with 404a its present refrigerant is 134a?....Pls. give me more info about this. Thanks

    Dante

  50. #150
    Join Date
    Nov 2008
    Location
    China
    Posts
    19
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi Dante,

    I think you can not charge it with R404a. Because the working pressure of R404A is too high to fit this pipe system. and the components, for example compressor, TXV, HPS.... are not suit R404A.

    transcold.

Similar Threads

  1. Container Reefer Unit for Controlled Atmosphere (CA)
    By reeferman in forum New Technologies
    Replies: 9
    Last Post: 26-08-2011, 09:26 AM
  2. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  3. Help cutting open 40ft reefer, we now have problems
    By adrian_uk17 in forum Industrial
    Replies: 50
    Last Post: 28-11-2010, 09:11 AM
  4. Reefer container
    By stevec in forum Commercial
    Replies: 2
    Last Post: 25-01-2009, 06:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •