    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi



    Hi all
    i have a starcool unite and i have alarm for motor evap failr.but in my stor i have not the same motor marc. I have a ABB motor.when i changed the unit work good but a few minut alarm caming again.what you must do.



  2. #552
    Join Date
    Nov 2013
    Location
    Singapore
    Posts
    8
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hi terminal,
    u have to change some wiring of new ABB motor.
    motor side wire to incoming supply wire
    " 4 to 6 "
    " 5 to 4 "
    " 6 to 5 "

  3. #553
    Join Date
    Mar 2009
    Location
    tanger
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Thank you sur. When i have this problem i wil try to change wirs.thanks

  4. #554
    Join Date
    Oct 2013
    Location
    Serbia
    Age
    58
    Posts
    6
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Dear reefer mechanic,I have no possibility to talk via skype.I can use only ship's e-mail.So would you be kind to give me your e-mail.Thank you in advance

  5. #555
    Join Date
    Oct 2013
    Location
    Serbia
    Age
    58
    Posts
    6
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Dear bruisermac, would you be kind to give me your e-mail,if you want to send help and support to me regarding reefer containers.My mail is: pesicgordan@yahoo.com I have no possibility all the time to use this forum,only ship's e-mail.Thank you in advance.

  6. #556
    Join Date
    Oct 2013
    Location
    Serbia
    Age
    58
    Posts
    6
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    I apologize to other members of this community, reefer mechanic and bruisermac are two best men who gave best answers all the time on this forum.Cheers

  7. #557
    Join Date
    Dec 2010
    Location
    Paranagua
    Age
    47
    Posts
    5
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Dear reefer mechanic,

    Someone has the carrier scrl5364.ml3 software, and the software menu0116.m2x?
    Please send me m_heckert@yahoo.com

  8. #558
    Join Date
    Apr 2013
    Location
    lusaka
    Posts
    14
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi All,
    I have a problem with a 69 NT 511 - 353 CARRIER CONTAINER

    The unit seems to be running in a vacuum on the suction side? it is equipped with a modulation valve and quench valve these seem to be both iced upto the suction service valve.

    the refrigerant seems to be charged ok because the unit is cooling at a struggle to - 8 - 10C the balls in the site glass on both glasses are at the top.

    Please advise if anyone has good knowledge of these units.

    Thanks


    New Picture.jpg

  9. #559
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14
    Probably problem with the regulation valve..
    Did you try to re-set the valve to a specific value?

  10. #560
    Join Date
    Apr 2013
    Location
    lusaka
    Posts
    14
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi no I didnt how would I do this?

  11. #561
    Join Date
    Oct 2015
    Location
    US
    Age
    57
    Posts
    1
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    New to the forum, and looking for any manuals, schematics, etc... on Noske-Kaeser refrigerated chemical trailers. The company that has them in my area got a 5 page printout from them but it is in German. I can't read German. Any help would be appreciated.

  12. #562
    Join Date
    Oct 2015
    Location
    Lithuania
    Posts
    5
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hello, i'm new in the forum and i'm looking for Carrier and Thermo King manuals, if you have some please send me, i'll be very grateful.

    My email: lukaspavalkis@gmail.com

    Thanks in advance.

  13. #563
    Join Date
    Oct 2015
    Location
    Lithuania
    Posts
    5
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    To be accurate i'm looking for Thermo King SLX, SL series and Carrier Vector, Maxima manuals. Thanks guys.

    my email: lukaspavalkis@gmail.com

  14. #564
    Join Date
    Dec 2007
    Location
    U.A.E
    Posts
    14
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Can anybody has a service manual for Thermoking MD200 And MDII? Specially the overhauling manual for the engine.Please I badly need it. This is my email address ruben_rumarate1@yahoo.com

  15. #565
    Join Date
    Jul 2007
    Location
    Vancouver, Canada
    Age
    49
    Posts
    97
    Rep Power
    17

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    plugged DPRV

  16. #566
    Join Date
    Jul 2007
    Location
    Vancouver, Canada
    Age
    49
    Posts
    97
    Rep Power
    17

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    drier is probably plugged

  17. #567
    Join Date
    Mar 2007
    Location
    UAE
    Age
    42
    Posts
    78
    Rep Power
    18

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Dear all,

    I need some suppliers for reefer containers.

    I am in oman.

    Kindly give a mail to jeyakumar@sfomuscat.com

  18. #568
    Join Date
    Jan 2016
    Location
    TURKEY
    Age
    47
    Posts
    3
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi tjk2007
    I did send an email to you.. How can i help you?

    Regards
    reefermerchanic

  19. #569
    Join Date
    Jan 2016
    Location
    TURKEY
    Age
    47
    Posts
    3
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi guys

    i m at here

    Best regards
    Reefermechanic

  20. #570
    tundra's Avatar
    tundra Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    its most likely a micro problem,a place in cali will go thru it for ya at a very reasonable price,here is their #7074250108

  21. #571
    Join Date
    Mar 2016
    Location
    China
    Posts
    1
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi all,
    I want to know if there‘s any software to read the real-time Tsup and Tret of MP3000 & MP4000? I know LogManPC can read the USDA values of MP3000, but now, many MP3000 containers have no these data. And, the LogManIIPC just downloads recording data from the Data Recorder. So, can anybody help me?
    my email:ap0505138@yahoo.com
    Thanks!
    Wenping

  22. #572
    Join Date
    Apr 2016
    Location
    KENYA
    Posts
    2
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Any one with the manual for Thermo king CB MAX + 20

  23. #573
    Join Date
    Apr 2016
    Location
    KENYA
    Posts
    2
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    my email ; nictind@yahoo.com

  24. #574
    Join Date
    Apr 2016
    Location
    Australia
    Age
    38
    Posts
    1
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi guys, this is a bit of a random question, but I thought you guys would have the knowledge to help me!... I'm an amateur screenwriter with an interest in the shipping industry and working on a movie script about a guy who gets locked in a reefer.

    I was thinking that in the script, the compressor would fail and the reefer would start to heat up inside. As a result of the rising temperature he has to get out of there fast.

    Is there any way that the guy in the reefer could cause this? Like if he blocked the airflow intake or outlet, could it overload the compressor? Or if he drilled a hole in the reefer or damaged the seal, could the increased moisture ice the evaporator coils over and overload the compressor, causing it to fail? Could he damage the electrics from the inside and shut down the compressor somehow? (Although I can't think why he'd be messing with the electrics) Anyway, I've just been trying to do some research and find some possibilities.

    I'm sure I'm overlooking a lot of practical realities but I have no idea what they are!

    You can probably tell from my question that I don't have much knowledge in this area, so any help you guys could give me would be awesome!

    Apologies in advance if this is in the wrong section or not the right kind of thing for the forum.

    Tom

  25. #575
    Join Date
    Sep 2009
    Location
    Decatur, TX
    Age
    61
    Posts
    19
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hello there. A question please.
    SB 200 TG Reefer unit. I want to replace the filter dryer on this thing. Do I need to do a pump down at compressor service valves only?
    Thank you in advance.

  26. #576
    Join Date
    May 2016
    Location
    Poland
    Posts
    1
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi guys.
    How to change fahrenheit degrees to degrees Celsius in Thermoguard 5D52175G01?

    Thanx

  27. #577
    Join Date
    Apr 2009
    Location
    viet nam
    Age
    47
    Posts
    6
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi! All
    Help me
    I'm having problems with one machine SB3 SR +, cycle-sentry operating mode, the engine does not work for high-speed mode, but when operating at continue mode, works well for high-speed mode

    Tks

  28. #578
    Join Date
    Aug 2016
    Location
    usa
    Age
    41
    Posts
    2
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    I have reefer trailer with SB-210. I have just replaced filters and run pretrip. It failed with clearable alert "refrig capacity low". This unit is only used for heating so do I need to add refrig r404a or is it ok to leave it like that?

  29. #579
    Join Date
    Sep 2016
    Location
    SHIP
    Age
    43
    Posts
    8
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hello Reefer Mechanic and others!
    I am a newbie here and I am happy to be part of this forum.

    Our 69NT40-541-322 have a problem on sup and ret temp. The sup cannot reach the set point of -23°C and it stays only at -20°C and ret at -18°C. When it was loaded the sup was -23°C and ret -19°C. My mate charge about 1kg of refrigerant even the DP already high but he suspect it has low charge. After the charging the sup and return goes up insted of going down and of course it alarmed HPS. He recover some to just below the limit of HP. We also observe some oil down of compressor and this compressor was recon because of the paint. We cannot find the leaking part by using electronic leak checker we did not find the leak. The next day i found it was off and main breaker was tripped off. We turned it on and observed. We obsrerved that warm air out of condenser fan was disappearing after few seconds of running, we change the drier. But still the sup and ret temp cannot reach set point. Here are some data I have:
    Suction pressure -0.6 bar
    Discharge pressure 20 bar
    CD60 -18°C, we dont know this
    Ambient 36°C
    SMV 100

    We tried defrost, plenty of water comes out but nothing change in temp after. We turned off the reefer but discharge pressue does not drop, it almost remain high but suction pressure goes up. By pump down the DP goes down. The reefer does not trip anymore. Tommorow i will check the DPRV by checking the pressure on discharge of compressor vs liquid-line. What do you think the problem is? Sorry for my grammar.

  30. #580
    Join Date
    Sep 2016
    Location
    SHIP
    Age
    43
    Posts
    8
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Checked DPRV, 1bar diff, seems ok.

  31. #581
    Join Date
    May 2008
    Location
    Kazakhstan
    Age
    57
    Posts
    12
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hello everyone! It became necessary to replace the so-called Quench Expansion Valve (part n. 14-00212-03SV). Absolutely no desire to buy it for $ 200 plus shipping (such prices at us, unfortunately), when it is possible to replace the OEM. The only problem is unknown, its capacity. Does anyone know? If so please respond.

  32. #582
    Join Date
    Oct 2016
    Location
    NJ
    Posts
    2
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hello everyone.

    I am working on a Thermo King TS-300 with a code 17, which is "engine failed to crank". I manually tested the starter, and it is good. The 8S circuit from the relay board is also good.

    Since I have an identical scrap unit handy, I tried a different relay board, microprocessor, cab command, cab command cable, and main on/off switch. None of those made a difference.

    The unit will preheat and the buzzer sounds, but it does not crank. Also, it appears that the pull in circuit for the fuel solenoid does not have voltage either. There is voltage at the 2A terminal on the board.

    I'm stumped. Has anyone dealt with this before? Thanks in advance for any assistance.

  33. #583
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    What voltage do you have at the feed to the solenoid of the starter,try disconnecting the feed and testing if you have a feed to it pretty sure there is a plug on this feed close to the starter maybe a break in the feed try a temporary cable from that 8s and see if it engages the starter ?

  34. #584
    Join Date
    Oct 2016
    Location
    NJ
    Posts
    2
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    I have done that. If I put direct power on 8S, the starter cranks. That tells me the plug and circuit are good.

  35. #585
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Over here we use desperate battery for the unit,sometimes I believe in the states they tap into the truck battery,there is an extra heavy wire fitted to the battery not sure if it goes to number ,has this wire got good power/ connection ?

  36. #586
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Whoops spellchecker ,should have spelt seperate!!! not desperate?

  37. #587
    Join Date
    Dec 2016
    Location
    United Arab Emirates
    Posts
    1
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi Reefer Mechanic,
    Could you please help me out, I have a transicold reefer 69NT40-541-301 of which display is blinking and unit is not working, Display comes and missing frequently.

    Thanks in advance

  38. #588
    Join Date
    Dec 2009
    Location
    Egypt
    Posts
    1
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    All dears,
    I have problem with MItsubishi Transport refrigeration unit with model CPE15-3B H?
    I need help please

  39. #589
    Join Date
    Feb 2017
    Location
    Toronto
    Posts
    1
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hey I have a thermo king unit c-600 and keep getting the code 24
    Heating circuit fault
    Any help guys

  40. #590
    Join Date
    Jul 2017
    Location
    Russia
    Age
    43
    Posts
    1
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hello !
    anyone have ISO 10368 pdf ?
    i try to understand aspects of protocol RMM<->REF, used over RS232 interface.
    best regards.

  41. #591
    Join Date
    Oct 2017
    Location
    INDIA
    Posts
    3
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Dear Friends,

    Any body have carrier software program e.g 5365,5165,5364..... Please advice me how to get it......

  42. #592
    Join Date
    Aug 2013
    Location
    ROMANIA
    Posts
    3
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Help me Mitsubishi TU42D alarm codes

  43. #593
    Join Date
    Sep 2016
    Location
    SHIP
    Age
    43
    Posts
    8
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by reefermechanic View Post
    Hi Friend. pls check Cd-18 and Cd-20 within codeselect menu via keypad. And also pls check the unit model number. Unit model label left side of compressor and reply to me. see you. reefermechanic.
    Mate it also happened to us before, i am working at cma-cgm container vessel, we have bad card also before and some of my mate did not replace the battery on the card. We ask our superior about the issue and the technical team provide us sram to usb adapter, so this solves previuos issues of bard card since all the files for configuration is there together with all reefer brand. Everybody should have this,no more battery involve and windows based.

  44. #594
    Join Date
    Sep 2016
    Location
    SHIP
    Age
    43
    Posts
    8
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hapag Lloyd and Cma-cgm also

  45. #595
    Join Date
    Sep 2016
    Location
    SHIP
    Age
    43
    Posts
    8
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi Reefer Mechanic,
    We got a problem on Starcool, a tricky Tsuc Invalid. We changed already the sensor, door and main controller. Resistance of sensor 19.32kohms and voltage from controller to sensor 1.3vdc. Already tightened the insulation of tsuc sensor location. We notiched that controller is hot due to high disc press, compared to other Starcools, controller is not hot because disc press only below 10bar. Temp is in-range. Also i notiched that most Starcools the high speed cond fan run to lower until 8bar, but this reefer use low speed fan to lower 16bar to 14bar. Can you help us on this tricky Tsuc Invalid?

  46. #596
    Join Date
    Sep 2016
    Location
    SHIP
    Age
    43
    Posts
    8
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hello Caummer,
    Try to check connection from controller to display panel and then restart the power. If still persist replace the display panel.

Similar Threads

  1. Container Reefer Unit for Controlled Atmosphere (CA)
    By reeferman in forum New Technologies
    Replies: 9
    Last Post: 26-08-2011, 09:26 AM
  2. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  3. Help cutting open 40ft reefer, we now have problems
    By adrian_uk17 in forum Industrial
    Replies: 50
    Last Post: 28-11-2010, 09:11 AM
  4. Reefer container
    By stevec in forum Commercial
    Replies: 2
    Last Post: 25-01-2009, 06:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •