    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by Will View Post
    F1 and F2 are ONLY for the controller.

    Replace controller with a known good one.
    Already replaced 2 new controllers MICROLINK2i, but all of their fuses F1 AND F2 keep blowing out.

  2. #2
    Join Date
    Dec 2005
    Location
    Upper left hand corner of the USA
    Age
    64
    Posts
    203
    Rep Power
    19

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by saleemsalem View Post
    Already replaced 2 new controllers MICROLINK2i, but all of their fuses F1 AND F2 keep blowing out.
    Then you have something really messed up in the wiring somewhere.

    Something like this; few years back had a 'weird' problem on a TK. Evap fan motor smoked so bad it was feeding high volt back to mother board via motor overload circuit.
    You don't know fun till ya find 460V in your control circuit.


    Will

  3. #3
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by saleemsalem View Post
    Already replaced 2 new controllers MICROLINK2i, but all of their fuses F1 AND F2 keep blowing out.

    Hi saleemsalem

    did you check TR(transformer)? You try replace the transformer with new one. Good luck.

    reefer mechanic.

  4. #4
    Join Date
    Jul 2007
    Location
    Vancouver, Canada
    Age
    49
    Posts
    97
    Rep Power
    17

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    check the heater kliksons or the smv module. the easiest way is to disconnect the loads then slowly plug them in until u blow a fuse.

  5. #5
    Join Date
    Dec 2005
    Location
    Upper left hand corner of the USA
    Age
    64
    Posts
    203
    Rep Power
    19

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by reefermechanic View Post
    You try replace the transformer with new one.
    I'm curious as to why/how you came to this conclusion ?

  6. #6
    saleemsalem's Avatar
    saleemsalem Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by reefermechanic View Post
    Hi saleemsalem

    did you check TR(transformer)? You try replace the transformer with new one. Good luck.

    reefer mechanic.
    Actually I did not replaced the Transfotmer, because its output Voltages were Normal 18volts and 22volts AC.

  7. #7
    Join Date
    Dec 2007
    Location
    Tampa, Florida U.S.A
    Age
    51
    Posts
    590
    Rep Power
    17

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by saleemsalem View Post
    Actually I did not replaced the Transfotmer, because its output Voltages were Normal 18volts and 22volts AC.
    I think Reefermech was thinking that if the voltage leaving the transformer was higher that this could cause higher current draws for the controllers devices. This does make logical sense, but since you have proper voltage on the secondary, then transformer is not the issue.

    You have changed the controller twice and still pops the fuses, do you know exactly when the fuses pop? Do they pop right away or does the unit continue through its start up sequence and then pop. If so in which part of the sequence does the fuse blow? During Evap fan start up, during condensor fan start up, during compressor start up? Typically this will give you clues as to what device that the controller is blowing the fuse on.

    If it is popping right away then you will probally have to get out your DMM and perform a resistance check on all inputs and outputs for a path to ground or internal low resistance due to a faulty shorted electrical device.

    Let us know what you find

    A-Z

Similar Threads

  1. Container Reefer Unit for Controlled Atmosphere (CA)
    By reeferman in forum New Technologies
    Replies: 9
    Last Post: 26-08-2011, 09:26 AM
  2. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  3. Help cutting open 40ft reefer, we now have problems
    By adrian_uk17 in forum Industrial
    Replies: 50
    Last Post: 28-11-2010, 08:11 AM
  4. Reefer container
    By stevec in forum Commercial
    Replies: 2
    Last Post: 25-01-2009, 05:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •