    all reefer container problems/daikin/carrier/thermoking/mitsubishi



    ...................

    reefer mechanic
    Last edited by reefermechanic; 24-04-2010 at 12:13 AM.



  2. #2
    Join Date
    Dec 2005
    Location
    Upper left hand corner of the USA
    Age
    64
    Posts
    203
    Rep Power
    19

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Welcome Reefermechanic.

    What ?, no StarCool ?

  3. #3
    opieman74's Avatar
    opieman74 Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi. Iam a commercial refrigeration tech and owner. I was just recently asked to repair and services a thermo king unit M/N RD II 30. I am looking for a services manual or where to get one. Could you tell what kind of problems to look forword to.

  4. #4
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi Will,

    Only, MAERSK using Starcool unit.Also i repaired a few unit but ı don't know everythings about starcool unit.What happen??You have problem starcool unit?Maybe i can help you)))

  5. #5
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi Opieman,

    I didn't understand you.But you must tell me right model.Your machine marine or trailer units??Beacuse on the Thermoking container units signs CSR,CRR and Magnum etc.If you give to me more information i will help you..

    Best Regards.

    reefermechanic

  6. #6
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi Opieman.

    İ think i found service manual of your machine.You need which one??

    RD-II and RD-II MAX (TK40181-1-MM).pdf

    RD-II Max (TK41023-1-MM Rev 1 10-27-03).pdf

    RD-II SR (TK41131-1-MM Rev 04-03).pdf

    RD-II TCI & RD-TLE (TK50394-1-MM Rev. 2-99).PDF



    Also you give to me your mail adress.İ will send to you)))

    See you,

    Reefermechanic

  7. #7
    Join Date
    Jan 2008
    Location
    Canada
    Posts
    579
    Rep Power
    17

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi reefermechanic and welcome.
    I think your calling truck / trailer units container units. On this side of the pond, container reefers are "sea going" containers.
    One last thing, you may get some flack for offering manuals here. If you decide to help someone this way, it's best to email them with the offer.
    I apreciate your wanting to help but some others may not.
    Cheers
    Abbs
    Last edited by abbsnowman; 29-10-2008 at 03:05 PM. Reason: spelling

  8. #8
    why me?'s Avatar
    why me? Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hello i was sent to an old carrier container wwhen i got there room temp plus 20 no ref running turn stat to minus 10 ref ran set stat to zero fridge ran to plus 10 then
    stopped turned down to minus 10 ref
    restarted can you help?

  9. #9
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by why me? View Post
    hello i was sent to an old carrier container wwhen i got there room temp plus 20 no ref running turn stat to minus 10 ref ran set stat to zero fridge ran to plus 10 then
    stopped turned down to minus 10 ref
    restarted can you help?
    Hi Why Me

    can you say to me whats model your carrier unit??for example 69NT40 -489 etc....

    Best regards.

    Reefermechanic.

  10. #10
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    16

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Reefer mechanic,

    welcome to RE and nice to have a new member who are more than willing to help and share his knowledge.

    regards,
    abet

  11. #11
    Join Date
    Nov 2008
    Location
    alaska
    Age
    58
    Posts
    11
    Rep Power
    0

    Question Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi guys:

    I have 4 carrier elite and thinline shipping container units rnning a holding room here. I would really like to intergrate their electronics with my plant plc so I could do things like initiate defrosts from it, and monitor them. Does anyone have any access to or ideas on either electrical schematics or interface programs for this?

    thanks

    Dan

  12. #12
    Join Date
    Mar 2008
    Location
    Portugal
    Age
    45
    Posts
    2
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi Dan,

    If you just want the basics like manual defrost and temperatures, the quickest way in my opinion would be to tap into the manual defrost switch (MDS) inputs (KA8 & KB8 - for the older ML2/ML2i controllers). Refer to Carrier's manuals (which contain wiring diagrams) you can download from Carrier's website. Hopefully the ML3 still recognizes these manual defrost inputs as the ML3 can replace a ML2i controller. For reading temperatures, if your PLC can support temperature sensors, then installing separate sensors would be the quickest option.

    The better but more complicated option: The MicroLink 3 (ML3) controller has a serial port which can communicate to your PC if you have the DataLine software. You can also download the latest Service pack 8 from Carrier's site (You'll need DataLine first though). If you're not bad at programming you can interface your PLC to the MicroLink directly but you'll need to figure out the communications protocol.

    If you get desperate I'll try my best to find a better solution for you. Good luck.

  13. #13
    Join Date
    Nov 2008
    Location
    alaska
    Age
    58
    Posts
    11
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Thanks, Ill start with that. we have pretty good programming assets, if I can get the software, we can probably make it all work. Ill update somewhere down the line.........

    Dan

  14. #14
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by abet_meneses View Post
    Reefer mechanic,

    welcome to RE and nice to have a new member who are more than willing to help and share his knowledge.

    regards,

    ...........
    Last edited by reefermechanic; 27-02-2013 at 09:48 AM.

  15. #15
    Join Date
    May 2008
    Location
    New Zealand
    Posts
    35
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hi there Reeferman, Iam am currently working on an old mitsubishi CPE53-2BAIIIPU container. have just finished replacing the main display board and now get 2 alarm codes that won't clear. they are 207 and 356. I am starting to look at the main relay board (P-MGC05) I have all clean voltage going to the board and the pahse sequence seems ok. The alarms tell me that the 207 is single phase and the 356 alarm is the current sensor. As far as I can see they all originate from the above mentioned board.

    any help would be very much appreciated as the customer wants to rent the box out over the Xmas period

    thanks for your time

  16. #16
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi London

    I have never seen CPE53-2BAIIIPU container.I don't know how is its??But if you send a picture and wiring diagram of reefer unit maybe i can help you..

    I m waiting your kindly informations of reefer unit.

    best regards.

    reefer mechanic...

  17. #17
    Join Date
    May 2008
    Location
    New Zealand
    Posts
    35
    Rep Power
    0

    Smile Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hi there reeferman , thanks for the reply. The mitsi box is now sorted. I did a factory reset with the dip switches on the main board (switches 6&7-moved them to the on position and powered up the container, then shut down and returned to the off position). I was told this by a guy who was an old hand at mitsi containers. this cleared the alarms that were hard latched in. I then proceeded to do a full PTI and the container passed. Thought this info might be handy to you and anyone else who may come across this problem

    kind regards and happy holidays




  18. #18
    Reefer tech's Avatar
    Reefer tech Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    reefer mechanic.. can you please help me find a manual for an SB 310 thermo king unit????
    Thanks

  19. #19
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    ...........
    Last edited by reefermechanic; 27-02-2013 at 09:48 AM.

  20. #20
    Join Date
    Mar 2008
    Location
    Romania
    Age
    43
    Posts
    44
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hello reefer mechanic
    I have some problems with a ThermoKing CFIII M5.
    This is the first container that i'm workink on, so, if you have some info (service manual, operation manual, etc),
    please send it to danyelstoica@gmail.com.
    Thank you very much.

  21. #21
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    hi exxe

    I did sen to e-mail to your mail adress.Check please than back to me..

    See you

    reefer mechanic

  22. #22
    hhbbsun's Avatar
    hhbbsun Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi reefer mechanic,

    I am looking for one kind of integrated reefer machine (except TK, Carrier, Daikin, Mit) with genset and one or two sets of refrigrating system. If you know any, please kindly let me know. My email address is hongbin.sun@cimc.com.

    Thank you for your help in advance.

    Gary

  23. #23
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    ...........
    Last edited by reefermechanic; 27-02-2013 at 09:49 AM.

  24. #24
    Join Date
    Feb 2009
    Location
    faversham kent
    Age
    58
    Posts
    19
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    I fault with a TK sea container not controlling at set point +4 the liqiud line solenoid will not shut if you remove the coil the unit will pump down but it will not cut out on LP

  25. #25
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by reefermechanic View Post
    Hi All,

    I m senior reefer technician.İf you have got any problem about reefer container units . i will be here....

    All the best.
    hi iceman uk here what is the weather like and any jobs i am a reefer expert with 25 years knowledge wanting to escape to sunny happy times

  26. #26
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    ............
    Last edited by reefermechanic; 27-02-2013 at 09:49 AM.

  27. #27
    andreiortan's Avatar
    andreiortan Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    i need a wiring diagram for conection cable , i whant to get data from thermo guard micro p. thanks

  28. #28
    Join Date
    Jan 2009
    Location
    Australia
    Age
    43
    Posts
    6
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi reeferman,
    We have recently had a problem with a mitsubishi CEP52 reefer, It had low refrigerant due to leak on sight glass, replaced sight glass, drier, and evacuate and charge, now we have high head pressure and low suction pressure problems with little cooling effect can't get below 20 deg c, we think maybe problem with electronic expansion valve, any Ideas ??

  29. #29
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi Andrew,

    Yes ,,you are right.If you seen high head pressure and low suction pressure there is problem on electronic expansion valve.Did you check its??

    Your unit is which one??

    MMCCIIIA-52CPE15-2BWIIINV 2BAIIINV, 2BAIIIFV, 3BAIIIAV, A2V


    I m waiting your reply..

    see you

    reefer mechanic.

  30. #30
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by AndrewB View Post
    Hi reeferman,
    We have recently had a problem with a mitsubishi CEP52 reefer, It had low refrigerant due to leak on sight glass, replaced sight glass, drier, and evacuate and charge, now we have high head pressure and low suction pressure problems with little cooling effect can't get below 20 deg c, we think maybe problem with electronic expansion valve, any Ideas ??

    Andrew,

    You have to check attached file.

    Good luck.

    Reefer Mechanic.
    Attached Images Attached Images
    Last edited by reefermechanic; 07-05-2009 at 04:31 AM.

  31. #31
    Join Date
    Mar 2009
    Location
    tanger
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    plz i have probleme with dakin for f 803 END F109; I WANT TO KNOW THE GOOD SOLUTION FOR THIS PROBLEME;THINKS MY TETCHER

  32. #32
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    ............
    Last edited by reefermechanic; 27-02-2013 at 09:50 AM.

  33. #33
    Join Date
    Jan 2009
    Location
    Australia
    Age
    43
    Posts
    6
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi ReeferMechanic,
    We changed the elextronic expansion valve, on the CEP52, now working really well, thanks for the tips
    Cheers Andrew

  34. #34
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by AndrewB View Post
    Hi ReeferMechanic,
    We changed the elextronic expansion valve, on the CEP52, now working really well, thanks for the tips
    Cheers Andrew

    Hi Andrew,

    Thank for kindly reaply I have become happy if i help you..Where are you working??What s name your company??

    See you ..

    Reefer Mechanic...

  35. #35
    Join Date
    Apr 2009
    Location
    Kent
    Age
    52
    Posts
    5
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Can anybody help ?. We provide trailer telematics devices GPS etc etc. We want to integrate it with reefer trailers, initially Carrier and Thermo King so that we can remotely gather temperatures and any other data available.

    I need to know what data can be easily collected, is there typically a data port we can gather the data from ? what is this data bus, RS232 / 485, CAN etc.

    Does anyboday have the protocols for communicating to/from the fridge units ?

    We are willing to pay for any consultancy work

    Thanks

    Telematics

  36. #36
    aku's Avatar
    aku Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hello Everybody.
    In my country haven't any freezer container and unit factory.
    But I am researching to cooperate company who can supply to us freezer container. But, I need to know which way is better?
    1st. We will studying workers then installing. /of course we must to purchase reefer machine like a Termo king, Daikin .... etc./
    2nd. We will purchase completely product freezer container.
    Actually our country is very cold in winter and summer time is very hot. So reefer machine must be work -40 +40C. And my countries climate dry. So reefer machine must be work in bad climate like a storm.
    Please tell me, which companies reefer machine much suitable in my country? and how teach my worker?
    oh there is one offer about installation inner and outer of container?

    Best Regards
    Ariunbold.Ts

  37. #37
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by aku View Post
    Hello Everybody.
    In my country haven't any freezer container and unit factory.
    But I am researching to cooperate company who can supply to us freezer container. But, I need to know which way is better?
    1st. We will studying workers then installing. /of course we must to purchase reefer machine like a Termo king, Daikin .... etc./
    2nd. We will purchase completely product freezer container.
    Actually our country is very cold in winter and summer time is very hot. So reefer machine must be work -40 +40C. And my countries climate dry. So reefer machine must be work in bad climate like a storm.
    Please tell me, which companies reefer machine much suitable in my country? and how teach my worker?
    oh there is one offer about installation inner and outer of container?

    Best Regards
    Ariunbold.Ts

    Hi Ariunbold,

    You must check and select to the DAIKIN units

    • <LI class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LINE-HEIGHT: 14.4pt; tab-stops: list 36.0pt">Inside temp range –30/+30 deg. C <LI class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LINE-HEIGHT: 14.4pt; tab-stops: list 36.0pt">Ambient temp range –30/+50 deg. C <LI class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LINE-HEIGHT: 14.4pt; tab-stops: list 36.0pt">Reduced power consumption with the design of Daikin’s digital temperature control software (DTMS and DTMS2) <LI class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LINE-HEIGHT: 14.4pt; tab-stops: list 36.0pt">Reliability in all weather conditions <LI class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LINE-HEIGHT: 14.4pt; tab-stops: list 36.0pt">Low maintenance and Operational costs <LI class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LINE-HEIGHT: 14.4pt; tab-stops: list 36.0pt">Operates using R134A (non CFC) – with the lowest GWP and subsequently the most environmentally friendly refrigerant. <LI class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LINE-HEIGHT: 14.4pt; tab-stops: list 36.0pt">Compliance with industry environmental regulations and forward looking design to comply with future legislation
    • Sensitive temperature control - to protect fresh produce from freeze damage
    • Hot gas defrost system – providing the most efficient and fastest defrost available with less heat escaping to the cargo area, improving conditions for the cargo
    http://www.daikinreefer.com/product-...vanced-design/

    Nice to meet you..
    Reefer Mechanic..

  38. #38
    derekcambodia's Avatar
    derekcambodia Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi my company The fair manufacturing Company, here is Cambodia has purchased a used 20' reefer with a thermo king c11 m40 refrig unit. It powered up ok but does require the coolant gas to be re filled/ re charged . Our local refrig guy (who is pretty good) wants to clarify what Coolant gas he is recommended to use. Also is there a recommended compressor oil to use ?
    Regards and Thanks in advance for offer to help us out there in this brave new world !!.
    Derek mayes

  39. #39
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by derekcambodia View Post
    Hi my company The fair manufacturing Company, here is Cambodia has purchased a used 20' reefer with a thermo king c11 m40 refrig unit. It powered up ok but does require the coolant gas to be re filled/ re charged . Our local refrig guy (who is pretty good) wants to clarify what Coolant gas he is recommended to use. Also is there a recommended compressor oil to use ?
    Regards and Thanks in advance for offer to help us out there in this brave new world !!.
    Derek mayes
    Hi Mr.Derek,

    You will find all your need informations within atteched files.

    Best regards.

    Reefer mechanic.
    Attached Images Attached Images

  40. #40
    Join Date
    Jul 2007
    Location
    Vancouver, Canada
    Age
    49
    Posts
    97
    Rep Power
    17

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by terminal View Post
    plz i have probleme with dakin for f 803 END F109; I WANT TO KNOW THE GOOD SOLUTION FOR THIS PROBLEME;THINKS MY TETCHER
    the problem is that one of the phase contactor coil is shorted to ground. if Fu1 pops when the contactor pulls in the coil is shorted. so you can change the faulty contactor or if an emergency rewire the 460V plug and swap 2 wires...this will change the phase and pull in the other contactor. F 803 is "protection devices have tripped 10 times" and will also probably have a E101 or E109 alarm. you can then clear any alarm by selecting the alarm and holding enter.

    im a container reefer pro and can help just like reefermechanic!

    good luck.

  41. #41
    william0707's Avatar
    william0707 Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi reefermechanic,

    I am a fresh guy on this site but work for reefer container for many years

    We got a problem on TK/MP3000A controller, we found the GMT time changed by unit on /off several times
    ( seems breaker of power supply tripped at terminal ) though we had reset the corrrect GMT time but problem still occured, We can't find anything wrong on this one year old controller of Magnum type.
    Is there possible the RTC battery dead
    or weak ? I had ask TK guy but can't get the answer till now. Do you have any idea about it ?

    Tks,

    William0707

  42. #42
    william0707's Avatar
    william0707 Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi PRO reefer Mechanic,

    I know the password " A " for MP300 but reset only can be done by LOGAMN PC

    We can reset to the correct GMT time but don't know what trouble lead to this change of GMT( but nobody do the setting, it reset by controller ). I have found 2 cases in two shipping line's datalog but can't expalin this trouble only by their datalog.

    Any comment will be appreciate !

    William0707

  43. #43
    Join Date
    Apr 2009
    Location
    MOROCCO
    Age
    41
    Posts
    6
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Im too i search the catallogue ; informations for reefer tec
    thanks monir_khatibi@hotmail.com

  44. #44
    Join Date
    Mar 2009
    Location
    tanger
    Posts
    30
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    tanks my tetsher i have one probleme for daikin end i want solution for this probleme
    f 803 END F1O9 END F 107
    I WAIT YOU SOON

  45. #45
    william0707's Avatar
    william0707 Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi PRO Reefer Mechanic,

    Unfortunately units were away from my terminal. The strange of GMT time
    ( time even record 2009-06-20 138:20:16- future time and abnormal hour ), we had checked the dehumidity sensor, gas sensor even replace to a new one to avoid high voltage then reset the GMT time, but it occured after power on/off for running 2 days. I guess it must be some short circuit or bug in the controller ? But it still passed the test by tester !

    I know it's hard to find out without current unit on hand for test, but just can't find a way to explain this defect, any idea? please share, tks!

    william0707

  46. #46
    Join Date
    Jul 2007
    Location
    Vancouver, Canada
    Age
    49
    Posts
    97
    Rep Power
    17

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    did you try to set the date with smartsponge and a laptop? or are you just using the logman?

  47. #47
    maiks's Avatar
    maiks Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hallo

    i bought the thermo king refrigerator container type hd-ha-ab951 2007 year. But i need manual.maybe you could help me!!!

  48. #48
    william0707's Avatar
    william0707 Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Hi Bruiser

    Mp3000 controller should be uploaded the setting or software by LOGMANPC 4.9.0 , of course we did upload the GMT setting by laptop P.C.


    We still get no idea about this defect, Any comment will be appreciated, tks!

    william0707

  49. #49
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    Quote Originally Posted by maiks View Post
    Hallo

    i bought the thermo king refrigerator container type hd-ha-ab951 2007 year. But i need manual.maybe you could help me!!!

    Hi Maiks

    you sure type is correct??I never seen to this modeldo you add a picture in here??Thanks..

    nice to meet you

    see you

    reefer mechanic..

  50. #50
    ccaarriinn's Avatar
    ccaarriinn Guest

    Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi

    I need to repair a Thermo Guard Up-IV for Thermo King SB-III SR, where can I get this done? or even where can I buy used one for not a lot of money?
    Thanks for any help you can provide.

    Oscar

Similar Threads

  1. Container Reefer Unit for Controlled Atmosphere (CA)
    By reeferman in forum New Technologies
    Replies: 9
    Last Post: 26-08-2011, 09:26 AM
  2. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  3. Help cutting open 40ft reefer, we now have problems
    By adrian_uk17 in forum Industrial
    Replies: 50
    Last Post: 28-11-2010, 09:11 AM
  4. Reefer container
    By stevec in forum Commercial
    Replies: 2
    Last Post: 25-01-2009, 06:30 PM