    Unhappy Retrofit existing R22 flooded plant



    Hi everyone
    I have a large two stage flooded R22 refrigeration plant ( about 5.000 Kg of refrigerant) with two separators -30ºC and -10ºC. Refrigerant is pumped by Witt pumps to the cold rooms. Compressors are Mycom screw units.
    I need some ideas to change refrigerant, Amonia is for the moment not an alternative, because evaporators are coper/aluminium.
    Kind regards



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Retrofit existing R22 flooded plant

    Is lubricant naphtenic mineral oil?

  3. #3
    Join Date
    Sep 2005
    Location
    uk
    Posts
    5
    Rep Power
    0

    Re: Retrofit existing R22 flooded plant

    Quote Originally Posted by cristovaol View Post
    Hi everyone
    I have a large two stage flooded R22 refrigeration plant ( about 5.000 Kg of refrigerant) with two separators -30ºC and -10ºC. Refrigerant is pumped by Witt pumps to the cold rooms. Compressors are Mycom screw units.
    I need some ideas to change refrigerant, Amonia is for the moment not an alternative, because evaporators are coper/aluminium.
    Kind regards
    r422d is a replacement were using on packs

  4. #4
    Join Date
    Aug 2007
    Location
    Seattle, WA. USA
    Age
    56
    Posts
    27
    Rep Power
    0

    Re: Retrofit existing R22 flooded plant

    I have a similar issue with pump recirculated R-22 on factory trawlers.

    One of our customers is considering the switch to ammonia but their condensers are cupro-nickel, and although almost all of the piping is steel I am sure there will be things that are forgotten which will bring up emergencies down the road...

    If anyone has experience with this it would be much appreciated. I have looked into R-422D but my concern is losing effectiveness as R-422D is not an azeotropic gas. It's a bit hard to justify removing and recharging 7,000Lbs, (3,180Kg) of refrigerant every time they have leaks...

  5. #5
    Join Date
    Sep 2003
    Location
    sout east uk
    Age
    45
    Posts
    15
    Rep Power
    0

    Re: Retrofit existing R22 flooded plant

    Iceon website for infomation:

    R417a for DX
    R422d for water chillers

    you may actually see an increase in efficiency!!

  6. #6
    Join Date
    Aug 2007
    Location
    Seattle, WA. USA
    Age
    56
    Posts
    27
    Rep Power
    0

    Re: Retrofit existing R22 flooded plant

    I can't find the website for iceon. Can you post it here?

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Retrofit existing R22 flooded plant

    IT's actually ISCEON

    http://refrigerants.dupont.com/Suva/...nds/index.html

    All drop in gases are actually worse than R22, and will cause widespread leakages and gasket failures.

  8. #8
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    639
    Rep Power
    20

    Re: Retrofit existing R22 flooded plant

    If your high side has sufficient design pressure, you will find that R-507 is your best choice for a replacement. It is not a drop in and will require checking all gasket/o-ring materials as well as a good lube oil flush.

    I stay away from all of the 400 series for anything but the smaller DX equipment.

    Another good refrigerant provided the compressors are compatible would be R-290, propane.

    Ken

  9. #9
    Join Date
    Jan 2009
    Location
    New Orleans
    Age
    77
    Posts
    6
    Rep Power
    0

    Re: Retrofit existing R22 flooded plant

    This is out of my league, as I do not do refrigeration, but in researching R22 alternatives, I have run across R290 (porpane) which is the closest to R22 in thermodynamic properties and compatible with mineral oils; does not mean it is a "drop in" replacement.

    Among the things I picked up, it is a very good replacement for flooded systems. Obviously with the proper safety precautions. It is being used for this in a number of places. I have also seen references to it's use in Europe for regrigerators. I can't point you to any specific source of information, but perhaps someone else can.

  10. #10
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    639
    Rep Power
    20

    Re: Retrofit existing R22 flooded plant

    Using R-290, propane, brings in a while new set of concerns. First you need to check if the insurance carrier has any problems with using R290. The electrical classification and ventilation for the engine room will need to be reviewed. The PSV exhaust need to be reviewed.

    Mineral oils can be used with propane, but you will have fewer problems a good synthetic oil.

    With the screw compressors, the oil system may require extensive redesign. Generally a screw on propane will have a lot less oil cooler load and some use no or reduced injection oil to help keep the discharge temperature up. Oil recovery will need to be reviewed.

    A propane conversion can be done, but you need a good consultant that is well versed in propane systems.

    Ken
    Last edited by TXiceman; 09-01-2009 at 02:22 AM.

Similar Threads

  1. Cop Of Brine Plant And Chilled Water Plant
    By patilvasudeo in forum Fundamentals
    Replies: 2
    Last Post: 16-07-2008, 06:43 AM
  2. Tube Ice Plant -Ammonia
    By tjk2007 in forum Industrial
    Replies: 3
    Last Post: 25-04-2008, 09:41 PM
  3. Water Softening Plant for Controlled Atmosphere Storage
    By dawoodaq in forum Technical Discussions
    Replies: 2
    Last Post: 04-03-2008, 11:20 AM
  4. Soap Plant Load Calculations
    By tjk2007 in forum Fundamentals
    Replies: 0
    Last Post: 25-11-2007, 06:59 AM
  5. HFCs for flooded systems?
    By garyb in forum Refrigerants
    Replies: 15
    Last Post: 21-04-2006, 10:02 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •