    Feb 2008
    Lima - Peru
    49
    ammonia pump oversized
    Whats happen if an ammonia pump(liquid overfeed system) is oversized for example:
    My system needs
    Q = 50 m^3/h
    Total Head = 35 m
    The pump was selected for work in the system
    Q = 50 m^3/h
    Total head = 50 m
    will i have any problem?
    Oct 2003
    5,630
    Re: ammonia pump oversized
    It will consume more but I don't think it will give you specific problems.
    Perhaps a small bypass or a VFD can be a solution.
    Aug 2005
    5,302
    As Peter said, it should work OK based on the information provided. However, I would caution you to verify the NPSHR of the pump and make sure you have adequate NPSH on top of the pump at that operating condition to make sure it works OK.
    India
    688
    We had similar experience with over sized pumps( as the ratio was 10:1 defined by plate freezer manufacturer). The excess liquid is bypassed when you adjust the glow rates through each equipment( like freezer, coil). We had suggested to use VFD to minimize the power consumption.
    Feb 2008
    Lima - Peru
    49
    smpsmp45:
    what is VFD?????? and does you have any drawing where i can see the bypass that you say me???
    Best Regards.
    Aug 2005
    5,302
    VFD = variable frequency drive; used to control the Hertz for the purpose of speed control
    The bypass valves mentioned is in the pump discharge line. As solenoid valves close, the pump discharge pressure will increase slightly. The bypass valve allows the pressure in the liquid line to bypass back into the tank.
    Feb 2008
    Lima - Peru
    49
    thanks guys. their comments are very important for me.
    if i don't have the solenoid valve, i could do the same if i close a little the discharge valve of the pump.
    Aug 2005
    5,302
    Quote Originally Posted by luissandoval
    ...i could do the same if i close a little the discharge valve of the pump.
    Yes, that is one way.
    However, the VFD works very well also. When you slow down the pump to control the discharge pressure the NPSHR reduces rapidly, which helps to reduce cavitation issues.
    India
    688
    US ICeman has answered it rightly
    Sep 2008
    Ireland
    Hi Guys, in my experience, the discharge side of the pump will have an adjustable pressire relief valve for venting to the top of the separator in case of "dead heading", the oversizing of the pump is not an issue if it is a centrifigual hermetic type pump, the inlet of the freezer will have a regulating valve for throttling the flow for the correct duty required.
    Sep 2008
    Canada
    811
    Quote Originally Posted by luissandoval View Post
    My system needs
    Q = 50 m^3/h
    Total Head = 35 m
    Q = 50 m^3/h
    Total head = 50 m
    This isn't oversized pump. Just head is greater than at design conditions. Adjustment of coil hand expansion valves will solve this diffrence.
  1. liquid ammonia pump calvitation
    By Kathleen in forum Trouble Shooting
    Last Post: 20-05-2011, 02:18 AM
  2. Ammonia liquid pump
    By jessica in forum NH3
    Last Post: 30-05-2008, 12:53 PM
  3. Oil Pump in Ammonia Compressor?
    By NNNNNN in forum Technical Speculations
    Last Post: 05-03-2008, 11:04 AM
  4. Liquid Ammonia Pump problems
    By smpsmp45 in forum NH3
    Last Post: 01-02-2008, 11:51 AM
  5. pressure drop of pump return line ammonia
    By Moeller in forum Fundamentals
    Last Post: 04-09-2007, 05:21 AM