23-10-2008, 11:06 PM #1
ammonia pump oversized
Whats happen if an ammonia pump(liquid overfeed system) is oversized for example:
My system needs
Q = 50 m^3/h
Total Head = 35 m
The pump was selected for work in the system
Q = 50 m^3/h
Total head = 50 m
will i have any problem?
-
24-10-2008, 06:02 AM #2
Re: ammonia pump oversized
It will consume more but I don't think it will give you specific problems.
Perhaps a small bypass or a VFD can be a solution.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
24-10-2008, 06:43 AM #3
Re: ammonia pump oversized
As Peter said, it should work OK based on the information provided. However, I would caution you to verify the NPSHR of the pump and make sure you have adequate NPSH on top of the pump at that operating condition to make sure it works OK.
If all else fails, ask for help.
-
24-10-2008, 09:25 AM #4
Re: ammonia pump oversized
We had similar experience with over sized pumps( as the ratio was 10:1 defined by plate freezer manufacturer). The excess liquid is bypassed when you adjust the glow rates through each equipment( like freezer, coil). We had suggested to use VFD to minimize the power consumption.
-
24-10-2008, 03:37 PM #5
Re: ammonia pump oversized
smpsmp45:
what is VFD?????? and does you have any drawing where i can see the bypass that you say me???
Best Regards.
-
24-10-2008, 04:00 PM #6
Re: ammonia pump oversized
VFD = variable frequency drive; used to control the Hertz for the purpose of speed control
The bypass valves mentioned is in the pump discharge line. As solenoid valves close, the pump discharge pressure will increase slightly. The bypass valve allows the pressure in the liquid line to bypass back into the tank.If all else fails, ask for help.
-
24-10-2008, 08:38 PM #7
Re: ammonia pump oversized
thanks guys. their comments are very important for me.
if i don't have the solenoid valve, i could do the same if i close a little the discharge valve of the pump.
-
24-10-2008, 11:41 PM #8
Re: ammonia pump oversized
Originally Posted by luissandoval
However, the VFD works very well also. When you slow down the pump to control the discharge pressure the NPSHR reduces rapidly, which helps to reduce cavitation issues.If all else fails, ask for help.
-
25-10-2008, 05:30 AM #9
Re: ammonia pump oversized
US ICeman has answered it rightly
-
25-10-2008, 04:20 PM #10
Re: ammonia pump oversized
Hi Guys, in my experience, the discharge side of the pump will have an adjustable pressire relief valve for venting to the top of the separator in case of "dead heading", the oversizing of the pump is not an issue if it is a centrifigual hermetic type pump, the inlet of the freezer will have a regulating valve for throttling the flow for the correct duty required.
-
25-10-2008, 05:53 PM #11
Similar Threads
-
liquid ammonia pump calvitation
By Kathleen in forum Trouble ShootingReplies: 23Last Post: 20-05-2011, 02:18 AM -
Ammonia liquid pump
By jessica in forum NH3Replies: 19Last Post: 30-05-2008, 12:53 PM -
Oil Pump in Ammonia Compressor?
By NNNNNN in forum Technical SpeculationsReplies: 22Last Post: 05-03-2008, 12:04 PM -
Liquid Ammonia Pump problems
By smpsmp45 in forum NH3Replies: 7Last Post: 01-02-2008, 12:51 PM -
pressure drop of pump return line ammonia
By Moeller in forum FundamentalsReplies: 5Last Post: 04-09-2007, 05:21 AM