    ammonia pump oversized



    Whats happen if an ammonia pump(liquid overfeed system) is oversized for example:

    My system needs
    Q = 50 m^3/h
    Total Head = 35 m

    The pump was selected for work in the system

    Q = 50 m^3/h
    Total head = 50 m

    will i have any problem?



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: ammonia pump oversized

    It will consume more but I don't think it will give you specific problems.
    Perhaps a small bypass or a VFD can be a solution.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: ammonia pump oversized

    As Peter said, it should work OK based on the information provided. However, I would caution you to verify the NPSHR of the pump and make sure you have adequate NPSH on top of the pump at that operating condition to make sure it works OK.
    If all else fails, ask for help.


  4. #4
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: ammonia pump oversized

    We had similar experience with over sized pumps( as the ratio was 10:1 defined by plate freezer manufacturer). The excess liquid is bypassed when you adjust the glow rates through each equipment( like freezer, coil). We had suggested to use VFD to minimize the power consumption.

  5. #5
    Join Date
    Feb 2008
    Location
    Lima - Peru
    Age
    41
    Posts
    49
    Rep Power
    0

    Re: ammonia pump oversized

    smpsmp45:

    what is VFD?????? and does you have any drawing where i can see the bypass that you say me???


    Best Regards.

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: ammonia pump oversized

    VFD = variable frequency drive; used to control the Hertz for the purpose of speed control

    The bypass valves mentioned is in the pump discharge line. As solenoid valves close, the pump discharge pressure will increase slightly. The bypass valve allows the pressure in the liquid line to bypass back into the tank.
    If all else fails, ask for help.


  7. #7
    Join Date
    Feb 2008
    Location
    Lima - Peru
    Age
    41
    Posts
    49
    Rep Power
    0

    Re: ammonia pump oversized

    thanks guys. their comments are very important for me.

    if i don't have the solenoid valve, i could do the same if i close a little the discharge valve of the pump.

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: ammonia pump oversized

    Quote Originally Posted by luissandoval
    ...i could do the same if i close a little the discharge valve of the pump.
    Yes, that is one way.

    However, the VFD works very well also. When you slow down the pump to control the discharge pressure the NPSHR reduces rapidly, which helps to reduce cavitation issues.
    If all else fails, ask for help.


  9. #9
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: ammonia pump oversized

    US ICeman has answered it rightly

  10. #10
    Join Date
    Sep 2008
    Location
    Ireland
    Age
    56
    Posts
    15
    Rep Power
    0

    Re: ammonia pump oversized

    Hi Guys, in my experience, the discharge side of the pump will have an adjustable pressire relief valve for venting to the top of the separator in case of "dead heading", the oversizing of the pump is not an issue if it is a centrifigual hermetic type pump, the inlet of the freezer will have a regulating valve for throttling the flow for the correct duty required.

  11. #11
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: ammonia pump oversized

    Quote Originally Posted by luissandoval View Post
    Whats happen if an ammonia pump(liquid overfeed system) is oversized for example:

    My system needs
    Q = 50 m^3/h
    Total Head = 35 m

    The pump was selected for work in the system

    Q = 50 m^3/h
    Total head = 50 m

    will i have any problem?
    This isn't oversized pump. Just head is greater than at design conditions. Adjustment of coil hand expansion valves will solve this diffrence.

Similar Threads

  1. liquid ammonia pump calvitation
    By Kathleen in forum Trouble Shooting
    Replies: 23
    Last Post: 20-05-2011, 02:18 AM
  2. Ammonia liquid pump
    By jessica in forum NH3
    Replies: 19
    Last Post: 30-05-2008, 12:53 PM
  3. Oil Pump in Ammonia Compressor?
    By NNNNNN in forum Technical Speculations
    Replies: 22
    Last Post: 05-03-2008, 12:04 PM
  4. Liquid Ammonia Pump problems
    By smpsmp45 in forum NH3
    Replies: 7
    Last Post: 01-02-2008, 12:51 PM
  5. pressure drop of pump return line ammonia
    By Moeller in forum Fundamentals
    Replies: 5
    Last Post: 04-09-2007, 05:21 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •