    Ammonia Chiller versus ***** Chiller



    Hello Guys!

    Could somebody tell me what kind of chiller is better, more efficient? It is said that ammonia is more efficient (and future) refrigerant than *****s... But if we have chillers to compare - which is better? I haven't got selections of both chillers to compare and don't even know which one have better EER (COP)...

    Thanks for any replies.

    Jacek



  2. #2
    Join Date
    Nov 2006
    Location
    Poland
    Posts
    91
    Rep Power
    18

    Re: Ammonia Chiller versus ***** Chiller

    P. S.

    Let's compare two chillers with the leaving water temperature of 7 deg. C

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Ammonia Chiller versus ***** Chiller

    I think the word efficient is over used today. This simple word is meant to explain all things better or worse.

    Ammonia has higher heat transfer coefficients than other common refrigerants. Does that make it more efficient? Perhaps, but the size of the ammonia chiller will be smaller than the R-22 chiller. Same for the condenser.

    What happens if we use the same size heat exchangers for both refrigerants and then compare the energy use, ammonia would be better because the approach temperatures would be smaller.

    I think it is important to compare the two refrigerants equally to get a factual analogy to the real facts.
    If all else fails, ask for help.


  4. #4
    Join Date
    Apr 2008
    Location
    The Netherlands
    Age
    49
    Posts
    67
    Rep Power
    16

    Re: Ammonia Chiller versus ***** Chiller

    Hello Iceman,

    I think your right but here in Europe we have antother problem.
    You mention R-22 but it's not allowed to use that anymore in new installations / chillers. And....from 2010 it's only allowed to use regenerated R-22 for service and from 2015 R-22 is banned completely.

    So it has to be antother *****type. But since here in Europe ***** use is getting worse and worse maybe other types (for example R134a) are also banned in the future.

    So since Jacek is from Poland i think the best option for them is NH3.
    The european union even gives taxcuts when you use natural refrigerants.

    Just so you know, didn't want to break down your help becuase you are right.

    Greets,

    Bart.

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Ammonia Chiller versus ***** Chiller

    Quote Originally Posted by Bart Nabbe
    You mention R-22 but it's not allowed to use that anymore in new installations / chillers. And....from 2010 it's only allowed to use regenerated R-22 for service and from 2015 R-22 is banned completely.
    I know, that was just an example. R-22 was the most prevalent refrigerant left over from the past. It was also close to ammonia in performance capabilities.

    I'm not trying to recommend other refrigerants. Ammonia is very good to use for a lot of applications. Especially fairly high temperature projects as chillers.

    Another aspect of refrigerant use are the local safety codes. If they limit refrigerant use for specific applications, it does not matter how efficient they are.
    If all else fails, ask for help.


  6. #6
    Join Date
    Nov 2006
    Location
    Poland
    Posts
    91
    Rep Power
    18

    Re: Ammonia Chiller versus ***** Chiller

    Hello Guys.

    Thanks for replies.

    Could someone make for me comparision between ammonia chiller and R134achiller and provide me with EER and ESEER (equivalent of American IPLV) for both chillers for comparison?

    We have conditions as below:
    1. Cooling capacity: 1000 kW.
    2. Water temperatures: 12/7 deg. C.

    I'd like to have these ESEERs for LCC analysis and know which chiller is better in, let's say, 15-year time. Asking for this, I don't think about enviromental aspects - I know that ammonia is the best solution...

    Thank you in advance.

    Jacek, from Poland

  7. #7
    Join Date
    Feb 2009
    Location
    Italy
    Age
    61
    Posts
    6
    Rep Power
    0

    Re: Ammonia Chiller versus ***** Chiller

    hello Jacek,
    here in Italy Nh3 is preferred on medium big size of plant (like yours 1000 kw for example is the starting size).
    Infact we have a lot of rules on Nh3 employ on plant from fire dept.
    On small plant usually we prefer ***** chiller units.

  8. #8
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Ammonia Chiller versus ***** Chiller

    Jacek, if you do not have the vendor softwear to select equipment, your best bet is to contact several vendors to get budget information on various refigerants.

    Typicall, the commerical "*****" vendor will not ahve any information for NH3 other than to bad-mouth NH3. Most NH3 equipment vendors can also provide a "*****" system.

    Each vendor can provide the ESEER data and whne provided with an energy cost, can provide a life-cycle operating cost.

    You will need to be sure all are compared on the same life-cycle, energy cost and cost of money.

    At this point you are actually getting into the duties of a consultanting engineer to make an accurate life time cost analysis.

    ken

  9. #9
    Join Date
    Nov 2006
    Location
    Poland
    Posts
    91
    Rep Power
    18

    Re: Ammonia Chiller versus ***** Chiller

    Quote Originally Posted by TXiceman View Post
    Jacek, if you do not have the vendor softwear to select equipment, your best bet is to contact several vendors to get budget information on various refigerants.

    Typicall, the commerical "*****" vendor will not ahve any information for NH3 other than to bad-mouth NH3. Most NH3 equipment vendors can also provide a "*****" system.

    Each vendor can provide the ESEER data and whne provided with an energy cost, can provide a life-cycle operating cost.

    You will need to be sure all are compared on the same life-cycle, energy cost and cost of money.

    At this point you are actually getting into the duties of a consultanting engineer to make an accurate life time cost analysis.

    ken
    Could somebody compare for me a NH3 chiller with a ***** chiller? Conditions are:

    1. Cooling capacity of 1000 kW.
    2. Water temperature: 12/7 deg. C.

    Each chiller is of water-cooled type and with (a) screw compressor(s). Probably an ammonia chiller can use only one compressor for such a capacity (more compressors are needed for a ***** chiller).

  10. #10
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Ammonia Chiller versus ***** Chiller

    jacek, it would be best if you called your local vendors and did your own work. Contact your local GEA or Grasso rep to get both bases covered. Carrier or Trane will quote ***** only and York/Frick can do both if you get the right office, not the commercial office.

    Ken

  11. #11
    Join Date
    Nov 2006
    Location
    Poland
    Posts
    91
    Rep Power
    18

    Re: Ammonia Chiller versus ***** Chiller

    Quote Originally Posted by TXiceman View Post
    jacek, it would be best if you called your local vendors and did your own work. Contact your local GEA or Grasso rep to get both bases covered. Carrier or Trane will quote ***** only and York/Frick can do both if you get the right office, not the commercial office.

    Ken
    Thank you very much.

    Nobody on the forum cannot give me the COPs (or ESEERs or IPLVs) for these two options?

    Jacek

  12. #12
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Ammonia Chiller versus ***** Chiller

    Quote Originally Posted by Jacek
    Nobody on the forum cannot give me the COPs (or ESEERs or IPLVs) for these two options?
    I doubt it very much. IPLV's are calculated values to account for part load efficiency and a given set of heat exchangers. Most ammonia chillers I have seen are custom built, not mass produced where it might be worth the effort to perform the IPLV calculations.

    The COP's and other calculated ratios or efficiencies can also change depending on how the equipment is selected and operated.

    If you lower the condensing temperature, the COP increases. If you raise the evaporating temperature the COP also increases. And on and on...

    This is a numbers game. Therefore by changing some assumptions you can get a new set of numbers. It might not be a true representation of what you actually get, but the numbers may look better.
    If all else fails, ask for help.


  13. #13
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Ammonia Chiller versus ***** Chiller

    IPLV and like numbers are pretty much specific to standard off the shelf design type units. You can do them for custom units which ammonia units fall into, can be done, but it is alot of work. I have done the calculations, and it is very time consuming.

    This is why I suggested you go back to the vendors and let them earn their commissions.

    Like Mike said...it is a numbers game and I think it has no real use for a custom unit or an ammonia unit.

    Ken

  14. #14
    Join Date
    Oct 2009
    Location
    Ukraine
    Age
    41
    Posts
    21
    Rep Power
    0

    Re: Ammonia Chiller versus ***** Chiller

    Jacek, here you are:
    Ammonia COP Sabroe PAC 163HF-A 1041Kw/200kW=5.2 (water cooled 25/30)
    McQuay 134a, PFS-B 296.2 1060kW/158kW=6.7 (water cooled 25/30)

    The difference in chiller design. This is the main point. I've compared the serial models.

  15. #15
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Ammonia Chiller versus ***** Chiller

    Haldotech, the numbers apply only to the specific units you selected and can be changed by designing with larger or smaller heat exchangers.

    By redesigning, you can make the units swap places.

    Ken

  16. #16
    Join Date
    Oct 2009
    Location
    Ukraine
    Age
    41
    Posts
    21
    Rep Power
    0

    Re: Ammonia Chiller versus ***** Chiller

    Quote Originally Posted by TXiceman View Post
    Haldotech, the numbers apply only to the specific units you selected and can be changed by designing with larger or smaller heat exchangers.

    By redesigning, you can make the units swap places.

    Ken
    Ken, as you know, different from serial design - different money. Of course, at equal chiller design ammonia is better.
    But I think Jacek asked exactly what I've answered.

  17. #17
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Ammonia Chiller versus ***** Chiller

    Quote Originally Posted by hladotech View Post
    Ken, as you know, different from serial design - different money. Of course, at equal chiller design ammonia is better.
    But I think Jacek asked exactly what I've answered.
    But he asked 2 years ago and has not been back to this thread.......



    taz



    .

  18. #18
    Join Date
    Oct 2009
    Location
    Ukraine
    Age
    41
    Posts
    21
    Rep Power
    0

    Re: Ammonia Chiller versus ***** Chiller

    Nevertheless...

  19. #19
    Join Date
    Nov 2006
    Location
    Poland
    Posts
    91
    Rep Power
    18

    Re: Ammonia Chiller versus ***** Chiller

    Many thanks hladotech.

    Best regards,

    Jacek

    Quote Originally Posted by hladotech View Post
    Jacek, here you are:
    Ammonia COP Sabroe PAC 163HF-A 1041Kw/200kW=5.2 (water cooled 25/30)
    McQuay 134a, PFS-B 296.2 1060kW/158kW=6.7 (water cooled 25/30)

    The difference in chiller design. This is the main point. I've compared the serial models.

Similar Threads

  1. ammonia refrigeration system
    By Lc_shi in forum Fundamentals
    Replies: 48
    Last Post: 25-06-2010, 10:03 AM
  2. Building a refrigerated warehouse
    By gaz in forum Fundamentals
    Replies: 45
    Last Post: 24-07-2009, 09:03 AM
  3. The Mysteries of Ammonia!
    By Grizzly in forum Ye Old Wifes Tales
    Replies: 63
    Last Post: 29-08-2008, 03:11 PM
  4. changing from ***** to ammonia
    By claude11 in forum Industrial
    Replies: 6
    Last Post: 07-05-2008, 05:08 PM
  5. ammonia refrigeration
    By deepakrbhat in forum Refrigerants
    Replies: 77
    Last Post: 23-04-2004, 12:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •