28-10-2008, 03:40 PM #1
Re: Flood back issue?
Assuming the TXV is adjusted correctly, the saturation temp must be about -4C or lower. This gives us an evap TD of at least 12C/21.6F. This seems excessive.
And for the frost to continue all the way to the compressor, we may be looking at a much lower saturation temp and much higher TD before the compressor decides to unload.Last edited by Gary; 28-10-2008 at 03:48 PM.