    Charge amount at altitude?



    I have a strange one here.....

    If we charge a capillary tube system with 180g of R404a at sea level the charge amount is perfect. If we charge the exact same unit at altitude with 180g it appears to be under-gassed?

    Help!

    Andy



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Charge amount at altitude?

    Welcome to the forum.

    There was another thread relating to charging at altitude which may be of interest....

    http://www.refrigeration-engineer.co...light=altitude

    By what critirea are you saying that it appears undercharged, can you give us some readings?

    Did you actually re-evacuate and reweigh in the charge at altitude or are things being done in a test chamber?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2008
    Location
    UK
    Posts
    8
    Rep Power
    0

    Re: Charge amount at altitude?

    Basically we have a plant in Mexico (@6500ft ASL) and a plant in Dallas and the UK. We have a unit we have been producing in the UK for years that is a cap tube system. We weigh in 180g and the unit has frost on the suction return about 1" away from the compressor. This is what I would call a critical charge (I am no refrigeration expert by the way).

    If we charge the unit in Mexico (on different scales) the unit looks undercharged and has no frost anywhere near the compressor. To gain the same result as a UK unit we need to use about 250g of refrigerant. If we then ship this unit to the UK it is overcharged and we have frost on the compressor.

    Sorry if the explanation/terminology isn't perfect

    Andy

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Charge amount at altitude?

    Explanation not bad, thanks

    What are the ambient temperatures in the different locations ?

    If the dew point temperature changes then the pipes may or may not start freezing/frosting.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Oct 2008
    Location
    UK
    Posts
    8
    Rep Power
    0

    Re: Charge amount at altitude?

    We have a test lab in the uk and the ambient temp is both 24 deg C in both locations, humidity is virtually identical too. In Dallas we shipped a unit and again similar conditions and the unit worked perfectly with 180g, The only obvious difference is altitude.

    We shipped some units back to the uk from Mexico and these we reclaimed the gas and got 230g to 240g. The guys here in Mexico had been critically charging the units and this is the amount it took.

    I am puzzled!!

    Andy

  6. #6
    Join Date
    Oct 2008
    Location
    UK
    Posts
    8
    Rep Power
    0

    Re: Charge amount at altitude?

    I should also say that this is a coiled well unit and 3/4 of the well has frost the last third does not unless I add more R404a.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Charge amount at altitude?

    Quote Originally Posted by awilkinsonuk View Post
    Basically we have a plant in Mexico (@6500ft ASL) and a plant in Dallas and the UK. We have a unit we have been producing in the UK for years that is a cap tube system. We weigh in 180g and the unit has frost on the suction return about 1" away from the compressor. This is what I would call a critical charge (I am no refrigeration expert by the way).

    If we charge the unit in Mexico (on different scales) the unit looks undercharged and has no frost anywhere near the compressor. To gain the same result as a UK unit we need to use about 250g of refrigerant. If we then ship this unit to the UK it is overcharged and we have frost on the compressor.

    Sorry if the explanation/terminology isn't perfect

    Andy
    This is what I think about your problem.
    You need to pressurize charging plant at sea level pressure of 1013 millibars to achieve simmilar density of air there and in, say, UK.
    Because of thinner air in your altitude evaporator gets lower amount/density of air and therefore it have lower superheat (and heat absorption capacity) and subcooling (and heat rejection capacity) than at sea level. That is why you need more refrigerant at higher level to compensate for lower density of air.

    If your products are for market at that high sea level then they should be calculated and charged for that air density.
    Last edited by nike123; 21-10-2008 at 10:21 AM.

  8. #8
    Join Date
    Oct 2008
    Location
    UK
    Posts
    8
    Rep Power
    0

    Re: Charge amount at altitude?

    That does make sense but would you expect the 6500ft altitude to give as much as 30% differential in the charge amount? I would have thought 10% but we are charging a unit that normally has 180g with 230g or more!

    Andy

    Thanks for the answer by the way

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Charge amount at altitude?

    I'm thinking a comparison of data might reveal the differences.

    Low side:

    Evap air in temp
    Evap air out temp
    Saturated suction temp (SST) converted from pressure
    Suction line temp at evap outlet

    High side:

    Cond air in temp
    Cond air out temp
    Saturated condensing temp (SCT) converted from pressure
    Liquid line temp at receiver outlet

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Charge amount at altitude?

    Quote Originally Posted by awilkinsonuk View Post
    That does make sense but would you expect the 6500ft altitude to give as much as 30% differential in the charge amount? I would have thought 10% but we are charging a unit that normally has 180g with 230g or more!
    I don't know. I am not designer of refrigeration equipment.
    That was only my logical thinking when I consider different air density on different altitudes.
    Inside the circuit, different altitudes cannot have any influence, because system is sealed from environment pressures.

    P.S.
    Do you have any difference in frequency and voltage on that locations?
    Last edited by nike123; 21-10-2008 at 06:16 PM.

  11. #11
    Join Date
    Oct 2008
    Location
    UK
    Posts
    8
    Rep Power
    0

    Re: Charge amount at altitude?

    There is one difference.....


    The units are designed for 230VAC 50Hz and we run them here at 230VAC 60Hz.

    This is a small 10cc single phase compressor.

    Andy

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Charge amount at altitude?

    Quote Originally Posted by awilkinsonuk View Post
    There is one difference.....


    The units are designed for 230VAC 50Hz and we run them here at 230VAC 60Hz.

    This is a small 10cc single phase compressor.

    Andy
    That's a BIG difference. The compressor and fans have 20% more capacity on 60Hz.
    Last edited by Gary; 21-10-2008 at 07:25 PM.

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Charge amount at altitude?

    Quote Originally Posted by awilkinsonuk View Post
    There is one difference.....


    The units are designed for 230VAC 50Hz and we run them here at 230VAC 60Hz.



    Andy
    OK, as Garry already said, that is what is your problem!

    You cannot use same compressor, evaporator, condenser and same amount of refrigerant at different frequencies because mass flow of refrigerant is not same with different frequency. Imagine that as you have inverter compressor.

  14. #14
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Charge amount at altitude?

    Quote Originally Posted by awilkinsonuk View Post
    There is one difference.....


    The units are designed for 230VAC 50Hz and we run them here at 230VAC 60Hz.

    This is a small 10cc single phase compressor.

    Andy
    There you go, typical designer.

    Only give you half the facts and save the deciding information 'til last

    At least we're all learning here Andy
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  15. #15
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Charge amount at altitude?

    Quote Originally Posted by nike123 View Post
    P.S.
    Do you have any difference in frequency and voltage on that locations?
    Good call, Nike.

  16. #16
    Join Date
    Oct 2008
    Location
    UK
    Posts
    8
    Rep Power
    0

    Re: Charge amount at altitude?

    Yes, I thought we were running a genorator but I only found out today we run a transformer and don't alter the frequency! As we say in the UK - assumption is the mother of all f**k-ups!!

  17. #17
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Charge amount at altitude?

    Quote Originally Posted by Gary View Post
    Good call, Nike.
    Thanks Gary!
    When it comes from authority like you, I am more than honored.

  18. #18
    Join Date
    Oct 2008
    Location
    UK
    Posts
    8
    Rep Power
    0

    Re: Charge amount at altitude?

    One thing though....

    We ran a unit in Dallas at 208Vac @ 60Hz and this ran ok and the charge amount was correct. If we run the same machine here in Mexico at 230Vac @ 60Hz it works totally different! I wouldn't have thought dropping 10% on the voltage would make up for the 20% increase in frequency would it?

    Andy

  19. #19
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Charge amount at altitude?

    if a system is designed to run on certain specifics be aware if you change something on what makes it to go to work ,power or pressure,the whole outcome will change.remember we are working whit thermo dynamic fluid and gases.

    Ice

  20. #20
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Charge amount at altitude?

    have seen it on two units,one next to the other,working on the same power line. stand alone they worked perfectly,together yore worst nightmare. giff them each a power line of their one and problem solved.

    we learn surprisingly each day,if we let it happen.

    Ice

  21. #21
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Charge amount at altitude?

    Quote Originally Posted by awilkinsonuk View Post
    One thing though....

    We ran a unit in Dallas at 208Vac @ 60Hz and this ran ok and the charge amount was correct. If we run the same machine here in Mexico at 230Vac @ 60Hz it works totally different! I wouldn't have thought dropping 10% on the voltage would make up for the 20% increase in frequency would it?

    Andy

    On a motor under load, dropping the voltage increases the slippage and therefore decreases the speed.

Similar Threads

  1. MHI FDCA400HKXRE4 Tech Info Please
    By L.JT in forum Trouble Shooting
    Replies: 5
    Last Post: 23-08-2008, 11:00 PM
  2. Estimating Refrigerant Charge with TEV TXV
    By GXMPLX in forum Fundamentals
    Replies: 0
    Last Post: 22-07-2008, 04:22 PM
  3. To charge or not to charge?
    By Fire and Ice in forum Old Refrigeration Photos
    Replies: 12
    Last Post: 20-01-2008, 08:11 PM
  4. Subcooling vs charge graph?
    By Larry2 in forum Fundamentals
    Replies: 4
    Last Post: 01-12-2006, 07:40 PM
  5. Who's in charge?
    By chillin out in forum Chit Chat & Service Stories
    Replies: 1
    Last Post: 01-10-2006, 10:51 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •