    VRV issue



    Hi sirs
    VRV can apply the situation of long distance between outside and inside units. I'm not sure how about the max pressure loss along the pipe. Who knows the practical data? thanks


    regards
    LC


    I hear...I forget;I see...I remember;I do...I understand

  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: VRV issue

    You would need to check with each manufacturer for those details.

    Mitsubishi, Daikin, Sharp, Samsung etc, etc.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2007
    Location
    Moscow
    Age
    40
    Posts
    82
    Rep Power
    17

    Re: VRV issue

    Hi, Lc_chi!
    I think you told about Daikin VRV. There are follow limits for this stuff: max. length between outdoor and indoor is 165 m (190 m equivalent length); max. difference between outdoor/indoor is 40 m (outdoor in bottom position) or 50 m (outdoor higher than indoor). You can rise the difference between outdoor and idoor units up to 90 m. In this case you should use reductor EKLD90P12 or EKLD90P18 (European kits) . This is official Daikin information for VRVIII. But Daikin didn't report anything about pressure loss along the pipe.
    Last edited by DVaider; 19-10-2008 at 04:59 PM.

  4. #4
    Join Date
    Jun 2006
    Location
    Ireland(ROI)
    Age
    44
    Posts
    28
    Rep Power
    0

    Re: VRV issue

    Lc_shi,

    once you stick to the max piping lengths(which you will get from the supplier, I presume it's Daikin with the VRV), you install the pipework correctly and you charge the system correctly, you won't have any problems with pressure drops/ loss. You won't be able to make much sense from pressure readings around a running VRV anyway.

    Good luck, Steve.

  5. #5
    Join Date
    Oct 2008
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: VRV issue

    VRF and VRV system manufacturers provide the restrictions on refrigeration pipe length and vertical elevation. Since pressure drops can’t be avoided, these restrictions will ensure that the pressure drop is within limit.

    Correct refrigerant piping is important. Excess pressure drops resulting from incorrect pipe lengths will have an impact on your system capacity. System capacity will drop which leaves you buying bigger outdoor units, costing you more money.

    You should also look out for oil return issues specially because you are dealing with a variable capacity system. If the VRV system is using an inverter compressor and is operating at low capacity, long pipe lengths will be an obstacle for low velocity refrigerant and oil to return to your compressor.

Similar Threads

  1. electrical heating cable issue
    By Lc_shi in forum New Technologies
    Replies: 2
    Last Post: 21-07-2007, 09:51 PM
  2. large refrigeration plant cooling tower issue
    By Lc_shi in forum New Technologies
    Replies: 4
    Last Post: 25-03-2007, 01:35 PM
  3. hydraulic floor heating issue
    By Lc_shi in forum New Technologies
    Replies: 6
    Last Post: 02-01-2007, 09:07 PM
  4. MIHI price issue
    By madwoody in forum Air Conditioning
    Replies: 7
    Last Post: 04-11-2006, 12:43 PM
  5. Air conditioning system cleaning issue
    By Lc_shi in forum Legal-Business-Marketing
    Replies: 2
    Last Post: 24-08-2006, 03:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •