    daikin vrv inverter compressor check



    i got L8 error from daikin VRVII system RXYQ30MYIK high ambient unit checked and found the inverter board's print was burnt out so anybody can guide me what r the precuations or checkings has to be do before changing a new inverter pcb assembly



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: daikin vrv inverter compressor check

    Megger test the compressor.
    Diode/resistance test anything that plugs into the board eg filter module and ipm if seperate to the main board, fan motors etc

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: daikin vrv inverter compressor check

    There is a thread about checking compressors HERE.
    And as Paul said (sorry, wrote) don't forget to check all other control related bits.

    One important test,often forgotten, is to check the incoming mains. A non existent Neutral might create 400 volt on a board where it should only be 240V. This will also happen if there is loose connections inside the unit.

  4. #4
    Join Date
    Aug 2008
    Location
    OMAN
    Age
    46
    Posts
    16
    Rep Power
    0

    Re: daikin vrv inverter compressor check

    thanks for your help i will tell my maintainance team to do as per that procedure

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: daikin vrv inverter compressor check

    You might also like to download a technical manual for that unit from here...

    http://www.daikinac.com/commercial/d...c=docs&page=39

    Click on the first one - RXYQ.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Aug 2008
    Location
    OMAN
    Age
    46
    Posts
    16
    Rep Power
    0

    Re: daikin vrv inverter compressor check

    Thanking you for the response also i checked your site there is only methods for checking compressor winding and grounding (by ohm tester and megger, done these checkings but shows normal and there is no loose connections or voltage problem found all other boards seems fine this inverter assembly is very expensive part and if i go through the new one i have doughts (becuase i couldn't found any fault for inverter assembly pcb blast ). So pls tell me there is any device for checking inverter compressor without connecting inverter assembly board that is just for checking any mechanical failure from compressor. that i need only for few seconds. Or any other methods to trouble shoot compressor failure(inverter) hope i can get a solution this unit is the combination of RXYQ10MYIK x 3 and now for emergency i started the system without this RXYQ10MYIK module

  7. #7
    Join Date
    Aug 2008
    Location
    OMAN
    Age
    46
    Posts
    16
    Rep Power
    0

    Re: daikin vrv inverter compressor check

    thnking u for the support but i couldn't find the model which is suitable for me RXYQ8MYIK & RXYQ10MYIK

  8. #8
    Join Date
    Jun 2006
    Location
    Ireland(ROI)
    Age
    44
    Posts
    28
    Rep Power
    0

    Re: daikin vrv inverter compressor check

    You can get an invertor board tester from Daikin direct (around £50 stg) or a spurious one from any good electrical supplier. It's a very handy tool, just take the spade connections off the compressor and connect them to the tester, switch on the power and through a sequence of flashing lights it will tell you whether it's the inv board or compressor.

    The only test you can do on the compressor direct is to check even resistances between windings and whether ny of them are down to earth. This won't tell you if the comp is seized though.

    As you say, the invertor board assembly is the more expensive part and you really don't want to be replacing it, only for a seized compressor to destroy the new one. Go get one of the invertor testers, can be used on any invertor technology, and seeing how it's getting much more common, it's prob worth the expenditure.

  9. #9
    Join Date
    Aug 2008
    Location
    OMAN
    Age
    46
    Posts
    16
    Rep Power
    0

    Re: daikin vrv inverter compressor check

    Thank u for the responce i allready ordered inverter checker,compressor&inverter assembly from daikin waitinf for those parts as you said i will do the procedure and let you know the result..........
    thank you

  10. #10
    jullah2009's Avatar
    jullah2009 Guest

    Re: daikin vrv inverter compressor check

    hi
    can you explain the difference between the digital scroll compressor and inverter compressor

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: daikin vrv inverter compressor check

    Quote Originally Posted by jullah2009 View Post
    hi
    can you explain the difference between the digital scroll compressor and inverter compressor
    Please, start a new thread here and use search function!
    Last edited by nike123; 21-11-2008 at 11:37 AM.

  12. #12
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: daikin vrv inverter compressor check

    hi there,
    the difference between a digital scroll compressor and an inverter is that a digital scroll is very similar to an unloader which unloads the refrigerant, where as an inverter type uses variable frequency to speed up and slow down the compressor to vary the refrigerant volume.

Similar Threads

  1. daikin L0 inverter problem
    By robin r33 gtr in forum Air Conditioning
    Replies: 17
    Last Post: 12-03-2010, 12:25 AM
  2. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 09:44 PM
  3. Daikin inverter checker.
    By on4hf in forum Air Conditioning
    Replies: 9
    Last Post: 20-08-2008, 07:22 PM
  4. Problem with an inverter compressor in V.R.V system DAIKIN R 407
    By Harris Greece in forum Air Conditioning
    Replies: 10
    Last Post: 24-11-2007, 01:53 AM
  5. new daikin inverter kit
    By allyjg30 in forum Air Conditioning
    Replies: 4
    Last Post: 09-06-2007, 12:04 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •