14-10-2008, 10:37 AM #1
Cek leakage in evaporator
I have new an evaporator using TEV externally equallizer intalled in this unit. I want to test leakage using gas with high pressure about 10 bar and using detergent water. I will fill the gas from inlet TEV. Is it permitted ? Is TEV valve in open orifice or closed orifice in the ambient temperature. I buy TEV from danfoss type TE N 2. I'm worried the gas can not pass through TEV and I can not check leakage in the evaporator side and pipe externally equalizer that is connected in the out of evaporator tube because there is no pressure inside tube. Please need your advice
BR,
Yudha
-
14-10-2008, 11:21 AM #2
Re: Cek leakage in evaporator
Hello Cewek
The gas will pass through the TEV ok but it will be a little slow.
TE2 N is for r134a so why 10 bar test pressure for leakage. Please check manufacturer recommendations for maximum.
here is a link for the TE2
http://www.danfoss.com/NR/rdonlyres/.../PFA00A102.pdf
-
24-10-2008, 11:54 PM #3
Re: Cek leakage in evaporator
about the 10 bar of 134a I allways thought we used ofn for oressure testing
-
25-10-2008, 09:16 PM #4
Re: Cek leakage in evaporator
Last edited by taz24; 25-10-2008 at 09:19 PM.
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Designing Roll Bond Evaporator
By Munzar Ata in forum FundamentalsReplies: 11Last Post: 05-08-2010, 11:31 AM -
Absortpion Refrigeration - Evaporator Basics
By knudo in forum FundamentalsReplies: 4Last Post: 28-08-2007, 08:03 AM -
What is the best location for a evaporator fan?
By Jasno999 in forum FundamentalsReplies: 3Last Post: 21-02-2007, 12:34 AM -
Air Source Heat Pump - temp of refrigerant leaving evaporator
By anup in forum FundamentalsReplies: 3Last Post: 06-11-2006, 05:04 AM