    Cek leakage in evaporator



    I have new an evaporator using TEV externally equallizer intalled in this unit. I want to test leakage using gas with high pressure about 10 bar and using detergent water. I will fill the gas from inlet TEV. Is it permitted ? Is TEV valve in open orifice or closed orifice in the ambient temperature. I buy TEV from danfoss type TE N 2. I'm worried the gas can not pass through TEV and I can not check leakage in the evaporator side and pipe externally equalizer that is connected in the out of evaporator tube because there is no pressure inside tube. Please need your advice

    BR,
    Yudha



  2. #2
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Cek leakage in evaporator

    Hello Cewek

    The gas will pass through the TEV ok but it will be a little slow.

    TE2 N is for r134a so why 10 bar test pressure for leakage. Please check manufacturer recommendations for maximum.

    here is a link for the TE2

    http://www.danfoss.com/NR/rdonlyres/.../PFA00A102.pdf

  3. #3
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Cek leakage in evaporator

    about the 10 bar of 134a I allways thought we used ofn for oressure testing

  4. #4
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Cek leakage in evaporator

    Quote Originally Posted by sedgy View Post
    about the 10 bar of 134a I allways thought we used ofn for oressure testing

    With 134a you can pressure test to about 13bar
    and yes pressure testing is done with OFN but sometimes
    if the leak is small and hard to find then it has been known
    to use some Helium because of the molecular size of the
    134a.


    Cheers taz.
    Last edited by taz24; 25-10-2008 at 09:19 PM.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Designing Roll Bond Evaporator
    By Munzar Ata in forum Fundamentals
    Replies: 11
    Last Post: 05-08-2010, 11:31 AM
  3. Absortpion Refrigeration - Evaporator Basics
    By knudo in forum Fundamentals
    Replies: 4
    Last Post: 28-08-2007, 08:03 AM
  4. What is the best location for a evaporator fan?
    By Jasno999 in forum Fundamentals
    Replies: 3
    Last Post: 21-02-2007, 12:34 AM
  5. Replies: 3
    Last Post: 06-11-2006, 05:04 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •