Thread: Ammonia
-
13-10-2008, 11:11 AM #1
Ammonia
Greetings. One small technical question - we have evaporator coils not working efficiently. The design criteria is 120kW at -9C. The problem we are experiencing is that the compressor is running unloaded and cycling off, would indicate under-sized evaps. The product load is still high. What we suspect is the latent load of 34kW was not added onto the capacity of the coil. Thus we could be running a coil of 86kW. Do you suggest anyone who could shed some light on this problem?
-
13-10-2008, 11:24 AM #2
Re: Ammonia
Johnco,
It seems from your description that you may not have enough ammonia in evap to make anything happen.
You could check air on/off unit temps to see if is doing much work .
Also liquid line strainer etc .
What suction pressure/temp are comps controling and pressure/temp at evaps ?
Are fans going correct way ?
How are you supplying ammonia to evaps ie tx valve liq overfeed ?
-
13-10-2008, 11:26 AM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Ammonia
Measure airflow, air in temperature and humidity and air out temperature and humidity (or Wb and Db temperatures) and post here.
Then we could see if you have design capacity, or lower then required.
If you can not measure air flow, make sure that evaporator is defrosted and all fans working good and post nameplate or catalog data for air flow, but measuring is prefered.
-
13-10-2008, 02:53 PM #4
Re: Ammonia
Originally Posted by Johnco
Are these evaporators using thermostatic expansion valves?
And,
How high are the evaporator coils installed above the compressors/receiver?If all else fails, ask for help.
-
14-10-2008, 07:54 AM #5
Re: Ammonia
Thanks for the advice, just to mention this is a new installation and we have recently changed our coil supplier / manufacturer, therefore are under the impression there could be a problem with the design / manufacture of the evaporators.
We have done the checks and balances on the system, all seems to be in order.
ON coil 0°C
OFF coil -2.8°C
Evap Temp -9°C
Clean Coil / Face Velocity 4m/s
RH on coil 85%
TD 9
-
14-10-2008, 08:01 AM #6
Re: Ammonia
We have done the checks and balances on the system, all seems to be in order.
These are measurements taken on site.
ON coil 0°C
OFF coil -2.8°C
Evap Temp -9°C
Clean Coil / Face Velocity 4m/s
RH on coil 85%
TD 9
Coil icing up after 4hrs of operation
Thanks for the advice, just to mention this is a new installation and we have recently changed our coil supplier / manufacturer, therefore are under the impression there could be a problem with the design / manufacture of the evaporators.
-
14-10-2008, 08:03 AM #7
Re: Ammonia
We have done the checks and balances on the system, all seems to be in order.
These are measurements taken on site.
ON coil 0°C
OFF coil -2.8°C
Evap Temp -9°C
Clean Coil / Face Velocity 4m/s
RH on coil 85%
TD 9
Coil icing up after 4hrs of operation
Thanks for the advice, just to mention this is a new installation and we have recently changed our coil supplier / manufacturer, therefore are under the impression there could be a problem with the design / manufacture of the evaporators.
-
14-10-2008, 09:59 AM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Ammonia
Air flow please, not velocity!
Air flow you can get by measuring air speed at few places (more is better) on evaporator surface, find average value and multiply that with evaporator surface! For your case, it should be around 75000m^3/h if that evaporator has 120kW sensible heat capacity.
Also, air off humidity is required for precise calculation!
If possible, tell us model# and make!Last edited by nike123; 14-10-2008 at 10:07 AM.
-
14-10-2008, 12:59 PM #9
Re: Ammonia
Originally Posted by me
Capacity @ TD
volume flow of air
etc.If all else fails, ask for help.
-
14-10-2008, 01:07 PM #10
Re: Ammonia
We have measured the airflow to be 87,696m³/hr. The air-off humidity is 94%.
-
14-10-2008, 02:57 PM #11
-
14-10-2008, 03:22 PM #12
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Ammonia
This is what is calculated:
You should have -3,8°C evaporator OUT temperature to have 120kW sensible heat.
If that is ***** I would say that you check, and if necessary, adjust superheat because Tao-Te of 6,2K is high.
For Ammonia I don't have a clue what should it be, but I suppose also not more than 5K.Last edited by nike123; 14-10-2008 at 05:25 PM.
-
14-10-2008, 09:30 PM #13
Re: Ammonia
Product type and temp would also be interesting .
Also what happens after defrost of coil ? Does compressor load up .
Similar Threads
-
contaminants in ammonia systems
By Johnny Rod in forum RefrigerantsReplies: 29Last Post: 17-10-2011, 05:26 PM -
Want to be trained as an ammonia operator
By Randy Williams in forum NH3Replies: 7Last Post: 26-11-2008, 08:15 PM -
Releasing ammonia into the environment.
By Tycho in forum NH3Replies: 21Last Post: 03-02-2008, 05:10 PM -
Ammonia and CO2 reactor
By gwapa in forum NH3Replies: 18Last Post: 07-01-2007, 04:50 PM -
New Ammonia Certification in United States
By JerrydNH3 in forum NH3Replies: 11Last Post: 15-08-2006, 03:10 PM