    Chilled water bypass problem



    I have a question, does anyone have an opinion as to the best place to locate differential sensors in a chilled water system to control the chiller bypass. The system comprises of 3 off 3,000 kWR chillers and a single 1,00kWR, with the bypass in the chiller plantroom. The chilled water loop is large and during some conditions the system pressure falls and certain areas lack chilled water flow. This is a tricky one as starting multiple chillers to get the correct flow is not the most efficient way. Currently the sensor is in the plantroom about ten metres past the bypass.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Chilled water bypass problem

    Has the system been balanced correctly, or, if it is an older system, does it need rebalancing.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    MACT's Avatar
    MACT Guest

    Re: Chilled water bypass problem

    The system is balanced as well as it can be, but considering there is about 2km of pipe, 30 AHU's and 50FCU's I am not about to do a system rebalance. The question really is does anyone have any design experience with sensor location, is it better to have the sensor close to the chillers or better further away. Obviously the static setpoint will change due to friction losses the further down the run you get but that is easy enough to calculate.

  4. #4
    Join Date
    Feb 2006
    Location
    Mumbai
    Posts
    49
    Rep Power
    0

    Re: Chilled water bypass problem

    Hi Mact,

    Are you using primary only variable pumping system or primary secondary variable pumping system.

    Regards

    Vijay Kumar
    Vijay Kumar
    HVAC Design Engineer

    BMCPL

    "The more you sweat in peace less you bleed in war"

  5. #5
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Re: Chilled water bypass problem

    Do you have some drawing of system?

  6. #6
    MACT's Avatar
    MACT Guest

    Re: Chilled water bypass problem

    Sorry no drawings renato, the system is primary pumping only with no variable speed, each chilled water pump and chiller comes in based on calculated loads from return chilled water temps. There is no problem with water temps, just flow to the field drops if enough chillers aren't running and a heap of valves are open. What I may do is log the system pressure and various other points to check if there is a lag in the control design, or if the pressure sensor is accurate. I will also be able to find a far better sensing point further down the index run this way. THanks for all your help guys.

Similar Threads

  1. pure water from air
    By Lc_shi in forum New Technologies
    Replies: 32
    Last Post: 26-02-2009, 12:25 PM
  2. Energy saving in Chilled water system
    By psrao in forum Tools and Calculators
    Replies: 5
    Last Post: 15-01-2008, 06:54 PM
  3. water pressure problem
    By Renato RR in forum Technical Speculations
    Replies: 3
    Last Post: 13-02-2006, 07:54 AM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  5. chilled water PHE
    By priti in forum Trouble Shooting
    Replies: 1
    Last Post: 31-07-2002, 08:25 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •