Results 1 to 12 of 12
    Feb 2008
    Sudan
    89
    Copper pipes pressure test
    Hi guys.
    I'm going to start a pressure test for 30 hp VRV-WII piping sysem.
    DAIKIN said don't pressurize more than 40.
    Our ambient temperature is variable and we afraid from the increasing of the pressure (causing damages in the equipments) due to temp increasing.
    Can I decrease the test pressure to 35 bar to prevent the damages. Is 35 enough?
    Thanks.
    Split Croatia
    57
    6,151
    36
    Re: Copper pipes pressure test
    You should do piping test before connecting equipment!
    Rise in pressure is 0,1bar per 1K ambient temperature rise! Predict highest temperature and pressurize according to difference in expected and present temperature.
    Feb 2008
    Sudan
    89
    Ok nike, very nice information.
    By the way I will do piping test after connecting equipment to test the flare connections (in& out).
    Thanks nike I will carrying out my test at 39 bars according to your informations.
    Split Croatia
    57
    6,151
    36
    Quote Originally Posted by 2007eng View Post
    That is leak test!
    It doesn't need to be carried out at that high pressure, and also you have possibility that nitrogen goes to outdoor unit thru leaking valves and you end up with non-condensables in system.
    For leak test with nitrogen 15 bar/12-24 hours is sufficient. Note ambient temperatures and pressures after temperature is equalized after pressurization (~2 hours later) and at the end of test.
    Feb 2008
    Sudan
    89
    Hi nike,
    The normal operation compresser pressur is 38 bar, you know that if there is a minor leaks on the system its dosn't appear when testing under low pressur.
    Split Croatia
    57
    6,151
    36
    Hi nike,
    I am sure that leaks at flares will show up even at 15 bar!
    But, you stick with what is manufacturer said!
    I usually make all piping work before and do pressure test at 45 bar. and then connect equipment and test with nitrogen and trace gas (r22) at 15 bar with electronic leak detector. No leaks yet!
    Feb 2008
    Sudan
    89
    By these steps I agree.
    I'm very happy to exchanging experience with a man like you.
    Thanks nike.
    Split Croatia
    57
    6,151
    36
    Thanks nike.
    I am glad to help!
    Mar 2006
    Merate (LC) - Italy
    2,549
    Is that a pressure burst test or a leak test?
    Leak test can be done at any pressure, while the pressure test has to be done in accordance with your country safety codes. Here in the EU it is according to 97/23/EC directive (PED)
    Feb 2008
    Sudan
    89
    Quote Originally Posted by NoNickName View Post
    It's a leak test. Thank you for this point
    Sep 2008
    Cheshire
    5
    From what I remember its.....
    leak test 1.1 x mwp
    strength test 1.3 x mwp
    (maximum working pressure)
    But if daikin tell you to not go over 40 bar you shouldn't.
    Cheers.
    Feb 2008
    Sudan
    89
    Quote Originally Posted by Chill'D View Post
    leak test 1.1 x mwp
    Cheers.
    Thanks for help.
  1. Leak Testing?
    By Thana in forum Trouble Shooting
    Last Post: 31-08-2010, 02:57 PM
  2. Compressor loading, cooling, and range of operation.
  3. Benji
  4. Building a wine cabinet