    First post, please be nice, prob with heat mode

    Hello Gents

    My first post hope you guys can help me.

    DOnt want to call out a service tech as we feel we get fobbed off all the time.

    We have 2 indoor convertible units connected to a multi split system one in in the living room & the other in our extension at the back. The system works perfect in cooling, maintaining room temp to within 1 degrees C, so comfortable room conditions are always possible in this mode.

    However we are having a problem with the maintaining of room temps. THe system has no problem outputting heat but far too much of it.

    If a temp of 22c is selected on the controller, the unit will sometimes continue until room temp reaches 3 or 4 degrees above this limit, meaning the temperature is very high and uncomfortable, and when the unit needs to kick back in it doesnt come back on quick enough meaning large differences in room temperature. We have noticed that the unit doesnt measure the room temp once the thermostat has shut off as the fan stops completly and doesnt come on again until well below set point as I guess it is measuring the temperature inside the unit which is going to be warmer as the thermister is behind a nice warm filter! I know that the coil sensor will stop the fan operating if its below 28c but in the manual still states the fan shud operate for 10seconds every 3mins to measure ambient... it doesnt do this and lg say it should do this despite their manual saying otherwise!

    We have measure the temp at the intake of the unit where the sensor is and we have noticed because these are mounted below our window sill about half a foot from the floor that the temperature down there is usually 1 or 2 degrees below what our digital thermometer says on our mantel piece. SO this is probably why it is not shutting off at about 22/23 as it hasnt reached that desired temp at the intake sensor.

    We are not sure what to do as presently we feel we are not getting benefits from the unit and will revert back to our cheap portable electric heaters as these maintain the temp better.

    We want to know what our options are with regards to this, the equipment is LG (some sighs i hear from doing a search on LG) LG say there isnt a fault with the units and we feel we are getting fobbed off our installer also doesnt seem to think there is a fault.

    We have had to look into matters our self and had advise of heating engineers

    We have noticed that if the sensor is poking out the intake grille so it is sensing the room air the unit comes back on if the temp drops below the set point by about 1.0c so we know that if its inside the unit in its correct place because the fan doesnt "cycle" every 3 minutes this is why room temp drops too much.

    We also have figured out that because the temp at floor level is going to be cooler than at the mantel piece this is probably why the unit is staying on for a lot longer with the large temp increases.

    With this being an inverter as well we find it still cycles on and off everytime it reaches thermostat off, it doesnt seem to wind down enough and it uses more electricity than it did on cooling mode when the outdoor temp is about 12c so its not having to work that hard either! The whole reason we spent so much on a system was to save money!!! Sometimes the actual time the system is giving out heat can be as little as 4minutes on and then 15minutes off. Is this bad for an inverter as we were told they dont shut off only wind down. Again on cooling mode works perfectly no probs whatsoever, with longer cycles on but still cycles off at set point. The units were purposely oversized so that they can heat and cool the entire ground floor of our house which they do very well! They were oversized by about 1.5kw we were told at install to allow for this? Perhaps this explains the cycling issue also in heat mode?

    What can we do now to avoid these large temp increases? Is it possible to install one of those room thermostats like you control your central heating with as these are very precise i think? Our hotel room on holiday had air con where you could only control the room temp and had the same as in the pic attached. Room temp was always perfect.

    Sorry for the long war and piece but judging from other peoples posts it seems that you guys prefer to have more information than not enough.

    Equipment are LG 3.5kw Convertible units.

    Kindest regards
    Julia
    Attached Images Attached Images

  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: First post, please be nice, prob with heat mode

    Did you cleaned filters recently?
    What is fan speed setting!
    I think that, mostly, problem is in placement of indoor unit.
    You could find some electrician to relocate indoor unit air temp. sensor to position of about 1,5 m height and far from windows, and heat sources.
    Last edited by nike123; 12-10-2008 at 01:58 PM.

  3. #3
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    Quote Originally Posted by nike123 View Post
    Did you cleaned filters recently?
    Filters are cleaned every 2 weeks, we know this is not a problem with the filters as they are always spotless.

    We clean them more often than they need to be cleaned, when we take them out they have nothing in them but we like to keep everything dust free.

  4. #4
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: First post, please be nice, prob with heat mode

    No, those controllers are no good, this is an inverter system and a simple wall thermostat does not interface with them.

    May be an install problem, are the units mounted very high, close the the ceiling?
    Or mounted above book cases, in corners or recessed walls?
    Are the unit's mounted very close to the outdoor unit (1m or less pipe work between them)?
    Do you run the indoor fan on high, or do you run it on quiet/super low/low?

  5. #5
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    Quote Originally Posted by paul_h View Post
    No, those conrtollers are no good, this is an inverter system and a simpe wall thermostat does not interface with them.

    May be an install problem, are the units mounted very high, close the the ceiling?
    Or mounted above book cases, in corners or recessed walls?
    Are the unit's mounted very close to the outdoor unit (1m or less pipe work between them)?
    Hello Paul

    Thank you for such a quick reply, we have got the units mounted under our baywindow in our lounge see picture attached.

    Distance to outside pipework on one unit is about 2metres.

    The lounge unit is about 1foot off the floor where the other unit is about 1.5 foot off the floor, both units have the same problem but the other unit one being higher off the ground seems to maintain temp better.

    Pic attached is the position of indoor unit in lounge, the main problem unit!
    Attached Images Attached Images

  6. #6
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    Forgot to add, we run the fan in low speed, we have 3 speeds, low, med or high, we find that because the units are oversized if we run them on high cooling and there are is a small cooling load it reaches set point far too quick, cooling is performed best in low speed so we assumed the same would be for heating. We have tried the system operating with the louvres also operating but find that it then reaches set point too quick as i assume warm air is directed to all levels of the room but then set point is reached at the unit very quick and our digital thermometer on the mantle piece is usually still below the 22c.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: First post, please be nice, prob with heat mode

    Quote Originally Posted by back2space View Post
    Forgot to add, we run the fan in low speed, we have 3 speeds, low, med or high, we find that because the units are oversized if we run them on high cooling and there are is a small cooling load it reaches set point far too quick, cooling is performed best in low speed so we assumed the same would be for heating. We have tried the system operating with the louvres also operating but find that it then reaches set point too quick as i assume warm air is directed to all levels of the room but then set point is reached at the unit very quick and our digital thermometer on the mantle piece is usually still below the 22c.
    Put fan at auto and try like that few hours!
    Also check my first post, it is updated!

  8. #8
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    Quote Originally Posted by nike123 View Post
    Put fan at auto and try like that few hours!
    Also check my first post, it is updated!
    Thank you, we dont have an auto fan setting. I have checked your first post as well, not sure about the location of the unit, it is a rectangle shaped room approx 4 by 5metres.

    it is mounted on the widest part of the room so blown across the width of the room.

    And how do we go about getting the sensor mounted further up the wall, it seems only a small cable and not long enouogh to mount up the wall but then we would want a neat fitting we dont want a black thermister cellotaped to the wall so to speak!

  9. #9
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: First post, please be nice, prob with heat mode

    With a normal split, they are designed for cooling. When they go into heat mode, the indoor unit is really undersized for the job of heating. It's better to run the fan on high when using a split on heat, otherwise they may overheat or incorrectly sense room temp and shut down the compressor speed.
    Inverters don't cycle normally, if yours is cycling on and off it's may be cutting out on a fault, like overheating.
    That's what i suspected at first with your issues, but most of what I said doesn't apply due to the fact you are running floor consoles rather than hi wall mount splits (ie close to the ceiling).
    If your system doesn't run better with high fan, you may have a piping or unit problem, or it may be a manufacture/design fault.
    sorry, I've never seen floor mount LGs, so I'm no expert on them.
    But basically most systems will shut down if the discharge pipe temp in the outdoor unit gets too hot, or they will slow the compressor down if the indoor coil temp gets too hot. Either can be caused by poor installation or even a fault with the unit.
    In australia, all such follow up work is done by the companies engineers or contracted people who know the system well. I really don't know what you can do in the UK when you have only the installer to deal with and no one to check the system out fully.
    There's an LG rep that is a member here and can maybe help, his name is hendrag and he does UK support for LG.
    Last edited by paul_h; 12-10-2008 at 03:39 PM.

  10. #10
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    We have spoken to him before, apparently they tested the same setup as ours in their workshop and they say the system worked fine. The installer checked all the piping and everything that he could. They say the units should heat up to +4C of the set point, but to be honest I think this is a load of rubbish as the manual states that it will only do this if it is mounted on the ceiling and set in that mode, which has been deactivated anyway.

    The problem seems to be that it doesnt monitor the temp. However if the unit 2 is blowing warm air and the unit 1 is thermo off then as long as their is warm refrigeratn circulating then the unit will do the 3 minute sample of air thing. However if both units are thermo off then no warm refrigerant circulating thus no monitor of air temp unless we place the thermister outside the unit in the room air. The only reason we can see that the units are cycling in cooling and heating more so in heating is because they are oversized and apparently it cannot adjust quick enough before the room temp goes over its setpoint??? I dont know if they are talking rubbish. The units are definatly not undersized though, this unit we have kicks out 4kw of heat and a small 2kw fan heater will heat the room just as well!

    I wish it didnt cycle though as much because in cooling it maintains it so well on hot days its only the cooler days where it cycles.

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: First post, please be nice, prob with heat mode

    What is indoor unit model#?
    By description it also could be that indoor units cables are mismatched.
    Last edited by nike123; 12-10-2008 at 03:55 PM.

  12. #12
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    MV12AH NE0 is the indoor unit.

  13. #13
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    What do you mean by mismatched?

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: First post, please be nice, prob with heat mode

    Quote Originally Posted by back2space View Post
    What do you mean by mismatched?
    When indoor unit pipes and cables are not connected at their respective places.

    Like 1. indoor unit cable is connected at A cable place at outdoor unit and pipes of same unit are connected at B place and vice versa for 2. indoor unit.

    It appears that everything works but temperature control and behavior is sometimes odd.

  15. #15
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    Quote Originally Posted by nike123 View Post
    Put fan at auto and try like that few hours!
    Also check my first post, it is updated!
    Quote Originally Posted by paul_h View Post
    With a normal split, they are designed for cooling. When they go into heat mode, the indoor unit is really undersized for the job of heating. It's better to run the fan on high when using a split on heat, otherwise they may overheat or incorrectly sense room temp and shut down the compressor speed.
    Inverters don't cycle normally, if yours is cycling on and off it's may be cutting out on a fault, like overheating.
    That's what i suspected at first with your issues, but most of what I said doesn't apply due to the fact you are running floor consoles rather than hi wall mount splits (ie close to the ceiling).
    If your system doesn't run better with high fan, you may have a piping or unit problem, or it may be a manufacture/design fault.
    sorry, I've never seen floor mount LGs, so I'm no expert on them.
    But basically most systems will shut down if the discharge pipe temp in the outdoor unit gets too hot, or they will slow the compressor down if the indoor coil temp gets too hot. Either can be caused by poor installation or even a fault with the unit.
    In australia, all such follow up work is done by the companies engineers or contracted people who know the system well. I really don't know what you can do in the UK when you have only the installer to deal with and no one to check the system out fully.
    There's an LG rep that is a member here and can maybe help, his name is hendrag and he does UK support for LG.
    We are even concerned as in cooling the compressor runs very slow hardly at all but in heating it whirs away and outside ambient is usually 12/13c it doesnt seem to slow down, even on low fan speed.

    They have checked the inverter and they say it will run faster in heating due to more work involved to remove heat from the air but we would expect it to wind down a lot even if its 1c off set point and try to maintain it, it just seems it dont slow down enough and this is when it goes way over set point due to the ammount of heat coming from it? But perhaps the position of the sensor is making it think setpoint is lower than it is?

  16. #16
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    Would be interesting to find out engineers opinions who have worked on these units in the past.

    Nike123, seriously though thank you for your help so far. I would give you more reputation but it wont let me do it again!

  17. #17
    Join Date
    Mar 2005
    Location
    Lanzarote
    Age
    41
    Posts
    372
    Rep Power
    20

    Re: First post, please be nice, prob with heat mode

    Probably not that then. What Nike123 means is that the communication wires between each indoor unit to the outdoor have been crossed. So the outdoor unit reads the temperatures from unit A, but supplies the hot refrigerant to unit B, and not units A as it should. Easy was to find out is switch just one of the indoor units on and see which set of pipes at the outdoor unit get hot. Be careful, because the pipes could be really hot.

  18. #18
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    Ok just done this the units are wired correctly as the one i switched on got hottest. The other one got warm but we were told its normal for refrigerant to circulate amongst the other unit to allow for oil return, The EEV is open 10% on the unit that is switched off in heating.

  19. #19
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: First post, please be nice, prob with heat mode

    Hi Back2space and welcome to the forum, it looks like you're getting lots of input to your problem already.

    One question from me, what type of controller do you have ?

    Sorry, 2 questions; is it a wall mounted controller or wireless.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  20. #20
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Smile Re: First post, please be nice, prob with heat mode

    Hi Brian

    Thank you for the warm welcome, this site is really friendly wish I had asked the initial questions on here rather than being given the run around by lg etc.

    I have a background knowledge of ac as I used to work in a helpdesk logging maintenance jobs for ac. we would log the faults and dispatch engineers, so I have knowledge of the "jargon" most would call it! SO being technical is not going to blag me so to speak!

    We use remote controls to operate the units, I wanted hard wired as I know that some have remote sensors in them that you can use instead of the intake sensor which in this case is low down the wall in the unit sucking in cooler air I work out!

    However our units (MV12AH) cannot be operated off hard wired so we have to use the remote controls.

    There is no problem with any wiring, initially the intake sensor was out of calibration on one of the units and in cooling it was 1C out of the setpoint, so if you was set 21C on the remote the unit aimed for 19 and then came back on at 21C when really it should aim for 20 and come back on at 22C.

    Thats all fixed now and cooling mode works perfect, just this damned heat mode we need to sort!

    Oh and rep added for being so polite!

    I have to ask wheres the biscuit tin I feel like im going to stick around and get involved on the forum!

    Kind regards

  21. #21
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: First post, please be nice, prob with heat mode

    Sorry, we don't do biscuits here it's doughnuts or nothing

    Yes I had asked because of the sensor in the remote and doing a quick look through the LG site http://mylg.co.uk after I had posted made me think that you would only have a wireless control. (Damn-it, strike one idea)

    I even see that there is a 'tech note' covering your problem exactly complete with a "tough luck" answer to it.

    I tend to go with previous suggestions about relocating the sensor.

    I suppose you could go exotic and buy some spare sensors. These could be mounted were you wanted and connected via a changeover switch with the unit sensor. Then you could chose which sensor you wanted depending on the mode selected.

    Why have easy when complicated costs more ??


    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  22. #22
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    Brian

    Ill have 2 donuts please! With Jam in!

    I have seen a technical note on there (product information sheet) , see below:

    It specifically states that cassettes and convertible units have the control strategy of 10seconds fan on every 3minutes to sense temperature. However LG say that that is a mistake and they dont mean convertables... i am being fobbed off totally here I think! THey either dont want to admit that the software of air con hasnt had this feature written into it when the coil sensor says that there is no hot gas circulating. As this control strategy works as long as one unit somewhere is giving out heat as refrigerant circulates through all units for oil return in heating mode.

    Have you seen a different techie sheet or are we reffering to the same: See below:

    <DIV dir=ltr align=left><SPAN class=140422204-04092008><DIV dir=ltr align=left>Product Technical Update Sheet 76

  23. #23
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    Not sure why the copy and paste aint working.

    See below as I have now copied into a word document. SOrry for the above few posts being rather blank!

    I have physically added the data sheet now that I have seen if there is another one Brian that you have come across can you attach it as mylg doesnt seem to be working tonight.
    Attached Files Attached Files

  24. #24
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: First post, please be nice, prob with heat mode

    Don't try to cut and paste from webpages, just copy the website address from your browser and post that as here...

    http://mylg.co.uk/data%20for%20site/...%20heating.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  25. #25
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    I am getting some random site coming up when clicking on that.

    CAn you put it into a word document, i think the mylg website is down its taking me to some travel media shopping thing.

  26. #26
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: First post, please be nice, prob with heat mode

    Just tried it again, works fine for me.

    "http://mylg.co.uk/data for site/Prod sht 76 my unit operates wierdly in heating.pdf"

    Also, be aware that cutting and pasting Word documents into your post may cause corrupted posts and is sometimes disallowed by the system.
    Last edited by Brian_UK; 13-10-2008 at 11:57 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  27. #27
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    Hmmm maybe problems with our internet (im at work) does it say anything different to the fact sheet 76 I attached.

    Thank you.

  28. #28
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: First post, please be nice, prob with heat mode

    Nope, same text, same non-helpful content.

    Anyway, I'm off to sleep now; hope you have a quiet night...
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  29. #29
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    Thank you Brian, I hope its quiet now.

    Could you elaborate on these extra sensors Malarky?

    I was wondering if theres a better controller out there for it?

  30. #30
    Join Date
    Feb 2008
    Location
    QLD
    Age
    54
    Posts
    74
    Rep Power
    17

    Re: First post, please be nice, prob with heat mode

    When it is called a convertible, does that mean this unit can be fitted under the ceiling, as well as on the floor?

    In that case, I have seen these issues before on another brand, and the indoor unit had a link or DIP switch to alter the thermostat characteristic, to allow

    The unit cycling on and off, is most likely due to being oversized.
    even if the unit winds down to the lowest speed, it is still heating more than required, quite common is autumn and spring.

  31. #31
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    Quote Originally Posted by stefs_cruiser View Post
    When it is called a convertible, does that mean this unit can be fitted under the ceiling, as well as on the floor?

    In that case, I have seen these issues before on another brand, and the indoor unit had a link or DIP switch to alter the thermostat characteristic, to allow

    The unit cycling on and off, is most likely due to being oversized.
    even if the unit winds down to the lowest speed, it is still heating more than required, quite common is autumn and spring.
    Hi there

    THanks for your reply, yes being a convertible it means it can be fitted under the ceiling or on the floor similar to how a radiator would be mounted. There is a switch inside the unit that you turn on if the unit is to be mounted on the ceiling, this then means that there is a temperature offset in heating of +4 degrees so the unit will heat to 4c above setpoint to allow for the heat that has risen at ceiling height. One of the units was set to this option by mistake but this was rectified, however these problems are still happening however its not the unit that is trying to heat to +4c as the air intake hasnt usually gone above the setpoint (we tested with a digital thermometer at the intake) and intake temp at floor level was sometimes 3C lower than at the mantel piece level.

  32. #32
    Join Date
    Feb 2008
    Location
    QLD
    Age
    54
    Posts
    74
    Rep Power
    17

    Re: First post, please be nice, prob with heat mode

    to allow for stratification, not quite sure how that bit disappeared :-)

  33. #33
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    Yes all is sealed well with expanding foam! I dont like draughts so I checked this over after the install.

  34. #34
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    Any one else got any input?

  35. #35
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: First post, please be nice, prob with heat mode

    Thinking sideways, as I do sometimes....

    Can an adjustable resistor be fitted into the sensor circuit?

    You could then use that to 'offset' the temperature being sensed and fool the controls.

    Visually you would end up with a small rotary knob on the side of the unit.
    Last edited by Brian_UK; 18-10-2008 at 10:57 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  36. #36
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    Not sure really I wouldnt be able to do this anyway if it was possible.

    I think the best thing to do is get the sensor mounted further away from the unit.

    Question is how can i get this done!

  37. #37
    murran's Avatar
    murran Guest

    Re: First post, please be nice, prob with heat mode

    Hi, I am new to the forum.
    I do not have a lot of experience with multi splits as ive worked mostly with larger industrial airconds.
    Ive read through all the info and what I can add is the fact that the aircond is at ground level will influance the heating capacity in particular due to the fact that heat rises.
    The temp at celing will be easily 3C higher than floor level. This means that by the time setpoint is reached at floor level where the sensor is situated the room temp will be a few degrees higher.
    To compensate for this you could set your thermostat at least 2 degrees lower than what you want instead of moving the sensor.
    The fact that it is running at full capacity for a short period suggests undersized unit.?
    The other factor in heating cycle is the outside temp.
    If it is very cold,the unit will ice up(this is normal) and goes into defrost cycle shutting down the heating for short periods.
    The best solution in my opinon is to relocate the aircond to ceiling level & to make sure you have sufficent capacity condensor.

    Hope this helps.

  38. #38
    Join Date
    Jan 2008
    Location
    Somerset
    Posts
    77
    Rep Power
    17

    Re: First post, please be nice, prob with heat mode

    Hi Back 2 Space,
    Please bare with me as I don't work on splits (much) and haven't posted here for quite a while, so you could say I'm a bit rusty. Personally speaking, I would definitely look to relocate the sensor. I would have thought that LG have a remote sensor available for this unit or failing that any electrician could extend the cable for you. It's interesting though that it doesn't vary the compressor speed on heating as well. I would have looked for a DIP switch to correct this as well. Is it the same problem on both indoor units? You could also try putting the sensor in ice to see if it runs for more than 4 minutes. This would indicate whether it is stopping on temperature or fault (if no fault indication is present).
    Hope this helps,
    Regards,
    Stuart

  39. #39
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    When i touch the sensor with warm fingers the unit will switch off. We have measured the intake temp and this is always about 1c lower than the actual room temp, i assume because of the high ceilings the floor is always going to be cooler.

    The sensor is therefore working correctly. The unit varys comppressor speed in cooling and i assume it is doing so in heating although maybe because it is oversized it cant slow down enough.

    LG say there is no remote sensor for this model and that they would charge for an extension of the sensor! Hardly fair!!!!

  40. #40
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: First post, please be nice, prob with heat mode

    Quote Originally Posted by back2space View Post
    When i touch the sensor with warm fingers the unit will switch off. We have measured the intake temp and this is always about 1c lower than the actual room temp, i assume because of the high ceilings the floor is always going to be cooler.

    The sensor is therefore working correctly. The unit varys comppressor speed in cooling and i assume it is doing so in heating although maybe because it is oversized it cant slow down enough.

    LG say there is no remote sensor for this model and that they would charge for an extension of the sensor! Hardly fair!!!!
    Who has made decision for indoor unit position? You or them?
    If you insisted that it must be there, then I don't see how is that not fair!
    If they are insisted with placement of unit there and did not tell you about possible difficulties with room temperature control, then they are responsible.

  41. #41
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    They told me where they were putting the unit as this was really the only place to put it with the outside wall, its a victorian house and it kept pipe runs to a minimum as well. If it had been mounted anywhere else in the room on another wall i think it would have been the same problems. There a no draughts from the windows at all and the unit behaves fine in cooling but it seems that the hot air is taking longer to fill the room due to stratification so taking longer to circulate to the lower floor area. if the louvre is set to move up and down itself then the unit reaches set point very quick but the actual room temp is lower than the unit thinks then due to warm air cycling back into the unit.

  42. #42
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: First post, please be nice, prob with heat mode

    Quote Originally Posted by back2space View Post
    They told me where they were putting the unit as this was really the only place to put it with the outside wall, its a victorian house and it kept pipe runs to a minimum as well. If it had been mounted anywhere else in the room on another wall i think it would have been the same problems. There a no draughts from the windows at all and the unit behaves fine in cooling but it seems that the hot air is taking longer to fill the room due to stratification so taking longer to circulate to the lower floor area. if the louvre is set to move up and down itself then the unit reaches set point very quick but the actual room temp is lower than the unit thinks then due to warm air cycling back into the unit.
    What you want is the unit to cycle off quicker. Iow a shorter heating cycle. You mention the solution yourselv in the quote. If the overall room temperature then gets to low you have to increase the set point until you acheive the correct room temperature.

    Generally speaking it is impossible to acheive an even heat distribution in the room without the direction of the air flow be either horisontal or downvard say 45 degrees. Downvard 45 degrees for ceiling or high wall inndor units and as close to horisontal as possible for low wall units. It is however important that no furnitures is in front near the inndor unit as this will cause excessive short cycling.
    Last edited by SteinarN; 21-10-2008 at 08:02 AM.

  43. #43
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: First post, please be nice, prob with heat mode

    I assume being a Victorian house that you therefore have quite high ceilings.

    If this is the case then there might be a valid argument for installed a ceiling fan the destratify the air.

    If the fan is used to draw the air upwards then the warm air is circulated without draughts.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  44. #44
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    Quote Originally Posted by Brian_UK View Post
    I assume being a Victorian house that you therefore have quite high ceilings.

    If this is the case then there might be a valid argument for installed a ceiling fan the destratify the air.

    If the fan is used to draw the air upwards then the warm air is circulated without draughts.
    Yes we have the high ceilings and we also have a ceiling fan in the said rooms, the bedroom unit seems to reach temperature better but this is mounted about another foot higher from the floor than the lounge one (problem one)

    The bedroom one is fine even without the ceiling fan on.

    If the lounge one is operated with the ceiling fan in reverse then we end up with an even worse a situation as the air is sucked upwards and thrown down the sides of the walls thus cooling it at the same time.

  45. #45
    Join Date
    Mar 2005
    Location
    Lanzarote
    Age
    41
    Posts
    372
    Rep Power
    20

    Re: First post, please be nice, prob with heat mode

    I was just going to suggest the exact same thing as Brian.

  46. #46
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: First post, please be nice, prob with heat mode

    I really do get the impression that that unit is well oversized.

    The hot/warm air being lifted by a ceiling fan should not really create a major change of effective temperature. Unless, the air is being heated in chunks (wrong word but can't think of a better one).

    This is always the drawback of blown warm air heating, as soon as the temperature of the supply air changes everybody notices.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  47. #47
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    The unit behaves perfectly in cooling however still cycles on and off, i dont think it can ramp down enough.

    We had various quotes, most quotes said we needed 12000btu unit for cooling, however one firm said a 10000btu unit???

    Obviously in cooling the indoor unit (MV12AH outputs 3.52kw of max cooling, however in heating it seems the max output increases to 3.87kw so slightly higher. See link and scroll to specs.

    http://mylg.co.uk/data%20for%20site/...onvertible.pdf

    Now when you compare this to the min/max outputs of the the outdoor unit, the max rated capacity of the outdoor in cooling is 8.5kw and the min capacity in cooling is 1.85kw whereas in heating the max is 9.38kw and the min is 2.22kw.

    Now it does say that the unit should be able to ramp down to 2.22kw which is 6300btu. Surely if the one guy said 10000btu was needed for cooling then similar capacity is needed for heating.

    Starting to get confused with the figures but i know the unit is oversized but we need this extra capacity as when we have friends over we have a full room then the unit doesnt tend to cycle it will ramp right down in cooling.

    HMMMMM me confused you all now i bet!

  48. #48
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    the above details are for the multisplit system that I have. The indoor units are the same as the type I would have if it was just a standard back to back split.

    Now what I have also looked into is the min/max ratings of standad back to back 3.5kw inverter split condenser unit. (1 indoor 1 outdoor)

    I notice straight away that the standard 1 on 1 split can ramp its capacity down lower than my multi split condenser.

    Cooling min = 1.40kw
    Heating min = 1.62kw

    So if on my multisplit condenser it has ramped right down to 2.22kw in heating and this is still too much for the room its going to cycle off isnt it. In cooling its cycle on is longer than a cycle in heating.

    Another worry is how do inverters handle short cycling issues? i know standard fixed speed ones wear out.

    In heating the unit cycles on for 6 minutes and then its off for about 20minutes.

    In cooling it will be perhaps 10 mins on and then 10 mins off.

  49. #49
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    Hi Murran

    Welcome to the forum, thanks for your input, everything so far is leading to the unit being oversized as it does not struggle whatsoever with heating the room at all in fact it is overheating the room, cooling likewise however precision temp control on cooling mode probably due to the way cool air circulates back to the unit.

    THe unit has never gone into defrost mode yet hasnt been cold enough does a oil recovery thing every 6 hrs though kind of like defrost operation but theres no icing up.

    We think the unit is operating at high speed when it kicks back in at thermostat on but the room is heating up quicker than the inverter can adjust to conditions so ends up cycling off.

    We tried compensating with lower set point (20) and found that whilst the temp at cycling off was more suitable (22). The unit would then not kick back in till the room temp had actually dropped to 19C so there was a big diff in temp, not ideal for a lounge.

  50. #50
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: First post, please be nice, prob with heat mode

    By short cycling what sort of lengths of time do we consider a short cycle?

    My units cycle on for about 5-7minutes and then off for 20 or longer on the heat operation

    In cooling its 7mins on and then off for ten minutes or a little less.

    Do inverters wear out this way, is it bad for them?

Page 1 of 2 12 LastLast

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  3. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •