Thread: gravity coil
12-10-2008, 05:29 AM #1
gravity coil
Hi Folks
It's been a while since I have been around here. I see plenty interesting topics to read but now I have a problem and need some help.
I have been searching for design info on natural convection cooling coils (gravity coils) and come up blank on all counts.
I have searched heat transfer text books, ASHRAE Handbooks, manufacturers data sheets, web...
The only text book cases I find are
- vertical or horizontal plates
- vertical or horizontal cylinder
- sphere
But, what are people using to calculate the duty of a fin and tube coil with natural circulation?
The closest I have found is a detailed review of natural recirculation systems by Harwell and the best match here is a tube bank.
Could it really be that there have been no studies on these coils.
I am expecting a correlation for the Nusselt number. This could be of the form
Nu = C (Gr Pr)^n
where C and n are determined by measurement.
Any info or feedback would be valued.
18-10-2008, 12:12 PM #2
Re: gravity coil
Someone must know how to calculate a gravity coil!
18-10-2008, 04:13 PM #3
Re: gravity coil
It's nice to see you back here and posting again.
I have never had to sit down and do what you are asking. Is this an academic exercise you are looking at?
My first impression would be based on the buoyancy effects due to air density differences. As the rate of air movement begins in the room the Reynolds number would reach a mean average, which could be used for a Reynolds number. Then you start the heat transfer calc.'s for a finned tube.
This is a really good question though. I do not think I have ever seen a study/report on this either.If all else fails, ask for help.
18-10-2008, 10:37 PM #4
Re: gravity coil
I seem to remember this information being in the old ASHRAE manuals from the 1950s.
19-10-2008, 06:42 PM #5
25-10-2008, 02:09 PM #6
Re: gravity coil
Thanks guys,
My earliest ASHRAE books only go back to the 80's but I will check with my more senior friends. I did notice that good design info was dropped over the years.
I took on this task for a US manufacturer, thinking that it would be easily to find info. I should have checked the books first!
In light of the lack of design info, I have proposed a simple test using a coil, hot water and a short vertical section of duct. I will run it at my local Uni as a student project and have some interest from an Australian Uni to do similar.
Evaporative Condenser in reverse cycle
By Friobernal in forum IndustrialReplies: 6Last Post: 16-04-2009, 02:06 PM -
heating coil or cooling coil?
By botching in forum Air ConditioningReplies: 8Last Post: 09-06-2008, 08:37 PM -
Dont be shy, advice needed.
By Sledge in forum Air ConditioningReplies: 9Last Post: 27-06-2007, 03:09 PM -
Burst Coil
By frank in forum Air ConditioningReplies: 13Last Post: 20-02-2005, 07:28 PM -
Article in ACH&R News
By Gary in forum FundamentalsReplies: 8Last Post: 20-05-2003, 12:27 AM