    Poor performance provision freezer



    Hi there. Im new to this forum, and hope you guys can help me out with a problem.
    Onboard this ship we have a provision cooling/freezing system consisting of 2 evaporators (one freezer and one in the cooling room) and two compressors sharing a common liquid line. Each compressor has its own condenser. System is running on R404
    Experiencing very low performance when running compressor 2. Suction pressure barely over 0 bar Head pressure around 12 bar. Freezer Evaporator temp is only -6C. Liquid is visible in sight glass wet indicator is OK.
    No problems when running compressor #1. -21C temp head pressure 15bar and suction pressure 1bar
    We recently needed to remove a lot of oil from comp2 as it fills up while comp1 is loosing oil when its running.
    We removed almost 2 liters. Max volume in sight glass is about 1 liter.
    After we removed oil from comp 2 we can see foaming inside the crankcase. Can all this be due to a faulty reed valve?



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Poor performance provision freezer

    Quote Originally Posted by CHENGTRIT View Post
    Hi there. Im new to this forum, and hope you guys can help me out with a problem.
    Onboard this ship we have a provision cooling/freezing system consisting of 2 evaporators (one freezer and one in the cooling room) and two compressors sharing a common liquid line. Each compressor has its own condenser. System is running on R404
    Experiencing very low performance when running compressor 2. Suction pressure barely over 0 bar Head pressure around 12 bar. Freezer Evaporator temp is only -6C. Liquid is visible in sight glass wet indicator is OK.
    No problems when running compressor #1. -21C temp head pressure 15bar and suction pressure 1bar
    We recently needed to remove a lot of oil from comp2 as it fills up while comp1 is loosing oil when its running.
    We removed almost 2 liters. Max volume in sight glass is about 1 liter.
    After we removed oil from comp 2 we can see foaming inside the crankcase. Can all this be due to a faulty reed valve?

    If nobody has added any oil before, you now have compressors starved with oil. Expect more compressor damage if system continue to run that way.

    What is oil level regulation method in that system?
    What is superheat and subcooling when compressor 2 is in operation?
    What is crankcase temperature of compressor 2?
    Does compressor 2 have crankcase heater and is he OK?
    What is evaporator air in and air out temperature when you measuring 0 bar suction?
    Does both evaporator solenoids are open when you have this low pressure?
    Describe control logic of compressors and evaporators solenoids activation.

  3. #3
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Poor performance provision freezer

    are the two compressors sharing a common suction line to??

    Ice

  4. #4
    Join Date
    Oct 2008
    Location
    Norway
    Posts
    10
    Rep Power
    0

    Re: Poor performance provision freezer

    Hi.

    There is no oil level control of the compressors.
    Only one compressor is running at any time. The compressors share a common suction line.
    Both solenoids are open. When running comp1 there are no problems. Same configuration running comp2 gives low suction pressure and reduced heat exchange in both evaps.

    ChengTrit

  5. #5
    Join Date
    Oct 2008
    Location
    Norway
    Posts
    10
    Rep Power
    0

    Re: Poor performance provision freezer

    Here is a schematic of the system
    Attached Images Attached Images

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Poor performance provision freezer

    From this blurred diagram, I think you have oil separators at every compressor. Is that correct?
    If you have bad read valve then suction pressure would be elevated!
    You could make pump down of both compressors and compare pressure equalization time to establish are the valves are OK!
    Are both compressor of same model# and one of them is as redundancy? They newer work together?
    Last edited by nike123; 12-10-2008 at 10:02 PM.

  7. #7
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Poor performance provision freezer

    Quote Originally Posted by CHENGTRIT View Post
    Hi there. Im new to this forum, and hope you guys can help me out with a problem.
    Onboard this ship we have a provision cooling/freezing system consisting of 2 evaporators (one freezer and one in the cooling room) and two compressors sharing a common liquid line. Each compressor has its own condenser. System is running on R404
    Experiencing very low performance when running compressor 2. Suction pressure barely over 0 bar Head pressure around 12 bar. Freezer Evaporator temp is only -6C. Liquid is visible in sight glass wet indicator is OK.
    No problems when running compressor #1. -21C temp head pressure 15bar and suction pressure 1bar
    We recently needed to remove a lot of oil from comp2 as it fills up while comp1 is loosing oil when its running.
    We removed almost 2 liters. Max volume in sight glass is about 1 liter.
    After we removed oil from comp 2 we can see foaming inside the crankcase. Can all this be due to a faulty reed valve?
    Hello CHENGTRIT

    low suction pressure would indicate a blockage, not damaged reed valves.
    Is all the valves open full?

    Would there be a drier for each condenser on the liquid line and is it ok?

    Kind Regards Andy D
    If you can't fix it leave it that no one else will:rolleyes:

  8. #8
    Join Date
    Oct 2008
    Location
    Norway
    Posts
    10
    Rep Power
    0

    Re: Poor performance provision freezer

    Yes that is correct.

    chengtrit

  9. #9
    Join Date
    Oct 2008
    Location
    Norway
    Posts
    10
    Rep Power
    0

    Re: Poor performance provision freezer

    No,there is only one common drier for both condensers.

    chengtrit

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Poor performance provision freezer

    Quote Originally Posted by CHENGTRIT View Post
    Yes that is correct.

    chengtrit
    Check pressure drop between compressor 1 and 2 discharge and at port before filter and compare both circuit.


    Last edited by nike123; 12-10-2008 at 11:38 PM.

  11. #11
    Join Date
    Oct 2008
    Location
    Norway
    Posts
    10
    Rep Power
    0

    Re: Poor performance provision freezer

    The highlighted valve is a non-return valve.

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Poor performance provision freezer

    Quote Originally Posted by CHENGTRIT View Post
    We recently needed to remove a lot of oil from comp2 as it fills up while comp1 is loosing oil when its running.
    This isn't clear.

    Are you saying that comp2 fills with oil and comp1 empties when comp1 is running?

    Or are you saying that comp2 fills and comp1 empties when comp2 is running?

  13. #13
    Join Date
    Oct 2008
    Location
    Norway
    Posts
    10
    Rep Power
    0

    Re: Poor performance provision freezer

    Quote Originally Posted by Gary View Post
    This isn't clear.

    Are you saying that comp2 fills with oil and comp1 empties when comp1 is running?

    Or are you saying that comp2 fills and comp1 empties when comp2 is running?
    Comp 2 fills and comp 1 empties when comp1 is running

  14. #14
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Poor performance provision freezer

    Quote Originally Posted by CHENGTRIT View Post
    Comp 2 fills and comp 1 empties when comp1 is running
    I'm looking at the diagram and trying to figure out how this is possible.

  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Poor performance provision freezer

    Quote Originally Posted by CHENGTRIT View Post
    The highlighted valve is a non-return valve.
    That symbol doesn't look like symbol on other circuit! It has something attached to it! What is that?

  16. #16
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Poor performance provision freezer

    Quote Originally Posted by Gary View Post
    I'm looking at the diagram and trying to figure out how this is possible.
    Maybe if oil return line from oil separator of comp.1 is blocked or oil float is jammed or oil filter is blocked! Oil then circulate and goes to common suction line and fills both compressors, but oil level is not equalized with missing oil equalization line.
    Last edited by nike123; 13-10-2008 at 07:40 AM.

  17. #17
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Poor performance provision freezer

    Ignore.....
    Last edited by nike123; 13-10-2008 at 07:57 AM.

  18. #18
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Poor performance provision freezer

    Or possibly the oil return line from separator1 is hooked up to comp2?

  19. #19
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Poor performance provision freezer

    Or maybe some sort of oil equalization system has been added that is not on the diagram?

  20. #20
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Poor performance provision freezer

    Looking at the diagram: When one compressor is running, what stops refrigerant from gathering in, and staying in, the inactive condenser?

    It seems to me that when using one system, the inactive system should be completely isolated by closing the hand valves before the compressor and after the condenser.

    You might try running each system with the opposite system manually isolated to see if this improves the performance.
    Last edited by Gary; 13-10-2008 at 05:08 PM.

  21. #21
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Poor performance provision freezer

    i think there is a valve not closing properly.or staying open.if you are working whit one line,there has to be a by-pass or a regulator to prevent things like that to happen??? or am i wrong ??
    something is not wright in the drawing....
    Ice

  22. #22
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Poor performance provision freezer

    After each condenser, there are two manual valves in series (?). It seems like one of these should be a check valve?

  23. #23
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Poor performance provision freezer

    Quote Originally Posted by Gary View Post
    After each condenser, there are two manual valves in series (?). It seems like one of these should be a check valve?
    By look of the symbol, it seems that valve after condenser is some kind of reduction valve. His left side is smaller than right side.

    If we could get clear schematic and symbol legend, than some things should be clearer.

  24. #24
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Poor performance provision freezer

    Gents,
    it is quite normal for oil to migrate to the off compressor where this type of common suction line is employed.

    I have even seen the oil migrate from the discharge lines, where a worn check valve was fitted.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  25. #25
    Join Date
    Oct 2008
    Location
    Norway
    Posts
    10
    Rep Power
    0

    Re: Poor performance provision freezer

    Thank you guys for all input regarding this problem.
    We will keep the standby compressor and condenser isolated and observe the oil levels in each crankcase.
    After 24 hrs running it seems OK so far.


    ChengTrit

Similar Threads

  1. ice cream truck freezer
    By GaryC in forum Transport
    Replies: 7
    Last Post: 06-12-2008, 02:19 AM
  2. Hotpoint FFA71 Freezer High Temp Light / Fridge is Freezing
    By sumnerpa in forum Trouble Shooting
    Replies: 1
    Last Post: 19-08-2008, 03:16 PM
  3. Freezer compressor running 20 Hours/day
    By rickcw in forum Domestic
    Replies: 12
    Last Post: 08-03-2008, 11:50 PM
  4. Trolley freezer & blast freezer
    By smpsmp45 in forum NH3
    Replies: 0
    Last Post: 25-08-2007, 07:29 AM
  5. Project needs a freezer box.
    By NC-Joey in forum Fundamentals
    Replies: 14
    Last Post: 16-08-2007, 01:27 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •