    Help with refrigerant selection



    Hey,

    We're designing a cascade system for a freeze-dryer, I was wondering if anyone had tips for how refrigerant choice effects the compressor. Should we be matching pressure differences or compressor power.

    Right now we're usign DUPREX, a program by Dupont to compare refrigerants, and so far are looking at R-404A for the high temperature loop and R-508B for the low temperature loop (-70 C).

    Any assistance would be greatly appreciated.



  2. #2
    Join Date
    Nov 2006
    Location
    Kolkata, West Bengal, India
    Age
    64
    Posts
    10
    Rep Power
    0

    Re: Help with refrigerant selection

    Use R-23 Gas, but be careful. At ambient temp the sat. pr. is extremely high

  3. #3
    CoolAids's Avatar
    CoolAids Guest

    Re: Help with refrigerant selection

    Tapas Is right,Use R-23 Refrigerant....Good matchup....Also be advise that R-23 is Costy $$$$

  4. #4
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Help with refrigerant selection

    http://www.xtremesystems.org/forums/...wpost&t=144007

    Read this thread, you get to watch one be designed, parted out, assembled and charged.

    All open for all to see and explained in detail, amazing auto cascade -141c! made from a 5000btu/h AC

    As posted in another topic, after reading the thread several times you'll have a far more indepth understanding of why and how refrigerents need to match up and such!

    I to am planning a Vacuum freez drier, I am opting for an auto cascade for obvious reasons of performance Vs power ratio is superior and equipment life will be longer too!

  5. #5
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Help with refrigerant selection

    start with evap load, based on evap duty you slect the best refrigerant, then based on evap temp and load you select compressor displacment.

    After figuring out the second stage systems total needed condesor duty you select the first stage gas and based on required temps & duty you select the first stage compressor!

    ALL WAYS START AT THE EVAP! This seems to be the most over looked basic fact by people trying to design their own kit! And be mind full of local ambient trends!

    - Design in a high safety margine
    - Use all manual reset safety devices to force the opperators to fix the issue
    - Ensure the first stage has plenty of condensor capacity to spare

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  4. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  5. Refrigerant Selection Guide from down under
    By US Iceman in forum Refrigerants
    Replies: 2
    Last Post: 10-11-2006, 11:02 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •