    R22 to R410A retrofit



    We have switched out 6 R22 Carrier Split Heat Pumps for 6 R410A Carrier Heat Pumps. There is over 720ft of piping in the system, is there a need to replace the linesets, also we have purged the lines with nitrogen as well had them under pressure for two weeks?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: R22 to R410A retrofit

    Have you also cleaned the lines of contaminants and oil ?

    Perhaps take out an accessible section of pipe and strength test it to R410a standards.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    jodem's Avatar
    jodem Guest

    Re: R22 to R410A retrofit

    Could clean the line sets with PF-16 Pro-Flush, but not entirely sure that this is necessary. The line sets are 99% horizontal line sizes are 7/8" and 3/8" on the liquid side. Were just talking about 3 ton systems.

  4. #4
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: R22 to R410A retrofit

    i think the best is to flush them twice to be sure they are clean.

    Ice

  5. #5
    jodem's Avatar
    jodem Guest

    Re: R22 to R410A retrofit

    Think that client is going to try to make us change out the piping. This is a terrible waste of resources.

  6. #6
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: R22 to R410A retrofit

    1/ Confirm wall thickness on the 7/8 tube & confirm with the copper tube manufacturer that the tube is strong enough for 410a pressure.

    2/ Confirm with Carrier what the saftey HP cutout pressure is.
    Some split & VRF systems have HP cutout at 41.5 bar for 410a & if the indoor unit air fillers get blocked because someone forgot to clean them or any other problem which causes reduced air flow then the system can run at over 40 bar on the 7/8 gas tube.

    3/ Make sure you have an oil drain port on the compressor shell & carry out oil test with a refractrometer after the systems has been running for a few days. Then you can measure any mineral oil contamination & carry out an oil change.

  7. #7
    Join Date
    Nov 2006
    Location
    Kolkata, West Bengal, India
    Age
    64
    Posts
    10
    Rep Power
    0

    Re: R22 to R410A retrofit

    The R-22 gas is used with mineral oil, but R-404a gas essentially requires synthetic lubrication oil. These two oils does not go together. Therefore abosolute cleaning is necessary

  8. #8
    Join Date
    Feb 2001
    Location
    Doncaster, England
    Posts
    199
    Rep Power
    25

    Re: R22 to R410A retrofit

    Jodem,

    have you any more details about your flushing agent you mentioned - PF-16 Pro-Flush?
    Tony

  9. #9
    MACT's Avatar
    MACT Guest

    Re: R22 to R410A retrofit

    Be very careful, R22 7/8" pipe is not rated for 410A use. 410A runs at a much higher pressure and the wall thickness of 410A pipe is much thicker. the oil problems may the least of your problems.

  10. #10
    Join Date
    Sep 2008
    Location
    kent
    Age
    52
    Posts
    8
    Rep Power
    0

    Re: R22 to R410A retrofit

    Quote Originally Posted by MACT View Post
    Be very careful, R22 7/8" pipe is not rated for 410A use. 410A runs at a much higher pressure and the wall thickness of 410A pipe is much thicker. the oil problems may the least of your problems.
    whats this about? i thought fridge pipe was just that. can you get different grades then?

  11. #11
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Re: R22 to R410A retrofit

    Its all down to the gauge.
    Check the link
    http://www.hrponline.co.uk/hrp.stati...dInfo18xls.pdf

    the copper also has to be undamaged - no scratches/gouges or dents as they will cause weakpoints in the wall
    Brit
    Brit

Similar Threads

  1. Pressure Testing for R410a
    By Pooh in forum Tools and Calculators
    Replies: 33
    Last Post: 13-08-2008, 11:41 PM
  2. R410A pressure in air conditioning
    By irwinchong80 in forum Technical Discussions
    Replies: 4
    Last Post: 06-10-2007, 07:33 PM
  3. R410A - state of art
    By MrReds in forum Refrigerants
    Replies: 2
    Last Post: 04-03-2007, 10:56 PM
  4. Detection - is it air or R410A?
    By stalker in forum Technical Speculations
    Replies: 21
    Last Post: 24-02-2007, 01:48 AM
  5. R410A captube sizing for 2.5 bar / 35 psi pressure drop
    By DaBit in forum Technical Speculations
    Replies: 10
    Last Post: 27-11-2003, 09:05 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •